This weekend warrior is tackling another project, and as usual, I've got questions. I'm sure I'm overthinking a lot of this, but I'd rather make decisions with the right information.
I'm adding a ceiling box for a light fixture into the ceiling of a bedroom. For the new NM-B run, I'm traversing the ceiling and going down a wall to tap into the switched outlet. This wall is shared with the garage. This bedroom is on the first floor, and the second story of the house is above. The second story extends over the garage a bit (approximately 20% of the garage depth). To give the lay of the land, the first photo is taken from the center of the room. You can see my drywall cuts for running the NM-B. The next photo is from the ceiling cut where I will install the box at the center of the room toward the wall in question. The 3rd photo is the same photo taken from the ceiling hole near the wall. In the wall, there is a standard 2x4 stud and 2 stacked 2x4s for the top plate - I need to drill through this top plate to run the wire.
1.) Any kind of description on the construction above my ceiling/what I'm looking at would be helpful. I assume the top OSB is the subfloor of my second floor?
Answered: I-joists/engineered joists
2.) Updated: see schematic. This is a cross-section view: imagine rotating your view 90 deg from the way the photos are taken, and looking through all the materials - that's what I tried to sketch. Based on the posts thus far, the black rectangle represents my proposed hole. Any structural issues with this? I would make the hole near the stud that is visible in my first photo. And do I still need nail plates even if it's the top plate? The schematic is to scale, only exception being that I guessed on the widths of the I-joist based on what I could measure (the width closest to the proposed hole).
3.) Switching gears to the ceiling box, it's looking like I need to add blocking to the joist running along the right side in the images to properly attach the box. There is only 9/16" of joist flange until the OSB gets in the way, so I need to cut an opening on the OSB to stick my blocking into the correct position. Any concerns or anything else I need to do here? Perhaps fire-rated greatstuff expanding foam when I'm done? I am planning to secure the blocking from below the ceiling (through the drywall, then patch the screw holes).
Anything else I'm not thinking about that I should? Thanks in advance!
I'm adding a ceiling box for a light fixture into the ceiling of a bedroom. For the new NM-B run, I'm traversing the ceiling and going down a wall to tap into the switched outlet. This wall is shared with the garage. This bedroom is on the first floor, and the second story of the house is above. The second story extends over the garage a bit (approximately 20% of the garage depth). To give the lay of the land, the first photo is taken from the center of the room. You can see my drywall cuts for running the NM-B. The next photo is from the ceiling cut where I will install the box at the center of the room toward the wall in question. The 3rd photo is the same photo taken from the ceiling hole near the wall. In the wall, there is a standard 2x4 stud and 2 stacked 2x4s for the top plate - I need to drill through this top plate to run the wire.
1.) Any kind of description on the construction above my ceiling/what I'm looking at would be helpful. I assume the top OSB is the subfloor of my second floor?
Answered: I-joists/engineered joists
2.) Updated: see schematic. This is a cross-section view: imagine rotating your view 90 deg from the way the photos are taken, and looking through all the materials - that's what I tried to sketch. Based on the posts thus far, the black rectangle represents my proposed hole. Any structural issues with this? I would make the hole near the stud that is visible in my first photo. And do I still need nail plates even if it's the top plate? The schematic is to scale, only exception being that I guessed on the widths of the I-joist based on what I could measure (the width closest to the proposed hole).
3.) Switching gears to the ceiling box, it's looking like I need to add blocking to the joist running along the right side in the images to properly attach the box. There is only 9/16" of joist flange until the OSB gets in the way, so I need to cut an opening on the OSB to stick my blocking into the correct position. Any concerns or anything else I need to do here? Perhaps fire-rated greatstuff expanding foam when I'm done? I am planning to secure the blocking from below the ceiling (through the drywall, then patch the screw holes).
Anything else I'm not thinking about that I should? Thanks in advance!