If you're using that receptacle, the wire already in the wall is going to dictate the ampacity capability of the circuit. What gauge wire is feeding it? Is it not already connected to a breaker?Ok thanks. I already have a 220V feed to where the lift is going. It’s ground level.
I have the panel to wall receptacle already, the rest my electrician has suggested.If you're using that receptacle, the wire already in the wall is going to dictate the ampacity capability of the circuit. What gauge wire is feeding it? Is it not already connected to a breaker?
Which portion of that do you have already? "Panel to wall receptacle" would mean that everything in bold above is already present. Is that the case, or are you ripping out what is already there?I have the panel to wall receptacle already, the rest my electrician has suggested.
Panel → 25A double-pole breaker → 10/2 NMD90 → NEMA L6-30R wall receptacle -> L6-30P plug → 10/3 SOOW flexible cord → BendPak motor.
Panel to a blank wall receptacle is in place now as described, NEMA L6-30R wall receptacle -> L6-30P plug → 10/3 SOOW flexible cord → BendPak motor is yet to do. Lift is scheduled Sept 8 for installation.Which portion of that do you have already? "Panel to wall receptacle" would mean that everything in bold above is already present. Is that the case, or are you ripping out what is already there?