I wanted to be sure to document this somewhere for the next person having these troubles, and Garage Journal seemed like a good fit.
Our house came equipped with a 16kW natural gas powered Generac stand-by generator (model 0052540 and serial 4643547) - for a Garage Journal tie-in, this generator also powers my shop garage when the power goes out
It is equipped with the 992cc engine model 0F9145 and serial number 8022413.
In the last year and a half or so, our generator has been struggling to start. The weekly exercise wouldn't always successfully get going, and sometimes the power changeover during an outage wouldn't happen automatically, either. I would need to use a little starting fluid to help get the generator to finally kick over and run. BUT, then sometimes the generator would shut off while running, and the Overspeed / No RPM Sense if Flashing error light would be blinking.
I have replaced my plugs, oil and filter on a yearly basis since taking over maintenance on the generator after we bought our house (the previous owner had a service company come out annually - they were less handy). The only bigger issue we encountered over the years was an oil leak from the old oil cooler lines (those were then replaced). This past summer, tried replacing the starter in hopes of getting the generator to start easier, but that didn't solve the problem. I installed another new battery in July and things seemed to be working (the generator starting) better. But lately the generator was not starting again.
At this point, I was either going to find a fix for the generator, or wind up buying a new one. I did a lot of research trying to find a solution. I again reviewed the parts and owners manuals for our generator (I've had those .pdf's for a few years already) and kept trying to find a solution to the hard-starting - that seemed to me to be the most troubling issue. Then I finally found this forum, and there were a few more insights here that led me to identify a couple of potential fixes for my issues.
In the end, I think there were two issues that were causing us trouble and that I was able to resolve:
1) Hard Starting - after reviewing a number of posts here, I was able to to identify that my choke plate was not providing a good enough seal of the intake barrel when engaged. There was play in the plate the plate with the spring in the wrong position, and it was greatly reduced after I corrected the position of its spring arm. Here's a video demonstrating what I found:
rumble.com
And, here are some pictures of the spring arm out of position (purple arrow) and then put in its correct position (green arrow):


2) Engine Shutdown and Overspeed / No RPM Sense if Flashing LED - the posts I found here were able to narrow down the issue's likely root cause to the behavior of the Stepper Motor / Controller. It seemed that the engine was being allowed to exceed the maximum speed, driving up the output frequency and tripping the engine safety shutdown. I removed the motor and measured the coils, but I surprisingly found that they all measured between 10-11 Ohms (within expected normal range). I moved the Stepper Motor through its range by hand, and it seemed a little difficult, but it did move through the range. My only indication that there may still be in issue is that I felt a slight "hitch" in the movement about halfway through its travel, and it was more pronounced in one direction than another.
I went ahead and ordered a new motor. It arrived and I installed it and the engine no longer over-revs and shuts down. Additionally, with the old stepper motor / controller, there seemed to be more surges or dips in the engine speed when running. With the new motor, the engine speed held spot-on. Here's a video or the engine starting, and it shows the full range of motion of the stepper motor and choke solenoid / plate:
rumble.com
I put everything back together and let the engine go through one last manual startup cycle to insure everything was 100% again. As part of this repair, I also installed a fresh battery. Here's a final video of the full startup:
rumble.com
Just to compile all my findings to help the next person, here are some of the other causes I considered for my hard-starting issues:
Our house came equipped with a 16kW natural gas powered Generac stand-by generator (model 0052540 and serial 4643547) - for a Garage Journal tie-in, this generator also powers my shop garage when the power goes out
In the last year and a half or so, our generator has been struggling to start. The weekly exercise wouldn't always successfully get going, and sometimes the power changeover during an outage wouldn't happen automatically, either. I would need to use a little starting fluid to help get the generator to finally kick over and run. BUT, then sometimes the generator would shut off while running, and the Overspeed / No RPM Sense if Flashing error light would be blinking.
I have replaced my plugs, oil and filter on a yearly basis since taking over maintenance on the generator after we bought our house (the previous owner had a service company come out annually - they were less handy). The only bigger issue we encountered over the years was an oil leak from the old oil cooler lines (those were then replaced). This past summer, tried replacing the starter in hopes of getting the generator to start easier, but that didn't solve the problem. I installed another new battery in July and things seemed to be working (the generator starting) better. But lately the generator was not starting again.
At this point, I was either going to find a fix for the generator, or wind up buying a new one. I did a lot of research trying to find a solution. I again reviewed the parts and owners manuals for our generator (I've had those .pdf's for a few years already) and kept trying to find a solution to the hard-starting - that seemed to me to be the most troubling issue. Then I finally found this forum, and there were a few more insights here that led me to identify a couple of potential fixes for my issues.
In the end, I think there were two issues that were causing us trouble and that I was able to resolve:
1) Hard Starting - after reviewing a number of posts here, I was able to to identify that my choke plate was not providing a good enough seal of the intake barrel when engaged. There was play in the plate the plate with the spring in the wrong position, and it was greatly reduced after I corrected the position of its spring arm. Here's a video demonstrating what I found:
16kW NG Generac 16kW stand-by generator (model 0052540, serial 4643547) Choke Plate sealing issues
This video shows what I did to correct a hard-starting condition on our Generac generator. In the end, one arm of the spring for the choke plate was in the wrong position. As a result, it was not p...
And, here are some pictures of the spring arm out of position (purple arrow) and then put in its correct position (green arrow):


2) Engine Shutdown and Overspeed / No RPM Sense if Flashing LED - the posts I found here were able to narrow down the issue's likely root cause to the behavior of the Stepper Motor / Controller. It seemed that the engine was being allowed to exceed the maximum speed, driving up the output frequency and tripping the engine safety shutdown. I removed the motor and measured the coils, but I surprisingly found that they all measured between 10-11 Ohms (within expected normal range). I moved the Stepper Motor through its range by hand, and it seemed a little difficult, but it did move through the range. My only indication that there may still be in issue is that I felt a slight "hitch" in the movement about halfway through its travel, and it was more pronounced in one direction than another.
I went ahead and ordered a new motor. It arrived and I installed it and the engine no longer over-revs and shuts down. Additionally, with the old stepper motor / controller, there seemed to be more surges or dips in the engine speed when running. With the new motor, the engine speed held spot-on. Here's a video or the engine starting, and it shows the full range of motion of the stepper motor and choke solenoid / plate:
Generac 16kW generator - Stepper Motor and Choke Plate fix and operation
This video shows the stepper motor / controller for the throttle and the solenoid for the choke plate going through their movements during engine startup on a 16kW NG Generac 16kW generator (model 005
I put everything back together and let the engine go through one last manual startup cycle to insure everything was 100% again. As part of this repair, I also installed a fresh battery. Here's a final video of the full startup:
Generac 16kW generator - startup after Stepper Motor and Choke Plate repairs
This video shows a normal startup of our generator after replacing the stepper motor / controller for the throttle and the solenoid for the choke plate on a 16kW NG Generac generator (model 0052540, s
Just to compile all my findings to help the next person, here are some of the other causes I considered for my hard-starting issues:
- Hardening or Cracking of the fuel pump diaphragm: this was mentioned as an issue for hard-starting that would result in the the engine not getting enough fuel/gas. The Diaphragm Regulator 0F9426 is no longer available. Had the problem traced to this part, I would have had to see if a newer regulator might work with our generator. Also, to trace the problem to this issue I would have needed a manometer to read the gas supply pressure into and out of the regulator. I'm always up for buying a new tool, though!
- Valves out of Adjustment: I have never adjusted the valves on our unit. I will add that to my next annual maintenance. I do not know if the previous homeowner had the valves adjusted as part of the service they used to maintain the generator, either. From what I read hear, if the valves are out of adjustment and not sealing correctly, then this could cause issues with poor compression or lack of strong-enough vacuum to pull in fuel and cause hard staring and poor running.
- Poor Compression: I did not check the compression on our engine this time. I think I looked at it in the past at one point, but do not recall the readings. The poor compression could cause hard starting and poor running. I do know that our engine has "a lot" of hours on it, though it is older and not equipped with an hour meter. We've had outages here that have lasted almost a week, and we have at least 1 or 2 multi-day outages per year. It's woodsy where we live

Last edited: