For 15+years, I NEVER ONCE had to use my generator and I store it underneath my workbench.
It has become such a fixture there that it became out of site, out of mind.
I bought it back in 2011 when a storm snapped a tree limb down the block and snapped our service line....
Photo circa 2011
Oh sure, I HAVE heard you have to run them
"every so often" or the winding do something...or this or that...but eh, life comes first.
I even printed out a service manual for the thing...where it sat, on top of the fuel tank, under the bench.
WELL....you know where I am going with this already, don't cha?!?!
Yup...."BOOM!" 100F/39C outside, AC running full tilt and we loose power.
No power to 2 sump pumps, 2 critical refridgerators, no GJ as the internet died....OMG. LOL!
Called to find maybe power will return in 2+ hours.
So I figured....NO TIME LIKE THE PRESENT to inspect and fire up the generator....
....not fully realizing it's been 15 years since it last started!
I poured some gas it it, flipped "ON" switch, turned gas valve to "OPEN", ....choked it...
...pull....
...pull...
...pull...
...unchoked...
...pull....
....pull..
........................................
"VROOOOOM!" ....SHE FIRED RIGHT UP!!!! WOO HOO!!!!!
So I stuck my incandescent test bulb on the left side of 110vac outlet......
LIGHTS BRIGHT!
................................................................on the right side of 110vac outlet.....NO LIGHT AT ALL!!
Checking the breaker, I find it has broken away from the faceplate and is recessed into the plastic box surrounding the electronics.

This will have to be repaired along with a
full oil change, but not today...too hot out, 100F/39C, as I mentioned earlier...document okay.
I get a screwdriver and realign it with the hole and press it, retest the right side outlet and it now WORKS!
I was very happy the generator is still able to work...and shut it down immediately!!!!!!
Documented the issues, pulled the fuel tubing off the carb and drained the tank, refitting the tube on the carb.
Added a ounce of Stabil and Marvels Mystery Oil to the tank, shook it up as there was a bit gas left in the tank ridges and started up the gene again until it ran dry and sputtered out.
Well, another repair to add to a pretty small list....just waiting for the weather to cool down to I can open up the plastic electrical box to investigate how those breakers are secured to the faceplate.
MY GUESS is a bimetal clip rusted out and stopped holding the breaker...stay tuned.
Also looking through the manual for oil specs, it said to check the engine specifications manual...the manual I didn't download!
However the internet found the engine from the gene's model number and the oil needed to replace the stuff in there from 15+years ago is.....
"Recommended Oil Type (Viscosity)
Choose your oil based on the outdoor temperature where you operate the generator:
- Above 40°F (4°C): SAE 30 high-quality detergent oil. This is the standard, most common choice for warm-weather operation. [1, 2, 3]
- All Temperatures / Best Protection: Synthetic SAE 5W-30 or 10W-30. Full synthetic oils offer the best engine protection across both extreme cold and hot operating climates without increased oil consumption. [1]
- Below 40°F down to 0°F: SAE 10W-30 or 5W-30. Avoid using standard SAE 30 in freezing weather, as it makes the engine very difficult to pull-start. [1, 2, 3]
- Capacity: 36 fluid ounces (approx. 1.1 quarts or 1.06 liters).
- Note: Do not overfill. Buy a standard 32 oz. quart and a smaller 10–12 oz. bottle, or a larger multi-quart container so you have enough to reach the full mark on the dipstick.
So thats works for me, I can do that and also will know when the crankcase is totally empty too.
Now the circuit breaker they show for replacemtny looks like this....
209872GS
I will be suprised if the right one that pulled away from the faceplate, looks the same...will know when I open the plastic housing up.
Might be a updated part for the exact same reason this one pulled apart.
So I got my marching orders....will let the "Dog Daze of Summer" pass by before I tackle this.