    Power to pole barn questions

    That sounds like a great idea. I'm all about less work! Thank you checkthisout!
  2. B

    Power to pole barn questions

    Thank you buddyboy.......that makes some sense.
  3. B

    Power to pole barn questions

    Okay, I think I have a grasp on the subpanel stuff. Thanks again to those who gave their input! Here's another question: Does it matter if the rods are inside or outside the detached barn? In my pole barn, the floor is not finished yet. Because it's a dirt floor, can I pound the ground rods...
  4. B

    Power to pole barn questions

    Thank you Pattenp. I see some holes on the lower right side of the box. I would assume that is for the the ground bar.I will pick up a kit today.
  5. B

    Power to pole barn questions

    This is the subpanel I bought yesterday. It looks to me like the 2 isolated bars(ground and neutral?) are connected with a insulated black strap. Should I disconnect and discard the black strap and attach one to the chassis? Or do I need to leave those 2 isolated bars alone (call them neutral)...
  6. B

    Power to pole barn questions

    Thank you wyliesdiesels.....I needed that clarification! I can use the feeder that I purchased. I won't drill holes in my conduit, just a thought. I already bought the sweeps....just need to get the remaining conduit. Thank you again.
  7. B

    Power to pole barn questions

    The holes in the conduit was a fleeting thought. Thank you.
  8. B

    Power to pole barn questions

    I won't. Thank you.
  9. B

    Power to pole barn questions

    CNGsaves said OP . . . you still need sparkies to tell you what BREAKER needs put in house to feed the garage as you're over 100 ft with the MHF 2-2-2-4 Al wire to the garage. At MOST, it can be 90A but may be LESS due to your length. Here is a rough aerial view of my layout. The house wasn't...
  10. B

    Power to pole barn questions

    Like I said in my original post, it is MOSTLY sand. If I were to estimate, I would say 10% rock. That being the case, I would hate to have frost push a sharp rock into my feeder. Here's a (maybe) dumb :Homer:idea: Drill drainage holes in the conduit and face the holes down. Any water...
  11. B

    Power to pole barn questions

    Oh, and thank you all again for your input. I have decided to go with conduit all the way. It just makes sense based on the cost and effort.
  12. B

    Power to pole barn questions

    I chose a 90amp breaker based on what I read in this forum. If I misunderstood what amperage I'm allowed, I will return the 90amp and get the right breaker for my distance. I am not great with math. I've seen references leading to web pages but when I went to them, I got more confused.:confused:
  13. B

    Power to pole barn questions

    Thank you all for your input! Today is Menards (like HD or Lowes) last day for 11% off everything so I will be purchasing the 100amp 20 space load center, conduit, 2 ground rods, etc.. while it's cheaper. Then off to work.......
  14. B

    Power to pole barn questions

    I guess I didn't mention all my amperage needs. I just purchased a Craftsman 113.24181 Table Saw. It is a direct drive, 240 volt, 7amp saw and the manual recommends a 15amp 2pole breaker. I also have a 220v hot water heater that I intend to hook up in the bathroom someday. Who knows what else I...
  15. B

    Power to pole barn questions

    Thank you for the most informative info oldwizard1! This is the best site ever!
  16. B

    Power to pole barn questions

    sorry oldwizard, I missed your replys....
  17. B

    Power to pole barn questions

    It does NOT have MHF printed anywhere on it ? Sounds fishy to me. Some Big Box store employees don't know their wire types. Southwire USE2/RHH/RHW2 wire is a single copper conductor. theoldwizard1 has me concerned. If the feeder doesn't have "MHF" printed on it, yet the dealer has it listed...
  18. B

    Power to pole barn questions

    I'm not sure why some are conduit supporters. Maybe they've had experiences in the past where conduit was needed and the feeder failed?
  19. B

    Power to pole barn questions

    The feeder says GENERAL CABLE S 2 AWG (33.6 mm2) COMPACT STABILOY (R) AA-8030 AL XLPE 600V USE-2 OR RHH OR RHW SUN-RES (UL) 2014 NOV I bought it from a local dealer The description listed it as 2224MHF Hope I didn't get the wrong feeder!!!
  20. B

    Power to pole barn questions

    This is what I purchased yesterday: