I have an idea in my head of how to power every 120 Volt circuit in a house from a 120 Volt generator, and I’d like to hear your feedback.
For the sake of this discussion, let’s assume you have a 3600 Watt Generator, which produces 30 amps at 120 Volts.
Let’s also assume you have a proper generator inlet box on the outside of your house, connected to your load center with a properly sized wire, and a properly installed manual interlock kit installed in your panel. (No need to start another flame war about suicide cords, killing linemen, etc).
(I think you could consider this circuit to be a continuous load and therefore would need to derate your backfed breaker by 20%, but let’s not get hung up on details like wire size or breaker derating, there’s plenty of that discussion in other threads).
Let’s also assume you live in the boonies, and there is no AHJ or inspector, so you just plan to follow the NEC.
Let’s also assume you have no MWBCs.
So you sized your wire to handle 30 Amps at 120 Volts, say a 10/2 WG.
In the panel, you take the single hot conductor from the generator with 30 amps, and pigtail it into two other #10 wires, and use those two #10 wires to backfeed TWO INDIVIDUAL SINGLE POLE 30 amp breakers, rather than the usual 240 volt backfeed double pole breaker.
When you have a power outage, turn off EVERY circuit in the panel, plug in the generator, start it up, open the main breaker (turn it off), then the interlock kit allows you to close (turn on) your two backfed breakers providing power to the panel from the generator.
Obviously it is imperative that you leave all 240 Volt appliances turned off while you are on generator power.
At this point, every single pole 120 volt breaker in the house has power available to it, regardless of which leg of the panel it is on. You can pull up to 30 amps total either onto a single leg of the panel, or split it between the two legs, and it does not matter how much power is on which leg. Your neutral going back to the generator is already sized for 30 amps, so it’s not overloaded. Your hots are protected by a 30 amp breaker at the generator, and the single pole 30 amp backfeed breakers in the panel.
I’m sure there’s someone out there who thinks this is either a violation of NEC or a generally bad idea, or both. Please tell me why, as I’m throwing this plan out there to be critiqued, and please include NEC references if you can.
For the sake of this discussion, let’s assume you have a 3600 Watt Generator, which produces 30 amps at 120 Volts.
Let’s also assume you have a proper generator inlet box on the outside of your house, connected to your load center with a properly sized wire, and a properly installed manual interlock kit installed in your panel. (No need to start another flame war about suicide cords, killing linemen, etc).
(I think you could consider this circuit to be a continuous load and therefore would need to derate your backfed breaker by 20%, but let’s not get hung up on details like wire size or breaker derating, there’s plenty of that discussion in other threads).
Let’s also assume you live in the boonies, and there is no AHJ or inspector, so you just plan to follow the NEC.
Let’s also assume you have no MWBCs.
So you sized your wire to handle 30 Amps at 120 Volts, say a 10/2 WG.
In the panel, you take the single hot conductor from the generator with 30 amps, and pigtail it into two other #10 wires, and use those two #10 wires to backfeed TWO INDIVIDUAL SINGLE POLE 30 amp breakers, rather than the usual 240 volt backfeed double pole breaker.
When you have a power outage, turn off EVERY circuit in the panel, plug in the generator, start it up, open the main breaker (turn it off), then the interlock kit allows you to close (turn on) your two backfed breakers providing power to the panel from the generator.
Obviously it is imperative that you leave all 240 Volt appliances turned off while you are on generator power.
At this point, every single pole 120 volt breaker in the house has power available to it, regardless of which leg of the panel it is on. You can pull up to 30 amps total either onto a single leg of the panel, or split it between the two legs, and it does not matter how much power is on which leg. Your neutral going back to the generator is already sized for 30 amps, so it’s not overloaded. Your hots are protected by a 30 amp breaker at the generator, and the single pole 30 amp backfeed breakers in the panel.
I’m sure there’s someone out there who thinks this is either a violation of NEC or a generally bad idea, or both. Please tell me why, as I’m throwing this plan out there to be critiqued, and please include NEC references if you can.