Aceman-
"You don't use the motor nameplate for sizing wire or breakers."
Says who? Your NEC code book?
--Doozer
using 2005 code, Yes, see 430.6(A)1:
"Other than for motors built for low speeds (less than 1200 RPM) or
high torques, and for multispeed motors, the values given in Tables 430.247, 430.248, 430.249, and 430.250 shall be used to determine the ampacity of conductors or ampere ratings of switches, branch-circuit short-circuit and ground-fault protection, instead of the actual current rating marked on the motor nameplate."
The purpose of this is to allow replacing same HP motors in equipment without having to redesign the branch circuit due to slight changes in motor efficiencies.
note that 430.6(A)2:
"Separate motor overload protection shall be based on the motor nameplate current rating."
This is NOT the same as the circuit breaker in the main panel. This is the thermal overload device located in the motor control box.
The compressor in question is 7.5HP per table 430.248 shows 40 amps.
430.22 says:
"Conductors that supply a single motor used in a continuous duty application shall have an ampacity of not less than 125 percent of the motor's full-load current rating as determined by 430.6(A)(1)."
Therefore 40x1.25=50amps. So 6 gauge NM would be appropriate (unless having to de-rate due to other conditions).
430.3x deals with overload (not short circuit or ground fault) protection. This protection is usually located at the motor (i.e. the motor control box).
430.32(A) - Continous duty motors (Greater than 1 hp):
"Each motor used in a continuous duty application and rated more than 1 hp shall be protected against overload by one of the means in 430.32(A)(1) through (A)(4)."
In this case, the compressor is protected by 430.(A)(1) Seperate overload device:
"A separate overload device that is responsive to motor
current. This device shall be selected to trip or shall be rated at no more than the following percent of the motor nameplate full-load current rating:
Motors with a marked service factor 1.15 or greater 125%
Motors with a marked temperature rise 40°C or less 125%
All other motors 115%
Modification of this value shall be permitted as provided in 430.32(C). For a multispeed motor, each winding connection shall be considered separately."
I don't have the details of what is in that motor control box, but I can it does have an overload protection device, and I assume a) that is came with the compressor manufacturer, and b) Ingersoll followed the code when they chose the device.
430.5x deals with "devices intended to protect the motor branch-circuit conductors, the motor control apparatus, and the motors against overcurrent due to short circuits or grounds. These rules add to or amend the provisions of Article 240."
430.52(A)1 Rating or Setting for Individual Motor Circuit - General:
"The motor branch-circuit short-circuit and ground-fault protective device shall comply with 430.52(B) and either 430.52(C) or 430.52(D), as applicable."
So 430.52(B):
"The motor branch-circuit short-circuit and ground-fault protective device
shall be capable of carrying the starting current of the motor."
Kinda obvious I think.
430.52(C)1:
"In Accordance with Table 430.52 A protective device that has a rating or setting not exceeding the value calculated according to the values given in Table 430.52 shall be used."
Looking at 430.52 shows that single phase motors using inverse time breakers are allowed up to 250%.
430.52(C)2:
"Where maximum branch-circuit short-circuit and ground-fault protective device ratings are shown in the manufacturer's overload relay table for use with a motor controller or are otherwise marked on the equipment, they shall not be exceeded even if higher values are allowed as shown above."
I don't have the data from the manufacturer, the original poster will have to answer this.
The rest of 430.52(C) doesn't really apply in this case and 430.52(D) doesnt apply at all.
So we have for the original poster, wire that can support 50 amps (such as 6 gauge romex or 8 THHN in conduit), protected by a breaker not to exceed 2.50x40amps=100amps, as well as the factory overload protection that IR put in the control box.
EDIT: OOPS just noticed Aceman typed up something really similar to what I just typed up.