Alright...it's me again as I continue the build. I spent time contemplating what Mr. FastHotRod had to say, and read his post about 20 times. Very informative and I learned a ton! Super thankful!
Glad I could help!
After going through my expected load pull I think I'm going to go with my idea of just putting a 125amp double pole breaker. I don't see needing to ever pull much over 100 even if I'm hosting a symphony of welders and tools at the same time. besides it will save on costs from the lug, smaller gauge wire, smaller conduit, smaller subpanel, and easier to pull it all together. Here's the plan...check me for insanity please:
125amp BR double pole
https://www.amazon.com/gp/product/B0009XAXJQ/ref=ppx_yo_dt_b_asin_title_o00__o00_s00?ie=UTF8&psc=1
Going to run:
#1 THHN x 3 for the two hots and neutral
#6 THHN for the ground
The only challenge is none of the big boxes carry it in stock....I may call around to some of the local sparky shops tomorrow, but I found it here for fairly cheap
https://www.wireandcableyourway.com/1-awg-thhn-building-wire.html
You are on the right path... but you probably don't want to 'guess' as to what your loads will actually be. There is a process that you can follow to help determine what size breaker/wiring that you need, then you can go from there. Article 220 of the NEC covers it.
Here's some articles that explain it better than I could:
https://iaeimagazine.org/magazine/2...anch-circuit-feeder-and-service-calculations/
http://www.codebookcity.com/codearticles/nec/necarticle220.htm
https://www.ecmweb.com/nec/sizing-circuit-protection-and-conductors-part-1
https://www.ecmweb.com/content/middle-wire-isnt-its-end
So I'd take a look at your loads in your shop and determine what is considered continuous and what is considered the maximum.
So assuming that you did that, then you would look to the NEC and see that for circuits under 800A, you can size the conductor based on the ampere rating you actually need, and can use the next higher standard rating of over current protection device (OCPD) if the one you need does not exist.
So for example, if you had it calculated out that you needed 60A continuous, (60 * 125% = 75A) and that you'll have a maximum of 105A you could run a #2 that is rated at 115A. (assuming 75 degrees C) Per the Code, you could feed that #2 with a 125A breaker because they don't make a 105A or a 115A breaker. (100A typically jumps to 125A)
I'm making assumptions in my examples here... so I would recommend that you take a look at Article 220 and your loads, and do a little homework if you want to nail it down correctly. You may find that while you have a lot of cool tools like welders, plasma cutters, etc... you may not use all of them at the same time, so your actual ampacity requirements may be lower than you initially thought.
I plan to make a 6-7ft run of Schedule 80 along the wall of the brick house that the main service is on....90 it down 18-20 inches below the ground, under my sidewalk, and then the short 3-4 feet distance to an LB on the bottom of the shop. I went ahead and dug out the trench from the house to the sidewalk to see what I would be up against....Wasn't much fun as I had base from the house foundation to deal with, but eventually got there.
Since I'm only talking about a 15-18ft run would you just stick with sch80 all the way? or should I convert to 40 under the ground? I'm just assuming I have to use 80 since it's exposed on my house, and then will be when it comes out of the ground to the LB at the shop.
For the price of schedule 80 for such a short run, I'd not worry about it. Your Authority Having Jurisdiction (AHJ) may say that schedule 40 is acceptable if there isn't a chance for impact damage... so you might want to reach out to your local AHJ (Code compliance folks) to see what they say about it if cost is a factor.
I was also planning on 2inch....I know it handles it from a fill standpoint, but thought it might be a tad easier to pull the cables through.
Correct. 2" would technically be good for more than that, too. So if you found that you have a bunch of friends over and were using so much equipment that you were popping the breaker, or added more cool tools and needed more ampacity, you would be able to re-pull larger conductors and swap the breaker based on your new loads.
You might consider dropping in an additional 3/4" or 1" in the trench for future use... security system, networking, etc... PVC is relatively cheap, and I'd rather have it and not need it, than need it and have to dig it out again.
I'll post a pick of my first trench.
Thoughts/suggestions/words of encouragement as I tunnel under the sidewalk are encouraged! lol
Best of luck you you... Please remember to call 811 before you dig. You never know what's in the area and how the lines are run, so try and avoid a costly mistake if you can. (Might be too late for that, but it's always good advice anyway.)
Mark