How many fluorescent fixtures on a 15 amp circuit?

Notch1988

Well-known member
Joined
Feb 20, 2006
Messages
527
Location
Fort Saskatchewan, AB, Canada
I'm planning to use the 8 foot, 4 bulb T8 strip light fixtures. With 4x32W bulbs per fixture I'm looking at about 1.2 amps in bulbs alone. I'm wondering if 6 of these fixtures on one 15 amp circuit is too much or should I go with 4 per circuit. I'm doing 12 fixtures in total, so it's either 2 circuits or 3.
 
To avoid these ads, REGISTER NOW!

Steevo

Well-known member
Joined
Aug 18, 2009
Messages
8,738
Location
43.49600, -112.04300
Six of the 8 foot, 4 bulb T8 strip light fixtures should be no problem on a 15A circuit.
Check the ballast for actual amperage draw, not a cumulative multiplier of bulbs
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Code says you cannot exceed 80% of the capacity of a circuit for continuous loads. Lighting is defined as a continuous load (3 hrs or more is the def of continuous, but code also defines specific items as continuous, including lighting).

Thus you should not exceed 12 amps on a 15 amp circuit, or 16 amps on a 20 amp circuit. This would make 10 fixtures your max on a 15 amp circuit. If these fixtures have magnetic ballast, the induction loads are much higher, and I would not put this many fixtures on a circuit.

Indeed, use data plate specs for the calculations, not a 4 bulbs times 32 watts calculation.

Charles
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Every 4 lamp T8 ballast I've looked at draws between .99-1.00 amp at 120v. It's easy to check for yourself.
 

marty_p

Well-known member
Joined
Aug 1, 2008
Messages
1,411
Location
SE LoUiSiAna
Every 4 lamp T8 ballast I've looked at draws between .99-1.00 amp at 120v. It's easy to check for yourself.

With 12 four-bulb fixtures, prepare for serious light!!! :cool:

Oh, and don't forget to post our sought-after pics later on... :thumbup:
 

eljefino

Well-known member
Joined
Feb 21, 2008
Messages
336
You can do a bunch on a circuit but check into what your 69 cent switches are rated for capacity. It's also cool to have a couple switches to "stagger" the startup and just have more control over things.
 

Ferrino

Well-known member
Joined
Mar 30, 2011
Messages
254
Location
San Diego, CA
Can I please ask which fixtures you went for? I'm in the same position of adding T8 lighting to my garage...
 
To avoid these ads, REGISTER NOW!

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
What do you mean "rated for a 20A circuit". It's a 12 gauge wire run on a 20A breaker, the lights don't care.
 
OP
N

Notch1988

Well-known member
Joined
Feb 20, 2006
Messages
527
Location
Fort Saskatchewan, AB, Canada
What do you mean "rated for a 20A circuit". It's a 12 gauge wire run on a 20A breaker, the lights don't care.

I just wired my basement and discovered that fixtures hard wired into a 20 amp circuit need to be rated for it. I had run a 20 amp circuit to the bathroom and put the lights and fan on it and got told it wasn't correct cuz the lights and fan weren't rated for a 20 amp circuit. I'm not sure how you find out if it is or isn't though.
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
Must be a Canadian thing. You can put a 7 watt Christmas light on a 20A circuit if you want. The 20A is just the circuit capacity maximum. Wire size is specified for certain max capacity of a circuit. 14 ga wire is typically used for a 15A, 12 ga is considered good for 20A. Rules require that lighting circuits only be loaded to a certain percentage of the capability of the circuit as noted above. You can hang permanent connected lights, etc on there until you reach the 80% max figure. The actual current draw or load on the circuit is determined by the sum of the connected devices and not by the size of the breaker or wire size installed. If your connected device(s) exceed the 80% max, then you have to upsize the wire and breaker that supplies the device(s). If I was looking for a circuit rating, it would be some minimum requirement specified by the manufacturer or just the voltage requirement - 120V or 240V. Reviewing the spec sheet shows that the ballasts are rated for use on 120-277V power.
 
Last edited:

miner

Well-known member
Joined
Oct 3, 2012
Messages
96
The way I have heard it described is: take amperage times voltage to get wattage capacity (e.g., 15 amps * 120 volts = 1800 watts) then you can distribute this capacity to as many fixtures as you want so long as the sum total of the rated wattages of all fixtures does not exceed this amount. Multiply by .8 for continuous load derating. If your fixtures are rated at 130 watts max, that would be about 11 fixtures on a 15 amp circuit.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
The way I have heard it described is: take amperage times voltage to get wattage capacity (e.g., 15 amps * 120 volts = 1800 watts) then you can distribute this capacity to as many fixtures as you want so long as the sum total of the rated wattages of all fixtures does not exceed this amount. Multiply by .8 for continuous load derating. If your fixtures are rated at 130 watts max, that would be about 11 fixtures on a 15 amp circuit.


on fluorescent fixtures you have to use the amps listed on the ballast, not the wattage of the lamps.
 

eljefino

Well-known member
Joined
Feb 21, 2008
Messages
336
Must be a Canadian thing. You can put a 7 watt Christmas light on a 20A circuit if you want. The 20A is just the circuit capacity maximum. Wire size is specified for certain max capacity of a circuit.