Let it be known that a wall mounted jib crane puts a tremendous load on it's mount points. Think of it as a big lever arm and the further the load is from the post or wall its mounted to, the longer the lever arm.
With a load rolled to the outer outer end of the I-beam, it converts this vertical load being lifted into very high tensile (on top mount) and compressive (on bottom mount) loads acting mainly horizontally on the pivot pins. There is still a combined vertical load on the mounts that equals the lifted load plus the weight on the crane itself and the top mount sees a majority of that.
On the other hand, with the load rolled over close to the wall, the load loses most of it's "leverage" on the wall and the horizontal loads reduce significantly. The lower mount now sees nearly all of the load in a vertical direction
Here are some numbers from the professional engineer to give you an idea:
1000 pound load at outer end:
Top mount - 3550# horizontal (tension), 1110# vertical
Bottom mount - 3550# horizontal (compression), 130# vertical
1000 pound load 12" from post:
Top mount - 700# horizontal (tension), 220# vertical
Bottom mount - 700# horizontal (compression), 1020# vertical
In my particular installation, when swinging the crane from one side to the other, the loads do, in fact, reverse from compression to tension on the two darker-colored beams (connecting to the post by the exhaust fan) as the crane swings through it's half circle. They reverse at the point when the crane is at 90 degrees where the loads in the dark beams (top and bottom) essentially drop to zero. I just wanted to clarify this point as there was some controversy above. Also, my particular installation is a bit weaker at the 0 and 180 degree positions than in the middle of the swing due to my non-symetrical structure, but I will keep that in mind as I'm using it.
Lastly, rest assured I will be the first one running if I here splintering wood!