All things being equal, can someone explain the difference (pros/cons) in using a 12K BTU unit that runs on 110 volts vs. one that runs on 220 volts?

Thanks in advance.
 
Last edited:
To avoid these ads, REGISTER NOW!

doan

Well-known member
Joined
Sep 25, 2012
Messages
585
Location
Frisco, TX
Assuming you're running a dedicated circuit for it, the 110 will cost more to install since you'll need to pull bigger wire. 110 will use twice the amps as 220.
 

JakeKohl

Well-known member
Joined
Feb 23, 2012
Messages
1,365
Location
Greenville, SC
Assuming you're running a dedicated circuit for it, the 110 will cost more to install since you'll need to pull bigger wire. 110 will use twice the amps as 220.

This is probably the most direct reason. You can run most 18kbtu units at 220V with standard 12 gauge two conductor romex. Also note that wire sizing for a dedicated circuit to an HVAC can be sized to the peak amperage rating on the unit - not so much the breaker size. For instance, you can run 12 gauge on a 220V single phase circuit behind a 25 amp (possibly 30...not sure) breaker. My 18kbtu units have a peak rating of 19.2A.
 
Last edited:

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
Less amps is gooder. Use 220 whenever possible.

It hasn't happened yet but some jackass will give you a hard time about 110 and 220 vs. the actual 120 and 240 that you actually have. I speak from experience with that.
 
To avoid these ads, REGISTER NOW!

JakeKohl

Well-known member
Joined
Feb 23, 2012
Messages
1,365
Location
Greenville, SC
Less amps is gooder. Use 220 whenever possible.

It hasn't happened yet but some jackass will give you a hard time about 110 and 220 vs. the actual 120 and 240 that you actually have. I speak from experience with that.

Old school and new school collide.
 
OP
S

sammm

Well-known member
Joined
Jun 7, 2010
Messages
609
Location
North Carolina
I realize that but if his unit has the option of 110 or 220 ten I am assuming his indoor units only are going to be pulling 110...

Thanks for the replies guys, I appreciate the info!

Tim, I wasn't referring to a unit that can do either. Some of the 12K BTU AC/heat pumps run on a 110 circuit, and others require 220.
 