Replacement Extension Cord Multi-receptacle

John in OH

Well-known member
Joined
Jun 2, 2007
Messages
2,444
Location
SE Ohio & Eastern Virginia
I have an 12/3 extension cord with a single-plug receptacle. I'd like to replace this single-plug receptacle with a multi-plug receptacle similar to this:

IMG_0478 small.jpg

Problem is, I've hunted numerous stores and on-line sites and I cannot find a replacement cord end of similar design. There are lots of new cords out there that have this design receptacle molded onto the cord, but I can't find a loose replacement-type end.

Anyone know of an on-line source for such a replacement multi-plug receptacle?
 
To avoid these ads, REGISTER NOW!

Jbullfrog

ALLIANCE MEMBER
Joined
Jan 9, 2007
Messages
2,347
Location
Avoca, Iowa
That would be due to the Osha requirement for power cords to have factory installed ends that are not removable.
 
OP
J

John in OH

Well-known member
Joined
Jun 2, 2007
Messages
2,444
Location
SE Ohio & Eastern Virginia
That would be due to the Osha requirement for power cords to have factory installed ends that are not removable.

I'm a little fuzzy on what you are trying to say here ....

Lowes, HD, Menards, etc. have shelves full of single-plug replacement receptacles for cords. What I'm looking for is a multi-plug replacement receptacle.

I can buy any of the multitude of single-plug receptacles, or I can buy single-to-multiple plug adapters such as this:

Multiplug.jpg

Or I can buy short extension cords that have single plugs on one end and multiple plug receptacles on the other end:

Multiplug 2.jpg

So why not multiple-plug replacement receptacles???
 

DesertSparky57

Well-known member
Joined
Apr 12, 2013
Messages
92
Location
Las Vegas
The end you are searching for does not exist, 15 years as a sparky and not once have I ever seen a multiple receptacle cord end that is replaceable. As far as I know, only the molded ends and adaptor type like you posted pics of have ever been available.

As far as why not? Probably because splitters in general have always been frowned upon by OSHA. In the heavy industrial setting I work in all 120v splitters are required to have a built in overload protection at the point of splitting. Yes really. A breaker molded into the splitter. Overloading extension cords is apparently OSHA's top priority of enforcement areas lately.
 
To avoid these ads, REGISTER NOW!

rsieracki

Well-known member
Joined
Mar 3, 2010
Messages
1,679
Location
Chicagoland Area
get a nice exterior/waterproof 4" box, 2 duplex outlets (1 preferably a GFCI), and a weather cover and wire/rig one up. a more 'correct' approch to the 4 inch metal box with 2 old outlets i (and many others) have put on a a few cords years ago that still work
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
You can always try this: http://www.molex.com/woodhead/produ..._DISTRIBUTION.xml&channel=Products&Lang=en-US


3000-1_ISO.jpg



These will do much better then any cobbled up mess like a 4 square box & raised cover.
 