It was done completely intentionally for many years, and caused no real issues until the government went looking for reasons to stick their nose into things yet again.
Well, kinda.
Just like my example of an "old" 3-wire dryer and oven circuit. Anything 120V returned on ground. Like the light bulb and some timers.
A few code cycles ago the NFPA determinded that this was not a good thing. Hence why there are now 4 wires running to dryers and ovens.
The 120V loads return on the neutral like there supposed to. That allows the ground to be carrying nothing, so there is less impedance to help clear a fault faster if it happens.
While there may have never been any real issues, it is (and always has been in my opinion) a less than a proper way to have a safe electrical install.
EDIT- These currents returning on ground can add up if there are many of them on a subpanel which has the grounds and neutrals seperated.
Not very likely though.
Sorry guys, NOT AT ALL true. Some of what I read on message boards really scares me.
The return current was NEVER allowed to be carried by the equipment ground. NEVER EVER.
Older dryer circuits used two hots and a NEUTRAL. The equipment ground was omitted. The NEUTRAL served as both the grounded and grounding conductors (neutral and ground).
It was required to either be part of an SEU cable assembly or be white insulated if part of another cable assembly or in conduit. A bare ground was NEVER used for this purpose.
From what I hear, it was not "the govt sticking it's nose into things" (sorry Mr. conspiracy), it was the govt trying to save copper during WWII as far as I know.
I don't know how this myth ever got started, but it is a shame that it is still being perpetuated to this day.
Current on ANY grounding conductor or grounding electrode conductor is NOT a good thing. And the manufacturer of this heater is certainly NOT allowing even .3A of current to flow on it.