I've seen a few threads on this topic, but no elegant or particularly safe looking solutions.
I got a liftmaster 8500 for my garage door, and I didn't want to mount the little remote light and have a cord running down my wall.
I found that liftmaster/chamberlain make these switches that can be synced up with the opener:
http://www.chamberlain.com/smartphone-control-products/lighting-controls/myq-interior-light-switch
https://www.liftmaster.com/For-Businesses/Accessories/CDO-Accessories/model-823LM
They're both the same exact thing except for the logo, both are around $30 shipped, but the Chamberlain comes with a little 3 button garage door opener remote, so that's what I got.
The only problem is that they're only rated for 2.5 amps of CFL lighting. I have four 8 ft four tube T5 fixtures from Home Depot. That's closer to ~8 amps, and the electronic ballast inrush(probably 200 amps), would weld the relay in the switch closed in short order.
The solution I found was this:
http://www.functionaldevices.com/pdf/datasheets/RIB2401B.pdf
It's a fully enclosed relay rated for 16A @ 277VAC of electronic ballast load. I verified with the manufacturer that it's good for that at 120VAC as well. I got the RIB2401B with the 120V coil for obvious reasons. The coil only draws 47mA, and I'm triggering it with the Liftmaster/Chamberlain switch. Only around $20 shipped. The older data sheets and relay labels make no mention of electronic ballast rating, so I'd stick with new stock(read the label if you're buying on ebay)
I had wired my lights with two switches and 14/3 romex, so that I could turn half of each fixture on. This didn't turn out to be particularly useful to me, but getting rid of that functionality allowed me to repurpose one of the hot wires to constantly power the common terminal on the relay without having to pull new wire.
I went to the first J-Box in the attic and popped a 7/8" hole in the cover to mount the relay and wired it up.
After letting the switch "charge up", everything works fine and the relay in the Liftmaster switch should last just about forever since all it's doing is triggering the RIB lighting relay.
If anyone else is interested in doing the same, I can post up a wiring diagram.
I got a liftmaster 8500 for my garage door, and I didn't want to mount the little remote light and have a cord running down my wall.
I found that liftmaster/chamberlain make these switches that can be synced up with the opener:
http://www.chamberlain.com/smartphone-control-products/lighting-controls/myq-interior-light-switch
https://www.liftmaster.com/For-Businesses/Accessories/CDO-Accessories/model-823LM
They're both the same exact thing except for the logo, both are around $30 shipped, but the Chamberlain comes with a little 3 button garage door opener remote, so that's what I got.
The only problem is that they're only rated for 2.5 amps of CFL lighting. I have four 8 ft four tube T5 fixtures from Home Depot. That's closer to ~8 amps, and the electronic ballast inrush(probably 200 amps), would weld the relay in the switch closed in short order.
The solution I found was this:
http://www.functionaldevices.com/pdf/datasheets/RIB2401B.pdf
It's a fully enclosed relay rated for 16A @ 277VAC of electronic ballast load. I verified with the manufacturer that it's good for that at 120VAC as well. I got the RIB2401B with the 120V coil for obvious reasons. The coil only draws 47mA, and I'm triggering it with the Liftmaster/Chamberlain switch. Only around $20 shipped. The older data sheets and relay labels make no mention of electronic ballast rating, so I'd stick with new stock(read the label if you're buying on ebay)
I had wired my lights with two switches and 14/3 romex, so that I could turn half of each fixture on. This didn't turn out to be particularly useful to me, but getting rid of that functionality allowed me to repurpose one of the hot wires to constantly power the common terminal on the relay without having to pull new wire.
I went to the first J-Box in the attic and popped a 7/8" hole in the cover to mount the relay and wired it up.
After letting the switch "charge up", everything works fine and the relay in the Liftmaster switch should last just about forever since all it's doing is triggering the RIB lighting relay.
If anyone else is interested in doing the same, I can post up a wiring diagram.