How much should I expect to pay for electricity in pole barn

Skdrcr23

Active member
Joined
Jul 29, 2015
Messages
40
Hello, I'm looking for some advice on running
Electricity to pole barn. It's about 100 feet from
My house. I plan on running a 60 gal 5gp compressor
And 2 post lift. I've searched a little bit on using the
Mhf 2 2 2 4 and 90 amp breaker and what not but
It may be just a little over my skillset to accomplish myself
 
To avoid these ads, REGISTER NOW!

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
You've already got the best low-cost recipe . . . MHF Al 2-2-2-4 which is about $1.50/ft. Then you would also have 2" plastic electrical conduit and the 90 degree sweeps for buried conduit coming out of ground.

Negotiate with your electrician that you'll dig trench and put in the 2" conduit and he'll pull wire and terminate, plus subpanel in garage. You'll also need 2 ground rods at the garage tied to the subpanel. The garage subpanel can just be matching 100A brand that you have in the house. Limiting breaker of 90A would be in the house feeding the MHF Al 2-2-2-4 to garage.

Dig the trench deeper than AHJ requires and put 2" electrical conduit on bottom. Then backfill 12" and install a 2nd conduit for low voltage stuff like CATV/internet/phone/security/intercom/etc.

UPDATE GJ Profile with a Location so you'll get best advice for country.
 

Pwrgeek

Well-known member
Joined
Oct 18, 2015
Messages
288
Location
Texas USA
Depends on what you have them do. Couple scenarios and what you would pay here for them.

You trench and install conduit. They pull and terminate wire and install sub panel. You install all circuits from sub panel to devices. They provide wire and panel. Your cost (here) about $1500 - $2000.

Same as above only they do the trench and conduit. Your cost $3000 - 3500.

They do the whole thing including a bunch of outlets and lights. All the point of use devices you mention. Your cost prob $10k plus.


Sent from my iPhone using Tapatalk
 

cajunfirehawk

Well-known member
Joined
Nov 29, 2011
Messages
2,566
Location
Ms Gulf Coast
I just ran mine or should say I had a licensed electrician run mine; 85' run to a 100 amp sub-panel he installed, labor and materials, $1k, YMMV.
20160220_114736_zpsys6orfc4.jpg
 
Last edited:

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
I just ran mine or should say I had a licensed electrician run mine; 85' run to a 100 amp sub-panel he installed, labor and materials, $1k, YMMV.

^ ^ ^ WTH . . . . HOW ??? You "secretly" pay with LOTS of 409 ???? :pimpflash . . :evil:
. . .
. . . . . you know . . . . for "medical" . . . . !!! ;)
 
OP
S

Skdrcr23

Active member
Joined
Jul 29, 2015
Messages
40
Thanks for the info guys. I think I will probably do the trench and conduit. Can the Mhf ai 2 2 2 4 be ran directly in the house to 90a breaker or will I need junction box?
 

Pwrgeek

Well-known member
Joined
Oct 18, 2015
Messages
288
Location
Texas USA
Thanks for the info guys. I think I will probably do the trench and conduit. Can the Mhf ai 2 2 2 4 be ran directly in the house to 90a breaker or will I need junction box?


Only requirement on MHF is that it must be in conduit anywhere above ground or inside a building.


Sent from my iPhone using Tapatalk
 
OP
S

Skdrcr23

Active member
Joined
Jul 29, 2015
Messages
40
So it's best to run conduit the entire length of the Mhf from house to shop then? 90amp breaker at house and
100 breaker at subpanel in shop. Why do I need 2 grounding rods vs just 1? Could I use 100 breaker on
Both sides if I can find 90a breaker to match the brand of my main panel? Also is it better to run single strand 14 Guage wire to recepticles vs romex since wire will be exposed in shop?
 

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
{A}So it's best to run conduit the entire length of the MHF from house to shop then? 90amp breaker at house and 100amp breaker at subpanel in shop??

{B}Why do I need 2 grounding rods vs just 1?

{C}Could I use 100amp breaker on both sides if I can't find 90amp breaker to match the brand of my main panel?

{D}Also is it better to run single strand 14 Gauge wire to receptacles vs Romex since wire will be exposed in shop?

I'm not a sparky, but based on hundreds of GJ threads with same questions that GJ Sparky's answered . . .
{A} Yes , Yes , Yes. Bury the MHF 2-2-2-4 deep in trench in conduit so you can backfill and add another conduit with low voltage wire like CATV, internet, phone, security, etc.
{B} Because it's code requirement.
{C} No. Need 90A breaker in house as that's maximum allowed to power the MHF Al 2-2-2-4 out to subpanel in garage.
{D} Your choice. What's there now?? Sheetrocked walls already or open studs?? Let's see PIC's of what's in garage now.

Finally, UPDATE GJ Profile with Location as electrical codes vary by country.
 
To avoid these ads, REGISTER NOW!

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
^^^ Your Location Is? ^^^

Sometimes a Ditch Witch works great. Where I live the ground is basically boulders... so that requires a mini excavator or a back hoe for the trench, and that adds $$$$ real quick.

I was quoted $2800 to pull a permit, trench 100 ft from meter box to barn, install 100 amp service with Square D breaker panel, install (1) outside light and (1) inside outlet.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,014
Location
Modesto, CA
So it's best to run conduit the entire length of the Mhf from house to shop then? 90amp breaker at house and
100 breaker at subpanel in shop. Why do I need 2 grounding rods vs just 1? Could I use 100 breaker on
Both sides if I can find 90a breaker to match the brand of my main panel? Also is it better to run single strand 14 Guage wire to recepticles vs romex since wire will be exposed in shop?


Indiividual conductors will need to be in conduit....
 
OP
S

Skdrcr23

Active member
Joined
Jul 29, 2015
Messages
40
Open studs. I was thinking of using 12 2 for the lights and
14 2 for recepticles. I'm still a few months away from doing anything. Still kind of just learning everything right now
 

Attachments

  • 20160215_160340.jpg
    20160215_160340.jpg
    138.7 KB · Views: 67

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,548
Location
East Bay SFO
Open studs. I was thinking of using 12 2 for the lights and
14 2 for recepticles. I'm still a few months away from doing anything. Still kind of just learning everything right now

Do you really intend to run 14 ga. wire for receptacles? Sometimes guys run 14 ga. for lights especially if they are running low wattage LED fixtures. But please spend a few extra pennies and run 12 ga. to your receptacles and protect the circuits with 20 amp breakers. You will thank me later. :D
 

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
^ ^ ^ This. Run 12 gauge wire for all outlets and 20A circuit breaker. That way you can run a 120v air compressor and not trip the breaker/overload the wire.

Only use 14 gauge for lighting wiring on separate circuit(s).
 

Pwrgeek

Well-known member
Joined
Oct 18, 2015
Messages
288
Location
Texas USA
^ ^ ^ This. Run 12 gauge wire for all outlets and 20A circuit breaker. That way you can run a 120v air compressor and not trip the breaker/overload the wire.



Only use 14 gauge for lighting wiring on separate circuit(s).


I ran all 14 ga for general use outlets and 12 for point of use tools (table saw, drill press, mini mill). One thing I did do though is run all circuits so that there are two duplex receptacles in each box and they are on separate circuits. 99.9% of 120V devices will run on 15A. You get into trouble when you end up with multiple large draws on a single circuit.


Sent from my iPhone using Tapatalk
 

matt151617

Well-known member
Joined
Dec 17, 2011
Messages
488
Location
New Jersey
Are you doing the interior wiring yourself? If so, you can definitely run the wire from the house panel yourself. It's still adding another circuit on, just like adding an outlet circuit. Put in more outlets than you think you'll need! I would also add a 240v outlet somewhere in the garage.

Whatever you decide on, make sure you pull the proper permits (now), and get it inspected.
 
OP
S

Skdrcr23

Active member
Joined
Jul 29, 2015
Messages
40
I have a bryant main panel house. Can I use an Eaton 100a sub panel in detached building. I believe the breakers/panels are compatable just making sure.
 

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
^ ^ ^ Post up PIC's of house main panel that you plan on adding breaker to feed the garage.
. . . . . PIC with cover on . . . . and . . . PIC with cover off.

Sparky's also will want your . . . . COUNTRY . . . Where you at ??

UPDATE GJ Profile with a Location.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,014
Location
Modesto, CA
I have a bryant main panel house. Can I use an Eaton 100a sub panel in detached building. I believe the breakers/panels are compatable just making sure.

Theres no code or requirement that says u have to match the brand of subpanel to the brand of main panel...
 