I want pre wire for a Mr Cool 36K unit. It looks like I need to run 10/2 wire to a AC disconnect. Am I on the right track?
I am installing the same unit and I will run 10/2 NM and put it on a 30A breaker.
Use the 35A breaker, your better off.
10 Gauge NM-A is rated for 30A max load per the NEC. A 35A breaker on 10 Gauge wire would be a code violation.
In most cases it's fine, just depends what the equipment label says.10 Gauge NM-A is rated for 30A max load per the NEC. A 35A breaker on 10 Gauge wire would be a code violation.
This is why you are a handyman and not an electrician.10 Gauge NM-A is rated for 30A max load per the NEC. A 35A breaker on 10 Gauge wire would be a code violation.
This is why you are a handyman and not an electrician.

LOL, that's why I'm here.I was gonna say that but held my tongue![]()
Use the 35A breaker, your better off.
No it is not, HVAC is one of a number of types of equipment that is allowed to use wire & overcurrent device combos that are not permitted for normal branch circuits, in fact if the OP wished, & 12 AWG THHN/ THWN & 35A fuse could be used & still be code compliant. You wire for the minimum & use the maximum size fuse or circuit breaker allowed on the label, the 125% has already been calculated also. It's always funny when home inspectors complain about 10 AWG w/ a 40A breaker on A/C equipment.In most cases it's fine, just depends what the equipment label says.
This is why you are a handyman and not an electrician.