20 Amp Circuit with 15 Amp Light Switches

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
So I'm out in the barn yesterday and noticed the light switches that the Sparky's installed are 15 amp..... Opened the electric panel and the circuit has a 20 amp breaker :headscrat

Checked and all romex is 12 gauge on the circuit.


  • Either the switches should be changed to 20 amp
or
  • The breaker should be changed to 15 amp

Am I right or is there some NEC rule that I am not aware of?

Thanks,

John
 
To avoid these ads, REGISTER NOW!

klassenl

Well-known member
Joined
Feb 20, 2016
Messages
713
Location
Southern Alberta
Really? Why is that? U have a code reference that says otherwise?

BTW arguing with a licensed contractor that knows his stuff wont end well for u.

Well if I start quoting code it won't help since we live in different jurisdictions.

I have worked for 3 "licensed contractors that knows his stuff" and I have won arguments about code with all three.

I asked my inspector recently about this and he told me that switch hs to be rated for the circuit it is connected to (remember different parta of the world). I would tend to agree with him even though logic says it should be related to the load. But legal issues, liability etc.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Well if I start quoting code it won't help since we live in different jurisdictions.

I have worked for 3 "licensed contractors that knows his stuff" and I have won arguments about code with all three.

I asked my inspector recently about this and he told me that switch hs to be rated for the circuit it is connected to (remember different parta of the world). I would tend to agree with him even though logic says it should be related to the load. But legal issues, liability etc.

I missed the fact that youre in canada so none of this matters. US code is different than canada on this subject
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Well if I start quoting code it won't help since we live in different jurisdictions.

I have worked for 3 "licensed contractors that knows his stuff" and I have won arguments about code with all three.

I asked my inspector recently about this and he told me that switch hs to be rated for the circuit it is connected to (remember different parta of the world). I would tend to agree with him even though logic says it should be related to the load. But legal issues, liability etc.

You should have preface your initial comment with "In Canada,".
 

MikeF2316

Well-known member
Joined
Dec 29, 2012
Messages
9,605
Location
Thornhill, ON
And yet, we (in Canada) buy the same lights with 9-12" of 18 gauge pigtails on them as you guys can. So that part of the circuit would have trouble with 15 A flowing through. And yet our houses don't burn down.

This is the kind of light I'm talking about:

attachment.php
 

Attachments

  • light.jpg
    light.jpg
    52.1 KB · Views: 1,095
OP
L

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,114
Location
SE MI
It may meet code ... but it is not "logical".

Of course I put 5-20 outlets in the ends of my 12/2 - 20A circuits when I rewired the garage.
 

ssbtech

Well-known member
Joined
May 1, 2012
Messages
420
Location
BC, Canada
I like the logic of sizing a switch for the load, but should the breaker not be the weakest link in the chain?
 

ssbtech

Well-known member
Joined
May 1, 2012
Messages
420
Location
BC, Canada
I don't see how a 3 amp bulb could fail in such a way that it would draw more current than the wiring can handle.

If the goal of the breaker is to protect the wiring from overheating and burning down your house, putting a 20A load on a 15A light switch on a 20A circuit doesn't sound safe to me.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
I don't see how a 3 amp bulb could fail in such a way that it would draw more current than the wiring can handle.

If the goal of the breaker is to protect the wiring from overheating and burning down your house, putting a 20A load on a 15A light switch on a 20A circuit doesn't sound safe to me.

maybe u should write a letter to the code making panels about this.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
I don't see how a 3 amp bulb could fail in such a way that it would draw more current than the wiring can handle.

If the goal of the breaker is to protect the wiring from overheating and burning down your house, putting a 20A load on a 15A light switch on a 20A circuit doesn't sound safe to me.

It's not permitted to do what your saying, if the switch is sized to the load it is fine, a 15A switch w/ a 20A load is not, just because the circuit is 20A does not mean the load is 20A.
 

ssbtech

Well-known member
Joined
May 1, 2012
Messages
420
Location
BC, Canada
The number of people I see who have put non-dimmable CFLs on incandescent dimmer switches should give you an indication of the likelihood that people will be checking the current rating on their light switches.

In all likelihood, nobody is sticking 20A worth of lights on a 15A switch. But all it takes is some schmuck to screw in an adaptor and run a heater off a bulb socket alongside 10A of lights.

I don't know about you, but it seems to me that this is what the breaker is designed to protect against.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
We don't put 20A loads on 15 switches. The sparky wires limited fixtures to it and some cases 15a recept Yes fixtures have smaller wire, again limited load.
 

jdieter

Well-known member
Joined
Nov 17, 2007
Messages
320
Location
Northern Indiana
Doesn't this question have to be taken in the complete context of NEC wiring practices. Switches are inside approved enclosures. Branch circuit wiring in a residential setting (which I'm assuming the OP is referencing) can be installed almost anywhere in a residence. The NEC is after all a fire/safety code, i.e. branch circuit wiring laying on top of or penetrating wood structure without the correct overcurrent protection is a fire hazard. A branch circuit switch experiencing overcurrent in an approved and correctly installed enclosure would not be considered a fire hazard. But if you succumb to the paranoia change all your table lamps on 20A breakers to 12 ga. & 20 amp switches as well as all the pigtails on your lighting fixtures or install an appropriate in-line fuse at each device.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Its a good thread, its got good stuff in it. Its a good question. My smart *** remark should be disregarded but for not one wireman or inspector wondered why. I tease lakeroadster a bit but I got a lot of respect for engineering. I didn't always but today understand someone with a mind greater than mind has figured it out ahead of me and I got to put mostly off the shelf pieces together like the pictures.
 
OP
L

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
You are an expert, its different.


........ But all it takes is some schmuck to screw in an adaptor and run a heater off a bulb socket alongside 10A of lights.

I don't know about you, but it seems to me that this is what the breaker is designed to protect against.

Agreed.

I changed the breaker from a 20 amp to a 15 amp. While I understand the logic, and that it meets NEC Specifications, I think it unwise for the code to allow a "weak link" other than the over current device.
 
Last edited:

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Specifications, I think it unwise for the code to allow a "weak link" other than the over current device
Ok, you think its unwise? You really figure to be that smart and the rest of the whole industry are idiots until you happened along? None of these people know what they are doing till you wired a ,,, or had a garage wired?
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
I ran all 12 AWG, my switches and outlets came in the 10 pack, cheap. I have yet to have to replace one. I only have one thing here that would fully load a 20A circuit anyway. That would be plugging in the whole 24x8.5 ft race trailer with the AC on full blast.
 

Radix2

Well-known member
Joined
May 28, 2014
Messages
1,853
Location
the thumb!, MI
Ok, you think its unwise? You really figure to be that smart and the rest of the whole industry are idiots until you happened along? None of these people know what they are doing till you wired a ,,, or had a garage wired?

Code is a minimum. He is perfectly capable of determining where or if he would like to do more.

No different than putting in R-19 when the code says R-13.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I am usually trying to tell some handymans,,, don't fuk with it, I know a couple mechanical genius types, one of these days, pow or,,, the next question will be,,,, why does my little compressor??/ Or chop saw do this and the last critical info to the thread will be,,,, I screwed with the circuit after the electrician left.
I read a lot too, can write the end to a lot of stories,,,,,,,,,,,,,, but my own will probably be,,, he finally fugged up,,,, ha I try to follow the instructions, if I don't know why,,,,,, I try to follow the instructions and usually after a while I find out why I was sposed to follow the instructions.
 
OP
L

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
Ok, you think its unwise? You really figure to be that smart and the rest of the whole industry are idiots until you happened along? None of these people know what they are doing till you wired a ,,, or had a garage wired?

I never said anyone was an idiot... those are your words.

As a matter of fact, I even thanked the fellas for their input.

I asked a question, got a lot of answers, and did what I think is prudent.
 
Last edited:

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
You did, sorry. It really was a good question. My point being that I got to wonder if I was the only one stumbled along and thought of this? The code is well reasoned, a lot of stuff that wouldn't occurred to me and not as the system it is,,, and first thing when I get an epiphany is would they let millions of these every day be installed wrong?
@nd, it does explain in it that it is for safety and property and not a design for efficiency etc but it doesn't mean all the minimum standards arte insufficient. Lots of equipment has run a long time with a wire 2 sizes too small. The 5 hp motor, some with a 22 run, wont overheat a 12 cable.
 

53Sparky

Well-known member
Joined
Feb 22, 2015
Messages
175
Location
Northglenn, CO
There is NOTHING wrong with replacing the 20A breaker with a 15A breaker for your peace of mind.

As a Master Electrician with 17 years of experience in your home state of Colorado, I can say with confidence that there wouldn't have been a risk of failure if you had left the 20A breaker in, and that it is common practice for your electrician to have done that.

The question is a completely legitimate question and it was good that you asked it.

What has always bothered me more than using 15A switches on a 20A circuit is that it is also completely acceptable to use 15A receptacles on 20A circuits as long as it isn't a dedicated circuit with only one opening. That one has been tougher to figure out why it's acceptable from a logic perspective because the load isn't fixed.
 

MikeF2316

Well-known member
Joined
Dec 29, 2012
Messages
9,605
Location
Thornhill, ON
Here's a real world example why this isn't a good idea. Back in the '80s I had a summer job at a place where the office lights were turned off at the breaker panel. Each 15 amp breaker did 9 fixtures, 4 40 watt florescent tubes per fixture. So that's 36 tubes x 40 watts = 1440 watts. 1440 watts / 120 volts = 12 amps. The lights all started tripping breakers. In our area started blowing the breaker, starting once a day, then getting more frequent. So we took a couple of tubes out, problem solved. For about a month. So a couple more tubes came out. I was there 4 months, we took out 6 tubes total. While I suspect the lamps and ballasts were drawing more current as they aged, I don't know for sure. So if these lights were on a 20 amp circuit with a 15 amp switch, they would have been using more current than the switch was designed for.

Of course in Canada, the CEC only allows 15 amp breakers for lights. Hmmm.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
What has always bothered me more than using 15A switches on a 20A circuit is that it is also completely acceptable to use 15A receptacles on 20A circuits as long as it isn't a dedicated circuit with only one opening. That one has been tougher to figure out why it's acceptable from a logic perspective because the load isn't fixed.
Because this applies to more than one receptacles on a circuit. A duplex receptacle is TWO 15A receptacles on a single device yoke. Pretty much all 15A duplex receptacles are rated for 20A feed-thru. GFIs have this printed right on them.
"15 amp" is NOT the rating of the device, it's the rating of each of the two receptacles on the device.
 

bczygan

Well-known member
Joined
Nov 4, 2009
Messages
22,002
Location
DETROIT! Arsenal of Scrappers
The number of people I see who have put non-dimmable CFLs on incandescent dimmer switches should give you an indication of the likelihood that people will be checking the current rating on their light switches.

In all likelihood, nobody is sticking 20A worth of lights on a 15A switch. But all it takes is some schmuck to screw in an adapter and run a heater off a bulb socket alongside 10A of lights.

I don't know about you, but it seems to me that this is what the breaker is designed to protect against.

Hey!.....Who you calling a schmuck?:lol_hitti
 
Last edited: