I used to work for a plastic molding company. we made lots of products including ABS and PVC fitting.
I have never really see a PVC pipe fail when used with air and I have seen several people use them. so, with that I had never understood why they would not hold up to the air pressure.
OK, back to the top. I went to work for a plastic company and we had a tester for pressure testing fittings and such. the tester is enclosed for safety so I decided to put it to the test.
took 2 fittings with a piece of pipe between them and then also took an expansion repair coupling.
installed the item, bled the air out and pressure testing the item. It is amazing to see those items take anywhere from 3-10 times the rated pressure. you can even see how the item expanded or streched a bit before failing. some wouldnt even fail before we maxed the testing limit.
ok, so I repeated a couple of the tests without bleeding the air. this means that there would be mostly air in the pipe or fitting with the pump pressurizing it by pumping water into the system.
depending on the item they failed EXPLOSIVELY at between 1/3rd and 1/2 of the rated pressure.
I can tell you that was one fun job. part of my job was to test and fail parts so we can document as well as taking care of certification testing.
my boss nick named me the 'manager of breaking ****'
so forget all you hear about theory of what it may do. I can tell you what it WILL do when tested.
typically test presure it 2.5 times rated pressure
bob
Bob, your tests only include new fittings that have not been exposed to fatigue from expansion due to pressure changes nor due to aged PVC that can become brittle, especially when exposed to UV rays.....although that isn't typically common in a garage. PVC may be fine for a little while, but after it expands and contracts due to pressure changes the fatigue will cause hairline cracks....which will cause a violent explosion with little PVC shreds as shrapnel. Factor of safety is commonly used when rating anything, and 2-3 is a common range for FOS.
From an OSHA article:
Information Date: 19880520
Record Type: Hazard Information Bulletin
Subject: The Use of Polyvinyl Chloride Pipe in Above Ground Installations.
"When PVC piping explodes, plastic shrapnel pieces are thrown in all directions."
"'We're seeing more incidents of explosive failure, and we're citing more employers for using PVC air system piping,' said Paul Merrill, senior safety inspector in L&I's Spokane office."
"'It's probably just a matter of time before someone gets seriously injured in one of these explosions unless everyone pays more attention to the manufacturer's warnings,' Merrill said.
Last year, a section of PVC pipe being used for compressed air exploded 27 feet above a warehouse floor. A fragment of the pipe flew 60 feet and embedded itself in a roll of paper. Fortunately, nobody was in the area at the time.
A PVC pipe explosion in a new plant in Selah broke an employee's nose and cut his face."
"PVC piping buried 3 feet underground at a Yakima manufacturing plant exploded, opening up a crater approximately 4 feet deep by 3 feet across."
"Only one type of plastic pipe has been approved for use with compressed air. That pipe, Acrylonitrile-Butadiene-Styrene (ABS), is marked on the pipe as approved for compressed air supply."
http://www.osha.gov/dts/hib/hib_data/hib19880520.html