I have some metallux 6 bulb fixtures to install in new garage.

I was told to hang one foot below ceiling which will be drywall.

I understand to suspend lights with chain and hooks

What is the best way to concealing the wiring going into fixture?

Should I mount ceiling boxes? Or just drop romex thru drywall?

I have 6 fixtures, I am running 2 circuits.
In circuit will be the 2 bulb ballasts in all 6
The other circuit will be the 4 bulb ballasts

So there will be a few wires.

Any advice is appreciated. The ceiling is wide open now and rough in inspection is coming up in a few days.
 
To avoid these ads, REGISTER NOW!

diskreet

Active member
Joined
Sep 13, 2016
Messages
39
Location
PA, USA
I drywalled, but even if I didn't I'd do the same; Get the depth adjustable new work boxes, and attach them where you want the lights. If you insulate and drywall, they are all set. If not, they still properly contain the wiring. I did leave a bit of slack in each wire in/out of the box so I could adjust the depth without any snagging or pulling of wires.

I also didn't hang my LED fixtures from chains - I just used an S hook directly on the mounting point. Just enough space between the ceiling and fixture to hold the extra wire.
 
OP
R

rockwvu

Member
Joined
May 29, 2009
Messages
9
I drywalled, but even if I didn't I'd do the same; Get the depth adjustable new work boxes, and attach them where you want the lights. If you insulate and drywall, they are all set. If not, they still properly contain the wiring. I did leave a bit of slack in each wire in/out of the box so I could adjust the depth without any snagging or pulling of wires.

I also didn't hang my LED fixtures from chains - I just used an S hook directly on the mounting point. Just enough space between the ceiling and fixture to hold the extra wire.


There will be insulation and drywall.
My question is what to do with the wire 12" between ceiling and light fixture.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,716
Location
NW Iowa
Put a box on the ceiling then flex to the light or sleeve the wire in some flexible conduit if you don't want to have a box on the ceiling.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
If a fixture is chain mounted, the wire will need to be stranded.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
Can you please expound on this? Is it code required?


Sent from my iPad using Tapatalk

410.56(E)

"(E) Stranded conductors shall be used for wiring on luminaire chains and on movable or flexible parts."
 

cory58

Well-known member
Joined
Dec 23, 2015
Messages
234
Location
Charlotte, NC
410.56(E)

"(E) Stranded conductors shall be used for wiring on luminaire chains and on movable or flexible parts."

Thank you! I learn something almost every time I visit GJ. Timely info, since I will hopefully be starting on the lighting for my garage soon.

Cory
 

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
Thanks Norcal. I had wondered about the flex issue and asked the electricians at our building how they hung lights. They run MC along one chain and apparently that passes inspection. It's probably not a big deal but I was planning to run black cord (SOOW?) to the ones I will install soon.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
Unless the MC cable is stranded, it's not code compliant to use it for chain mounted fixtures.
 