Box for connecting SER to MHF

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,328
Location
Alexandria, VA
This is for installation of a QO sub-panel in my garage, breakered at 60 amps in the main panel.

Inside the house: I have 2-2-2-4 SER running from my main panel across the house to my exterior basement wall and ending inside an unfinished storage closet.

Outside the house: I then have 2-2-2-4 MHF buried in conduit, running from my detached garage over to the point where I will drill through the basement wall. The MHF cable is rated for USE-2 RHH RHW.

My plan was to have the MHF come through the wall in 2" conduit, and mount an LB box on the inside of the wall. I would then come down the wall with the SER and connect the SER to the MHF inside the LB box. Then I looked at how small the LB volume is, considering the size of the wiring.

Question: Can the 2" LB serve as a junction box for the 2-2-2-4? Do I need more space to connect the SER to MHF, or is another type of box needed to meet code requirements?

Thanks,

Bruce
 
To avoid these ads, REGISTER NOW!

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
A LB can serve as a junction box if it has the cubic inch capacity stamped on it. I wouldn't want to splice MHF in one though for sure. I would come into a large plastic box for that. I think I spliced my 2-2-2-4 SER in the basement in a 8x8x6 or something close.
 
OP
7

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,328
Location
Alexandria, VA
I have concluded that it definitely makes more sense to use a much larger box than the 2" LB. The junction box will be mounted on an unfinished basement wall under the stairs, so box size doesn't really matter for aesthetics.

Bruce
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
A 2" LB conduit body is to small to splice 2-2-2-4. Basically if you have 2" conduit entering a junction box the box needs to be 6 times the conduit size which will be a 12" X 12" box.
 
OP
7

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,328
Location
Alexandria, VA
The 2" conduit is probably a little bigger than I really needed, but I used that size to make the MHF easier to pull.

Do you really think I need a 12" X 12" box just to connect four wires (2-2-2-4)?

I figured an 8" X 8" box should be big enough - but maybe not. One advantage of the 12" X 12" box is that its also 6" deep (instead of 4"), so it has a lot more capacity than the smaller box.

Bruce
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,071
Location
Modesto, CA
The 2" conduit is probably a little bigger than I really needed, but I used that size to make the MHF easier to pull.

Do you really think I need a 12" X 12" box just to connect four wires (2-2-2-4)?

I figured an 8" X 8" box should be big enough - but maybe not. One advantage of the 12" X 12" box is that its also 6" deep (instead of 4"), so it has a lot more capacity than the smaller box.

Bruce

What are you gonna use to splice the wires?

If insulated tap connectors, they take a lot of room and you will be glad you have that extra 2" of depth when having to cram it all back in the box.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Do you really think I need a 12" X 12" box just to connect four wires (2-2-2-4)?

I figured an 8" X 8" box should be big enough - but maybe not. One advantage of the 12" X 12" box is that its also 6" deep (instead of 4"), so it has a lot more capacity than the smaller box.

Bruce

A 8X8X4 box is actually large enough for the 2-2-2-4 splicing but the controlling factor is the size of conduit feeding the box. If you had used 1.25" conduit the 8X8X4 would be okay, but the 2" conduit could hold up to 5 or 6 #2/0 wires and the 8X8X4 box is too small for #2/0. The code makes you size the box comparatively to the conduit size so you aren't cramming too much wire in a junction box relative to the capacity of the conduit. I hope that makes sense.

Edit: This is for junction boxes containing #4 and larger conductors. See NEC 314.28
 
Last edited:

terabitdan

Well-known member
Joined
Jul 16, 2016
Messages
152
I'm curious, anything wrong with the OP using a bushing to enter the box as 1 1/4"? Say coming out the back of the outside LB wth 1 1/4" conduit into the inside junction box.


Sent from my iPhone using Tapatalk
 
OP
7

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,328
Location
Alexandria, VA
I considered the same question about downsizing the conduit size, since I really only needed 2" conduit to make the pull easier. However, I decided I will pick up a 12x12x6 box today and see how well it fits. The junction box is high on the wall in the back of a basement closet under the stairs, so its not like it will really get in the way.

I had glanced at NEC 314.28 a couple of times, but never realized that for large gauge wires the conduit size used is as significant as the number of wires in the box. I am more used to standard house wiring, where the number of wire connections and wires is the main factor for calculating box size.

Bruce
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I've used both 8" & 12" boxes for the splices on 2-2-2-4 and needless to say the 12" is a lot easier than a 8". The 8" box is okay but if you used 2" conduit I wouldn't reduce the conduit to 1.25" just for the purpose to get by with the 8" box if space is not an issue for the 12". The only thing is the price of a 12" box.
 
OP
7

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,328
Location
Alexandria, VA
I picked up the 12"x12"x6" box today and it was $35. Not much more than the smaller box.

I also picked up a 2" conduit box adapter, and the info says it is used to attach PVC conduit to the box. However, its so simple (and cheap) that I want to make sure I have the right fitting.

The 2" conduit will be coming through the brick wall into the basement, and I plan to mount the junction box over the hole in the wall. If I mount the conduit adapter and conduit onto the back of the box, I can just stick the conduit through the wall, and then make the final connection of conduit outside. Does this make sense, or am I missing something?

Thanks,

Bruce
 

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
Sounds fine.

You have a few mm of 'adjustment' in terms of wet PCV glue, to get everything 'precise'- if there is an LB on the outside, then this will be flush against the wall- and on the inside the back of the box will 'just; sit on the shoulder of that 2" fitting. I'd mount inside first, locknut to the box- then finish up outside.
 

Jon_E

Well-known member
Joined
Aug 19, 2015
Messages
575
Location
Southwestern Vermont
I spliced 2-2-2-4 SER to 2-2-2-4 MHF in a j-box mounted to the foundation of my house. I used 2" conduit for the MHF and was informed by the electrician assisting me that I needed a 12" x 12" box. It's a little out of place but not bad, but it is definitely the right size.
 