The Concrete Underground's Guide to Floor Slabs
ConCretin
Central Maine
There have been many GJ discussions on garage slabs but I'm hoping a simple outline will be helpful to those who haven't done a lot of concrete work and are getting ready to place a slab. So let’s lay out the basics that will give the average guy a good shot at a great slab.
Base - What’s under your slab is just as important as the slab itself. Slabs on grade are thin, non-structural surfaces that can’t span very far over soft ground. If the ground under your slab can't support the weight you put on your slab, it will crack.
Start by removing all organics and top soil. It's a good idea to proof roll the sub grade by running a roller or compactor over it. If the soil is dry, stable and compact-able, you can go ahead and place your slab or if you need the bring the grade up, you can start adding base material. If the sub grade is soft, wet, contains silt or expansive clays, additional steps may be necessary.
Even if the native soils are fine, it's good practice to add a few inches of granular material to provide a capillary break and a surface that can withstand rain and construction traffic without getting muddy and rutted.
Base materials must be well compacted to provide uniform support to the slab. Your base should be a granular material such as crushed stone, sand or what we in the Northeast call gravel; a blended material with a range of aggregate sizes including fines that compacts without voids. A maximum aggregate size of 3/4" in the top lift will make it easier to fine grade.
Place and compact the material in 6" lifts. For a free-standing slab, extend the base far enough to ensure compaction and good support under the slab edges. Grade your base to 1/4” +/-to keep your slab thickness consistent.
Slab Thickness - Since you are building on a solid base, a 4" slab is more than adequate for most uses. While it's true that making a slab thicker makes it stronger, it's just not necessary since the base is carrying the load. Your slab would have to be several times thicker to be truly self-supporting so you aren't getting any real benefit from a few extra inches of concrete.
With that said, if you plan on installing a two post lift, I'd consider a 5" slab. While most manufacturers specify a minimum thickness of around 4", there are always variations in elevation in the base and top of concrete, which can result in thinner areas. An inch of concrete only adds .003 cy per sf and will ensure you have enough concrete when you drill your anchor holes.
Formwork - Use lumber that's a little narrower than your slab thickness avoid fighting high spots in the base and set the top to grade by nailing it to your stakes. Avoid anything sticking up so your finisher can screed and finish right over them. Backfill the bottom of your forms to fill any gaps and keep them from getting pushed down if stepped on. Your forms may move during the placement so it's a good idea to run some strings and check for straightness as the concrete goes in.
Grades - Many garage floors are level although some codes require the slab to be pitched to the door. Your slab should pitch to drains and away from the outside face of your garage door to keep water from running back underneath. If you want to minimize birdbaths on your sloped slab, you'll need an 1/8 to 1/4 inch per foot pitch depending on the skill of your finisher.
Vapor Barrier - This is a plastic sheet that goes between your slab and the ground to prevent water vapor from coming through the concrete. While it's always desirable to limit moisture intrusion, it's really only necessary if you intend to apply an adhered floor covering such as epoxy because moisture will interfere with the bond.
There is one potential downside to a vapor barrier that you should be aware of. You could get additional bleed water after concrete is placed, which can cause surface defects if not handled properly. More on that later.
A vapor barrier can be 6 or 10 mil poly but it often gets damaged during construction and degrades over time. A better choice is a 15-mil product such as Stegowrap which will stand a lot more abuse. Seams and penetrations need to be taped to provide a complete seal.
Insulation - In heated structures, particularly with in-floor radiant, a minimum of 2" of rigid board insulation is typically placed under the slab. You can use either XPS or EPS as long as it meets ASTM C578. In cold climates, rigid insulation should also be used vertically on frost walls to keep frost from getting under your slab.
You can protect unheated or floating slabs from frost movement by placing insulation under the slab and extending it out or down to frost depth around the perimeter. The insulation will retain the natural heat from the ground and keep the frost out.
Expansion Material - This is a compressible material that is installed on perimeter foundation walls and penetrations. It allows the concrete to move freely to help prevent cracking. I like to use a closed cell foam with a 1/2" deep perforated strip at the top you can remove and fill with sealant.
Shoot grades, chalk lines and attach the expansion material with spray adhesive. An added benefit is that your finisher can see where grade is, which will help keep your floor flat.
Reinforcing - Concrete is stronger in compression than it is in tension i.e. it's harder to crush concrete than it is to pull it apart. In structural members, reinforcing steel is used to compensate for this lack of tensile strength. Many people assume that using reinforcing will keep their slab from cracking. Unfortunately, it doesn't work that way.
A slab on grade isn't thick enough to carry heavy loads so it 'bends' and transfers the load to the base below. If the base can't support the load, the concrete will crack regardless of how it's reinforced. Unlike the cables in pre- or post-tensioned concrete, standard reinforcing is passive and doesn't come under load until after the concrete has already cracked.
Another common cause of cracking is shrinkage and reinforcing won't prevent shrinkage cracks either. In fact, reinforcing can actually increase the likelihood of cracks by restraining the slab from contracting as shrinkage occurs.
What reinforcing will do is keep cracks from separating, which helps maintain the integrity and levelness of the slab. Think of steel reinforcing as crack restraint rather than crack prevention.
Slab reinforcing can be either rebar or welded wire fabric (WWF), often referred to as wire mesh. They perform the same function but since rebar is more rigid, it's easier to support while mesh is usually less expensive to install.
If using rebar, I’d suggest #3 bars at 18” o.c. supported every 3’ or #4’s at 24” o.c. supported every 4’. When using mesh, I'd recommend a heavier wire such as 6x6-W2.9xW2.9 supported every 3'. Don't let your finisher convince you he can pull the wire off the ground as he places as this rarely works consistently. If you are placing a load bearing monolithic slab, especially in colder climates I'd recommend using rebar including a couple bars in the bottom of the thickened edge. Floating slabs have the potential for more movement and rebar will hold everything together.
You want to support the reinforcing as high as possible in the slab to keep cracks tight but you also need adequate concrete cover and clearance for cutting control joints. This generally places it close to the center of a 4" slab. There are many products available to support your reinforcing such as concrete dobies, metal slab bolster or plastic chairs. Make sure your supports can stand up to finishers walking on them and that they don't poke through your vapor barrier.
Overlap rebar splices a couple feet and tie your mat together well enough to keep it in place during placement. When using mesh, overlap the sheets one square and tie the sheets together. Stagger adjacent runs to minimize the number of sheets intersecting in one spot.
Another option is Fibermesh which consists of fiberglass strands that are mixed in with the concrete. Fiber is often discussed as an alternative to steel reinforcing, but it actually performs a different function. Fibermesh adds some tensile strength to concrete to minimize early age shrinkage cracks thereby reducing or eliminating the need for control joints. Fiber doesn't significantly increase the load bearing capacity of your slab and unlike steel reinforcing, it won't hold cracks together once they occur.
There are advanced types of fiber called macro fiber or steel fiber that not only limit cracks but like rebar, actually restrain cracks from getting wider. These products are expensive and have downsides of their own such as clumping and finishing issues. They have their uses but unless you know what to ask for and your finisher has experience using these products, I'd steer clear of them.
To summarize; If you want to minimize or eliminate control joints, use fiber. If you don't mind control joints and want the peace of mind that comes from steel holding everything together, use wire or rebar. If you have a solid, stable base you can even forego reinforcing entirely and save some money.
Concrete - Most concrete is what's called ready mix. Trucks are loaded at a batch plant with aggregates, cement, water and various chemicals called admixtures. The concrete gets mixed in the truck's drum on the way to the job site.
Concrete mixes are classified by their projected compressive strength at 28 days, which is determined by the ratio of water to cement. The more cement that is used relative to the mix water, the higher the strength will be. Since a certain amount of water is needed to make the concrete flow, more cement is needed to provide higher strengths.
Many suppliers replace some cement with finely ground fly ash or blast furnace slag. These materials slow the set a bit but otherwise behave the same as cement and aren't a concern.
The amount of mix water in concrete is typically measured using a slump test. To measure slump, a 12" tall, tapered steel cone is filled with concrete and then slowly lifted off. The distance the concrete drops is referred to as it's "slump". The advertised compressive strength is usually based on the amount of water that will produce a 4" slump. Because of the correlation of water and viscosity, slump is commonly used to describe how wet or flowable the concrete is. For example, a 3" slump is stiff and hard to work with while a 9" slump flows easily.
It's advantageous to limit water but it's also important to have a workable mix to get a good slab. Dragging around a 4" slump is hard work. The best way to avoid killing your finisher or having him add water the second you turn around is to order a mid-range water reducer. This chemical admixture will give you a 6" slump with less water than normally required for a 4" slump.
While you don't need high compressive strength from a structural standpoint, you do want a durable surface. As I mentioned earlier, a higher strength mix will contain more cement which will help provide a stronger surface. Most residential concrete falls in the 3000 psi range. For a hard working garage slab, I'd go with at least 4000 psi.
3/4" aggregate is typical. The smaller the aggregate, the more shrinkage so stay away from 3/8" mixes. If you really want to minimize shrinkage, you could go with 1 1/2" aggregate but it is a little harder to work with.
Air entrained concrete contains a chemical admixture that forms millions of microscopic air bubbles that help the concrete resist damage from moisture in freeze/thaw conditions. Avoid using air entrained concrete with interior, steel troweled finish especially in warm weather. Air entraining admixture slows down bleed water and if the surface is sealed with steel blades too soon, it will pool under the surface and create voids. This leads to delamination as the thin layer of concrete above the voids spalls off. Unless your finisher is experienced using it, air entrained concrete is best left to exterior applications with a broom finish.
If you are buying the concrete, call the supplier's sales dept. ahead of time to get a quote, make payment arrangements and see how much notice they need when ordering. To order concrete you'll speak to their dispatcher. Your order is going to sound something like this; "I'd like __ yards of 4000, 3/4, no air with mid-range. I'm looking for a 5-6" slump. I'd like the first truck at __ o'clock and __ min apart after that".
You can hire a testing lab to test your concrete but in my experience, low breaks are extremely rare. Keep your slumps in the proper range and you'll be fine.
Finishing - The goals here are flatness, finish and durability. The techniques used by your finisher will determine whether you achieve these goals or not. There is no substitute for experience and craftsmanship, but you need to establish your expectations. There are three things I'd say to my finisher.
• "I want a flat floor". Can you walk me through your finishing process". He should have an accurate way to establish grades such as screeds, a laser to set wet pads or preset grade points. He'll also need a way to strike off the concrete such as a straightedge or vibra-screed. I'm not a fan of jitterbugs. A bull float should be used, preferably perpendicular to the direction of the screed. Finally, the floor needs to be uniformly floated with float blades or a pan. These steps will determine flatness before the finish is applied with steel blades.
• "I want a _______ finish". It's important to tell your finisher what finish you want but this can be challenging because the terminology varies. A flat or smooth troweled surface will be smooth but without much shine whereas a burnished or burnt finish will give you a glossy surface. If you are going to epoxy or tile the floor, you'll want the former. You definitely don’t want to see any float or trowel marks and it’s a good idea to mention that you expect some hand work around the edges and penetrations.
• "I want water kept to an absolute minimum". In addition to ensuring design strength is achieved and shrinkage is minimized, controlling mix water is vital to avoiding a range of common surface defects. As the fines settle in freshly placed concrete, excess mix water rises to the surface as bleed water. Water on the surface of a slab is never a good thing but excessive water from higher slumps can create serious problems including shrinkage cracks in the surface paste (crazing), a weak, chalky surface (dusting), blisters & de-lamination. Most concrete has some bleed water and finishing should not proceed until it has dissipated. Bleed water should never be worked back into the surface.
It's a good idea to mention to your finisher to make sure he has enough help to keep up with the finishing and that you don’t want to see water splashed on the slab because it got away from him. Water applied to the surface has the same effect as excess bleed water.
Finishers can be a crusty lot and may not appreciate being questioned but if you have any doubt that your guy is willing and able to do what you want, find one who can. No matter how payment is structured, you are very likely stuck with what you get on pour day. It’s nearly impossible to fix a bad slab and the reality is that very few get ripped out and replaced. You will probably only get one shot at this so find the right guy.
Crack control - There are basically two types of cracks; structural and shrinkage. Structural cracks are caused by overloading the slab/base and are easily prevented by proper design and construction but the most common cause of cracking is shrinkage, which is difficult to prevent.
Concrete shrinks as much as 1/2" in 100' as it sets. As your slab contracts, it is restrained by the ground, obstructions, reinforcing etc., which causes tension. Since this occurs when the concrete's inherent tensile strength is very low, shrinkage cracks often result.
There are things you can do to minimize shrinkage. The most important is to limit slump. More water means more volume will be lost when the concrete dries and the more it will shrink. Placing in cooler temps, fibermesh, increasing aggregate size and proper curing will help but there is a practical limit to how big a slab can be built before shrinkage cracks become inevitable
Control joints (CJs) prevent surface cracks you can see by creating a weak spot for the slab to crack where you can't. CJ's can be tooled into the slab while the concrete is plastic or saw cut after it hardens. Both should be cut at least 1/4 of the slab depth.
By definition, tooled joints are done early in the placement but it's vital that saw cuts be done in a timely manner too. Tension starts growing in your slab quickly as drying shrinkage occurs. If you don’t relieve this tension with CJs, the slab will do it for you in the form of random surface cracks.
If your finisher will be tooling the joints, make sure his groover is deep enough. He'll have to cut the joints with a pole mounted groover while the concrete is still plastic to move the aggregate aside and re-groove to ensure the joint doesn't fill back in.
If you are cutting your joints, use an early entry or Soff-Cut saw and make your cuts immediately after finishing. These saws have a thin blade that turns into the floor and a plate that presses down on the concrete, which keeps the blade from pulling up the surface.
Plan your CJ layout in advance and provide a sketch to your finisher. Recommendations for CJ spacing start at 8-12' but with some attention to overall crack control, you can spread them out twice that. Keep the panels created by the CJs as square as possible with a maximum ratio of length to width of 1.5 to 1. If you are going to install a lift, most manufactures require a min distance from CJ's to the posts so take this into account.
When it comes to cracks, think of it this way - use fiber to minimize them, control joints to hide them and/or reinforcing to hold them together.
With all that said, control joints aren't mandatory. A lot of people find a few random surface cracks less objectionable than a grid of dirt collecting saw cuts. The crack is the same in both cases. The only difference is the aesthetics and what you would prefer to look at. Many people think a visible crack is a sign of concrete failure not realizing that there are even more cracks that they can't see in the bottom of their control joints. There's nothing wrong with just letting the slab crack where it wants especially if you take steps to minimize the amount of shrinkage and use steel reinforcing installed as high as possible to keep the cracks tight.
One final note regarding what are called re-entrant corners. This is an inside corner that projects into your slab and is virtually guaranteed to produce a crack. As the concrete shrinks, tension is concentrated at the corner as the slab tries to move in two directions making diagonal crack from the corner almost inevitable. One obvious solution is to avoid square openings in your slab if possible - a round hole has no corners to crack. About the only other thing you can do is cut a diagonal control joint to the point of the reentrant corner to hide the crack.
Curing - The goal here is simply to prevent the mix water in the concrete from evaporating prematurely. Concrete gains strength as mix water reacts with cement in a chemical process called hydration. If the mix water is lost to evaporation, the process stops. It's always a good idea to protect your slab from drying out prematurely but it's most important in warm or windy weather.
One way to cure concrete is simply to keep it moist by spraying or ponding it with water and/or by retaining moisture with poly or a curing fabric such as ConKure. The concrete doesn't use the extra water - it just seals the surface. Avoid burlap since it will stain your concrete.
There are also chemical curing compounds that you spray or roll on. They are simple to use, reasonably effective and fast - just one application and you are done. Just be aware that these products can interfere with floor coverings you may want to put down later including penetrating sealers, which are typically applied 28 days after placement.
The important thing is to start curing as soon as possible after finishing and if you are moist curing, leave it in place for at least 7 days.
Hot or Cold Weather Concrete - Most slabs are going to be placed outside in the elements. It's a patient and wise man who waits for favorable weather because there is no substitute for a calm, cool day to produce a high-quality slab. Sometimes this isn't an option, so you need a understand the risks and have a plan for mitigating them.
In hot weather, particularly if it is windy, the primary risks are crusting and excessive shrinkage cracking. Crusting occurs when the surface sets before the concrete underneath can support the weight of finishers resulting in webs of fine cracks called crazing. Crazing can also be caused by too much water on the surface, which causes shrinkage cracks in the cement paste.
Build wind breaks and use an evaporation retarder such as Confilm or Day1, which will slow down the surface set and give the underlying concrete a chance to catch up. To minimize shrinkage cracks, cut your joints and get your curing in place as soon as possible after finishing.
In cold weather the primary risk is obviously freezing. Placing when temps are below freezing is risky and best left to those with experience. Concrete will set very slowly, which will delay finishing. An accelerating admixture is a must because you’ll need to get your slab finished and covered before the surface freezes.
Your fresh concrete must be protected against freezing until it gains adequate strength to resist damage. Insulated blankets can retain the heat of hydration to a point (maybe to 25 degrees) but below that you’ll need to provide additional heat and cover to protect the concrete. Avoid unvented heaters because they can cause chalking of the surface.
You’ll ideally want to cure a concrete slab at 55 degrees for at least 72 hours before exposing it to freezing temps. Use a probe type thermometer in a drilled hole near a corner to check concrete temp.
So there you have it. This is obviously just one man’s opinion in 20,000 characters or less. There are a lot of experienced guys on here who might have something to add or might even take issue with my statements. Feel free to weigh in but if the average garage builder follows these steps, I’m confident it will result an attractive and durable garage floor. Feel free to post or PM if you have questions.
CarBikeGuy70
Western CT
Thank you. Very informative and well stated. A pleasure to read, The end result is always the sum of the parts involved- and you have broken the parts down in detail that is understandable. Thanks again.
jtbinvalrico
Tampa FL
Great read! I’ll be digging, doing rebar, and building forms for the pits for a recessed scissor lift install. First order of business after I make my cuts and excavate will be to find a concrete ready mix outfit that I can sit down with. I plan to have the pros deliver and place the concrete, and I’ll be their helper for the job.
clawman
We just finished pouring a new floor in shop. The lower level is 4" thick on gravel base. The upper level is 4" poured on pre stressed concrete planks. How long should I stay off walking, driving, parking trailer and boat?'
C
ConCretin
Central Maine
The concrete will have adequate compressive strength pretty quickly but the surface will take a little longer to resist abrasion, impact, etc. You can lightly walk on any of it right away. I'd give the slab on grade 3 days before you drive on it. I'd probably stay off the plank for a week just to be safe - you should be close to 70% of design strength by then.
C
ConCretin
Central Maine
I'm glad you guys are finding this interesting and hopefully informative. It was a challenge to fit all that hot air under the character limit but I think I got most of it in. Most of this is probably old news to a lot of you. I hope you will feel free to weigh in if I missed something.
all that info is spot on that llwillysfan posted. only thing thay i disagree with is the sawcutting timing. yes you can cut same day if you burn the floor in. and is best practice but if the floor isnt burnt in then you need to wait atleast a few hours depending on conditions, also you will have nicer cleaner cuts with waiting a few hours to cut.
i am a concrete finisher by trade
there is also accelerators and reducers you can add depending on temperatures to help the set time.
also flyash is a filler they put in to substitue some of the portland used in the concrete. flyash mix is tougher to get a nice finish out of and requires the use of more confilm generally then a bag mix
LifeLongWNYer
South of Rochester, NY
Very nice, and I suspect more info than many so-called "builders" know. I too, am saving this for the near term ( hopefully ) use when I put in a floor.
Two questions:
#1: You mentioned extending the under-slab insulation for 4' outside of the actual floor. Does this mean, that, in the case of a pole barn, the foam actually extends 4' past the building walls? If so, how you landscape the exterior of the building. By that, I mean does top soil go on top of the foam, what if I want to plant shrubs around the building? I presume the floor will be 4-6" think, so the foam woun't be very far below grade, please elaborate.
#2: It the case of a pole barn, what is the sequence of laying/compacting sub-base, pouring floor, drilling for poles, setting poles, and hanging exterior metal? I was planning to lay and compact my base, then put up the building, using the traffic which goes on during construction to further compact the base, then, pour the floor. I see other buildings around here go up in that sequence, I am wondering if that is correct.
Thanks for taking the time to post your "guide", I've copied it to a safe place.
C
ConCretin
Central Maine
Hopefully some pole barn experts can weigh in on this. We don't do many pole barns up this way so I'm not sure what the conventional wisdom is.
Placing insulation under a slab and extending it out a few feet protects the slab from frost movement by retaining the natural heat from the earth. This technique is usually applied to mono slabs. The insulation is under a thickened edge, which puts it's low enough to keep it out of harms way.
In the case of a pole barn, I suspect the slab and structure move independently but both are susceptible to frost. I guess you could use insulation to keep everything from moving but it seems most just let it all float.
With regard to pole barn sequence, I'm no expert but I'd be tempted to prep my pad completely before I drilled my posts to ensure my slab edges were well supported.
Sorry if that's not much help. It's not something I know much about.
LifeLongWNYer
Thanks LLWilly'sFan. Here in WNY we get some pretty unfriendly weather, so the insulation under a floor is important to me. I appreciate your info/feedback, hopefully others will weigh in.
lakeroadster
Central Colorado
It's done different ways, mostly due to varying soil conditions, weather and how close the columns are to each other. If you can auger in the holes for the poles, without using an excavator / backhoe, and your support columns aren't in close proximity to each other, your plan is a good one. If you run into rock that requires using an excavator, or the columns are so close you need to dig a large holes for the multiple columns, some of the sub-grade time, effort and money is wasted.
When I lived in Ohio some Amish folks built our 30x40 Lester barn. The building site was flat. They scraped off the top soil, augered the holes (no rocks, virgin soil), installed the columns, installed and compacted the sub-grade, installed the rest of the wooden substructure, and then poured the floor.... then installed the steel sheathing and trim.
Here in Colorado the Lester crew finished the barn structure and metal mid-winter, then I had a sub-contractor do the sub grade and concrete in late spring. Digging the holes for columns was done with a mini excavator. We had holes the size of a VW Bug due to large boulders and the close proximity columns.
You don't really want to do the sub-grade until the holes are augered and the poles erected. If you do you'll:
  • get dirt mixed into the sub grade
  • have issues getting consistent compaction around the holes that matches the compaction in the rest of the sub grade.
Our Ohio Barn:
The Colorado Rock Quarry
protegeV
DFW
Are the base requirements soil and climate dependent?
I ask because my concrete guy claims there's no need for rock under the concrete here. Just some sand over the dirt, vapor barrier, then rebar and concrete.
C
ConCretin
Central Maine
Base requirements do vary based on native soils. If the existing material is free of silt, clay and organics, is compact-able and drains well, you can place right over it but I'd verify your builders opinion before I spent all that money on a new slab.
I'd be leery of sand because it tend to move around during construction. You want a material that packs firmly when compacted and doesn't get rutted up with construction traffic and weather.
protegeV
DFW
The soil around here is largely clay with a bit of sand. 4 dump truck loads of dirt got dropped off yesterday. Idk if you can tell by the picture I attached what the soil looks like. I know nothing about concrete work, but the concrete guy comes highly recommended by both the builder and metal company. Does a lot of commercial as well as residential pad work. That said, my neighbor across the street owns a trucking company and can get me a good deal on road base crushed rock of I want some of that under the slab.
C
ConCretin
Central Maine
I'd like to be more help but it's awfully difficult to comment on your specific situation from afar. Materials vary tremendously from region to region. Clay can be unsuitable in some areas and perfectly fine in others.
Short of hiring a geotechnical consultant, the best you can do is hire reputable contractors with local experience regarding what works. Get references and check their work.
Good luck with your project.
protegeV
DFW
That's what I figured. So many variables. The guy comes highly recommended so I guess I'll trust him.
lakeroadster
Central Colorado
Well.. another fella here did just that... https://www.garagejournal.com/forum/showthread.php?t=390630&highlight=concrete
You could specify that they only use materials that have been previously Proctor tested for compactibility. Any good aggregate yard has those.
Then you could have the sub grade tested to ensure it has been compacted properly. That's what the state and county does when they build projects using your tax dollars. More on that here: Proctor Compaction Testing of Sub-Grade Material
Ggg
N.W. IL.
Going to have a 6" floor poured. The majority of the rock around here is limestone. I have reservations using it in the concrete because it's so soft. I can get pea gravel or river rock if I ask for it. Is it worth getting the river rock v/s limestone? I do plan on installing one or two vehicle lifts, it was recommended to get fiberglass fibers too. My finish plans are to polish it and seal it. Much like you find in the box stores.
C
ConCretin
Central Maine
I am only generally aware of limestone being used for concrete aggregate. Up here in the northeast we use crushed rock almost exclusively.
I don't see any reason not to use the limestone aggregate. I'm sure your ready mix supplier has tested their concrete for compressive strength, which would be the primary concern. Crushed aggregate such as limestone is generally superior to smooth stone such as river rock and concrete made with pea stone will generally shrink more that larger aggregates.
A lightly polished floor doesn't expose much aggregate so I'm not thinking the limestone is too much of a concern here either. Maybe others have some thoughts?
Ggg
N.W. IL.
Thanks for the input on the aggregate.
Any thoughts on the fiber? My thoughts are it's a little better for securing bolt anchors to the floor, but maybe I'm wrong on that. I have several items that will require being bolted to the floor. They charge $6/yd I'm pouring a little over 60yds. so it's not a ton of money to add the fiber.
If it makes any difference the floor will be exposed to salt in the winter due to what melts off the vehicle. It will have floor drains so the snow melt off can be hosed off.
Southeastern Connecticut
Thanks LLWillysfan for taking the time to provide all of the information on slabs. I am about to pour my floor in my 32x46 garage and have been struggling because I am installing radiant heat.
If it wasn't for that, I'd be parking in the darn thing already.
C
ConCretin
Central Maine
Fiber prevents early age shrinkage cracks. It doesn't eliminate cracks so for larger slabs like yours, control joints are usually cut to keep the cracks hidden. Fiber is relatively cheap insurance against random cracks forming before you can cut your joints. For what it's worth, I rarely use it. I do however make sure to cut my joints as soon as the concrete can take it.
Fiber won't provide any structural benefit with regard to imbedded or post installed anchors. Fibermesh claims to reduce absorption of chemicals but I tend to doubt it provides much protection against salt.
Glad you found the info helpful. Good luck with your slab!
C
ConCretin
Central Maine
Welcome to the GJ Wozer1. Since you have another thread on the subject, might have been better to PM me to avoid redundancy but since you asked;
Insulation under the lift pits is fine from a structural standpoint. It's also true that you'd probably never notice the difference in your heating bill in your lifetime if you left it out.
Whether i did it or not would depend on the circumstances. If it were simply a matter of laying down a piece or two of insulation, I'd probably do it. If it was any more complicated than that, I'd skip it. Not very definitive I know but hopefully helpful.
rattle_snake
Chandler, AZ
So, concrete is expensive, heavy and will crack?
Nice write-up, to the point, concise. I learned a few things you wrote about during and after my pour that would have been helpful beforehand.... good info. Thanks.
Wozer1
Bolton England
Sorry about the other post. Didn't realise i could pm you. Thanks for reply. I have done some research on the insulation and there are different strengths of insulation some commonly used in coldroom floors where heavy traffic like forktrucks are used. Another issue with the high density insulation is the narrow widths of the boards. They are manufactured in 2400 x 600mm sizes only. Not quite wide enough.