I have decided to pull the trigger on HVAC in our shop. A thread with pictures will be made when I do this.
The specs:
40x60x17 All steel, All welded. Think of a pole barn but with 5" pipe, I-beams and red iron instead of wood posts, trusses and lumber. 4/12 pitch roof.
Standard metal building insulation. White backing, silver radiant barrier towards the metal sheeting.
3 roll ups (insulated) Two 12x14 and One 8x8. Need to put the seals in at the top (gap at top of roll). Two steel 3070 man doors. East wall (60 ft) is shaded by trees. West wall (60 ft) is shaded by 30x60 lean to. South wall (40 ft) is exposed.
4 Emerson 60" heat fans. Over 10000 cfm each on high.
NO GAS. 200 amp service, single phase.
Here is my plan. Use residential split system. Ruud 14 SEER 5 ton condenser, Ruud 24" air handler with ECM blower and 5 ton coil. Build a return plenum mid way down east long wall (60 ft). Will use 2 filter grills for intake filtration (two 20x25 or larger will flow 2000 cfm) Set air handler and use a 4 ft supply plenum vertical.
As for ducting, not sure if I just want to use a couple of large, wide throw registers on the plenum? Or run about 10-15 ft of snaplock each way and use register boots and registers?
Next decision is:
AC/20kw heat (68240 btu)?
AC/25kw heat (85300 btu)?
Heat pump/20kw backup heat?
(Heat pump specs 47* 57000 btu, 17* 35800 btu)
I have 2 heat pumps at the house. Love them. But heat pumps are a "gentle heat" and not a quick temp rise like resistive. Also more expensive up front, cheaper to operate... I'm thinking keep this simple and just go resistive.
Also in the scope of work is to setup Ubiquiti Nanobeams for a point to point connection to the house (700 ft). This is so I can use a WiFi thermostat to control the system remotely. Example. I want to work in shop after work. 4 pm, ramp heat up. Arrive at shop at 5:30 pm, its warm but haven't had to run the heat all day...
Let's see what y'all think!
CT
I have decided to pull the trigger on HVAC in our shop. A thread with pictures will be made when I do this.
The specs:
40x60x17 All steel, All welded. Think of a pole barn but with 5" pipe, I-beams and red iron instead of wood posts, trusses and lumber. 4/12 pitch roof.
Standard metal building insulation. White backing, silver radiant barrier towards the metal sheeting.
3 roll ups (insulated) Two 12x14 and One 8x8. Need to put the seals in at the top (gap at top of roll). Two steel 3070 man doors. East wall (60 ft) is shaded by trees. West wall (60 ft) is shaded by 30x60 lean to. South wall (40 ft) is exposed.
4 Emerson 60" heat fans. Over 10000 cfm each on high.
NO GAS. 200 amp service, single phase.
Here is my plan. Use residential split system. Ruud 14 SEER 5 ton condenser, Ruud 24" air handler with ECM blower and 5 ton coil. Build a return plenum mid way down east long wall (60 ft). Will use 2 filter grills for intake filtration (two 20x25 or larger will flow 2000 cfm) Set air handler and use a 4 ft supply plenum vertical.
As for ducting, not sure if I just want to use a couple of large, wide throw registers on the plenum? Or run about 10-15 ft of snaplock each way and use register boots and registers?
Next decision is:
AC/20kw heat (68240 btu)?
AC/25kw heat (85300 btu)?
Heat pump/20kw backup heat?
(Heat pump specs 47* 57000 btu, 17* 35800 btu)
I have 2 heat pumps at the house. Love them. But heat pumps are a "gentle heat" and not a quick temp rise like resistive. Also more expensive up front, cheaper to operate... I'm thinking keep this simple and just go resistive.
Also in the scope of work is to setup Ubiquiti Nanobeams for a point to point connection to the house (700 ft). This is so I can use a WiFi thermostat to control the system remotely. Example. I want to work in shop after work. 4 pm, ramp heat up. Arrive at shop at 5:30 pm, its warm but haven't had to run the heat all day...
Let's see what y'all think!
CT
That will stretch the legs of a 200 amp service! Local branch or the warehouse of the supply house we use don't even show a 25kw or 30kw in stock. 20kw most common (in the south) for a 5T system.