Would you all mind double checking my figures. Let see if I can ask the question right. 
Currently, I have 3 #12, with a #12 ground in 3/4" conduit. Two of the 3 are lights on different switches and the other one for a power outlet.
I used this website for the fill calculations. https://www.southwire.com/calculator-conduit
I may pull one of the light circuits out. It was a light that was on when the outlet that was for the portable air compress was on. I am adding a circuit for stationary air compressor. The motor tag says 17.2 FLA. I have the #10 laying around, so, for now, I am going to use that. I am extending the conduit along the wall for the compressor junction. I can pull out the #12 ground and replace it with the #10 ground.
So for the fill calculations, there are 6 #12 and 4 (L1,L2,N,G) #10. The fill for 3/4" is 26%. 26% less than 40%, good there.
The shop is currently not air condition. So the correction factor I am using here in Oklahoma is (96F to 104F) for THHN is .91. Maybe I should future proof for global warming and use the (105F to 118F) .87.
I think I read somewhere, for dereating you use the 90* column.
#12 CU =30amp
#10 CU = 40amp
30 X .87 (temp) X .80 (# of wires) = 20.88
40 X .87 (temp) X .80 (# of wires) = 27.84
Even being smart aleck, the #12 on 20amp breaker is ok, but I am a little shy on #10 for a 30amp. I would guess we are only 10 to 20 days a year over 100F and above 105F is rare. I would feel ok with a 30amp on the #10.
So, am I on track or is there something I am forgetting? Thoughts?
Do I need to change out the ground from a #12 to #10?
Currently, I have 3 #12, with a #12 ground in 3/4" conduit. Two of the 3 are lights on different switches and the other one for a power outlet.
I used this website for the fill calculations. https://www.southwire.com/calculator-conduit
I may pull one of the light circuits out. It was a light that was on when the outlet that was for the portable air compress was on. I am adding a circuit for stationary air compressor. The motor tag says 17.2 FLA. I have the #10 laying around, so, for now, I am going to use that. I am extending the conduit along the wall for the compressor junction. I can pull out the #12 ground and replace it with the #10 ground.
So for the fill calculations, there are 6 #12 and 4 (L1,L2,N,G) #10. The fill for 3/4" is 26%. 26% less than 40%, good there.
The shop is currently not air condition. So the correction factor I am using here in Oklahoma is (96F to 104F) for THHN is .91. Maybe I should future proof for global warming and use the (105F to 118F) .87.
I think I read somewhere, for dereating you use the 90* column.
#12 CU =30amp
#10 CU = 40amp
30 X .87 (temp) X .80 (# of wires) = 20.88
40 X .87 (temp) X .80 (# of wires) = 27.84
Even being smart aleck, the #12 on 20amp breaker is ok, but I am a little shy on #10 for a 30amp. I would guess we are only 10 to 20 days a year over 100F and above 105F is rare. I would feel ok with a 30amp on the #10.
So, am I on track or is there something I am forgetting? Thoughts?
Do I need to change out the ground from a #12 to #10?