12/2 Romex with ground for 230v minisplit install?
Raisedonadeere
Central KY
I have plenty of the 12/2 w/g laying around and the mini split doesn’t require a neutral. Can I color the white wire red and use it. I know it will work but is there some compelling reason not to. I go blind reading code books.
Norcal
What does the equipment data plate say about minimum circuit amperes?
R
Raisedonadeere
Central KY
All the other questions mentioned so far are covered. I just am used to a red and black wire when I do 230. No neutral and the color coding gave me pause.
But the wiring diagram for the minisplit does not include a neutral so that leaves the color coding. I am wondering if any of you would just go and purchase some other wire configuration. I will be using other stuff to go from disconnect box to the unit. It is about a 60’ run to the disconnect box.
Thanks for your response.
mm08822
Post the equipment nameplate to determine the required minimum circuit ampacity (MCA).
NM-b could be used to feed the line side of the disconnect if not exposed to weather or in conduit exposed to weather - i.e. - back side entry into disconnect through wall.
mm08822
IF you have the correct size cable for the application, the white wire can re-identified (at all ends) to any color other than green or gray. No need to purchase 3/c cable and leave the white un-used.
Color coding of "Romex" used for that size of a load/wire is "optional", as long as the installation permits the use of Romex". Not a bad idea to market the white wire with red tape. Prevents newbies from freaking out when they remove the cover off of a load center !
Perfect example ! Code would probably require a weatherproof flexible conduit (with THWN) from the disconnect to the compressor.
Norcal
Remarking the white of a cable when when used as a ungrounded (hot) is required it is not "optional".
R
Raisedonadeere
Central KY
Thanks, you and Norcal answered my question. Looking back at my question I should have ask about color coding.
BTW the com wires were supplied with the line set install kit.
02vito
Colorado
I agree with the other posters who suggest that you color the white wire red either with tape or with permanent marker [my preference]. I do not agree that it is optional to do this.
According to my local electrical inspector, who is extremely competent, you can recolor a white wire to red if the wire is in a cable, but if you were pulling individual colored conductors through conduit, you would need to pull a red wire.
Norcal
The NEC does not require it to be red, just not white, gray, or green.
Apparently he is not very knowledgable.
The NEC does not have a mandated color code for ungrounded conductors other than the stinger leg of a 3-phase delta service...
teamextreme
Lakewood, CO
I would say he probably is knowledgeable, but you're nit-picking the use of "red", which may have been just been paraphrased by the poster. I think he was just explaining that the white had to be colored, be it black, red, blue, etc. Something other that white to indicate a hot wire. Point being, to the OP, you are required to re-mark the white wire in your application. I just use black tape, since I always have it available. Red is really not necessary, but nothing wrong with that either.
bubinga
What is Phase tape?
Electrical tape (or insulating tape) is a type of pressure-sensitive tape used to insulate electrical wires and other materials that conduct electricity. It can be made of many plastics, but vinyl is most popular, as it stretches well and gives an effective and long lasting insulation.
no expert here (me),but I don't see a issue?
mm08822
Say what?! How do you mark then, sharpie? That's a lame method compared to tape, IMO.
After last job, where i had to re-identify 12 ft (total) I finally went out and got the right marker.
I now use a "Magnum" Sharpie with a small v notched out of the chisel tip. 3 swipes and it's done. Looks better than tape and faster.
Comes in blk, red, blue - pick your flavor.
Angelfire
New Mexico and Ireland
Are you saying the disconnect is 60' from the unit?
It's been a couple of years since I wired mine up but I seem to recall your disconnect needs to be within 50' of the unit, accessible, and visible.
Personally, I'd locate it as close to the unit just for convenience sake.
Cheers.
Norcal
Cheers.
I would take it as it’s a 60’ run to the disco.
Jim greengo
Behind my house
Are you just running it to the disconnect or are you trying to use it inside a whip?