Say I'm running a 12/3 cable to install two seperate dedicated 20A 120v outlets, with a shared neutral. When you share a neutral like that, does that mean the cable needs to be hooked up to a 20A double pole breaker? Or can I use two individual 20A breakers?
 
To avoid these ads, REGISTER NOW!
OP
N

Number22

Banned
Joined
Nov 25, 2009
Messages
106
Location
OR
Does it make any difference if I run THHN instead of 12/3? Or is it the "shared neutral" that makes the code?
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Double pole breaker with the handles tied together.

Its the shared neutral which creates a circuit called a multi-wire or Edison multi-wire circuit, doesn't matter how its wired, romex or conduit and THHN wire, same difference. They want both hots to trip if one does. Also insures that you are using both busses or "phases" of the panelboard. With two separate breakers, improperly installed, both on the same side of the buss (electrically), you would overload the neutral.

Neutral must be wired so the removal of a receptacle does not interrupt it (code), thus it must be pigtailed. Cannot just run the neutral in and out of one receptacle and off to the next.

Charles
 

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,687
Location
Maine
can you tell me what section that is in? I want to make a note of it for when our AHJ changes over to the 2008 code.

210.4(b), each multiwire branch circuit shall be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates.
 

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
that has been code from the 1980's.don't have to wait for ahj what ever that is.it has been there all along.
 

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
number22!sounds like you are just getting going doing electrical work.if so there is a good book for you.practical electrical wiring by herbert p. richter and creigton schwan.you can get one at most book stores.
 

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,687
Location
Maine
that has been code from the 1980's.don't have to wait for ahj what ever that is.it has been there all along.

No it hasn't, it said if it was going to the same yoke it had to have a 2 pole breaker, if it wasn't going to the same yoke you could use 2 single poles.
 

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
but if you used two single pole breakers you had to use handle ties.
 

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
the oldest book i have is 93.and it say's same as your 2008 book.so it isn't anything new.not trying to be a jerk.just like a good spirited conversation....mike
 
Last edited:
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Walrus is correct. 2005 code said that when "a multiwire circuit supplies more than one device or equipment on the same yoke, a means shall be provided to disconnect simultaneously all ungrounded conductors........ "

The 2005 codes wording was a complete revision of earlier code (which I do not have, but it has a revision bar next to it) This statement leaves open that if the multiwire circuit does NOT supply two different devices on the same yoke, that separate breakers, not connected to trip together, could be used.

2008 code is again revised, simply stating "Each multiwire branch circuit shall be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates." leaving no doubt about the intention of the code, that all multiwire circuits installed under the 2008 code must use breakers that trip open both hot circuits.

Charles
 

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
i will go with that.although since the middle 80's,every place i have worked,inspectors wanted double pole breakers.it is a lot safer.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Backing up further, 2002 code reads like 2005 code but is preceded with a "In dwelling units...." leaving it open that multiwire circuits supplying two devices on the same yoke, but NOT in a dwelling, did not have to have the simultaneous trip.

That is the oldest version NFPA will allow me to access online.

Charles
 
Last edited:

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Over the summer i noticed the rear portside bag would always fill very slow.
after doing a little research i found that my system uses one big pump to fill all the bags. so why would only one bag fill slow.
ow yea this is on a 2005 xlv with gravity 3 ballast system.

SPAM moderators notified.

Text unrelated to the discussion at hand and links to koozies at the bottom of the post, and post number one by the "member"

Charles
 

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,687
Location
Maine
i will go with that.although since the middle 80's,every place i have worked,inspectors wanted double pole breakers.it is a lot safer.

They can want what they want, they're supposed to enforce the rules
 

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
never saw any problem with doing it.but now you have to do it that way any how.
 

Torque1st

MEMBER EMERITUS
Joined
Sep 14, 2008
Messages
5,668
Location
KC Metro, Kansas
The oldest code I have access to presently is the 1984 NEC which reads:
_In dwelling units a multiwire branch circuit supplying more than one device on the same yoke shall be provided with a means to disconnect simultaneously all ungrounded conductors at the panelboard where the branch circuit originated.
_Multiwire branch circuits shall supply only line to neutral load.
--Exception No.1: A multiwire branch circuit that supplies only one utilization equipment.
--Exception No.2: Where all ungrounded conductors of multiwire branch circuit are opened simultaneously by the branch-circuit overcurrent device.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
The oldest code I have access to presently is the 1984 NEC which reads:
_In dwelling units a multiwire branch circuit supplying more than one device on the same yoke shall be provided with a means to disconnect simultaneously all ungrounded conductors at the panelboard where the branch circuit originated.
_Multiwire branch circuits shall supply only line to neutral load.
--Exception No.1: A multiwire branch circuit that supplies only one utilization equipment.
--Exception No.2: Where all ungrounded conductors of multiwire branch circuit are opened simultaneously by the branch-circuit overcurrent device.

Those exceptions still exist under a paragraph (C) which says you can only have line to neutral loads. I guess the exception allows me to tap line to line (240V) off of the circuit if I wanted to.

Charles
 
OP
N

Number22

Banned
Joined
Nov 25, 2009
Messages
106
Location
OR
Also insures that you are using both busses or "phases" of the panelboard. With two separate breakers, improperly installed, both on the same side of the buss (electrically), you would overload the neutral.
Right - that's probably the main reason for the code. My shop is actually 3 phase and I found mutiple existing breakers overloading neutrals like that. :rolleyes:
 