220v question....

pipehack

Well-known member
Joined
Feb 23, 2009
Messages
923
Location
chicago
I posted a thread about "220v confusion" a couple weeks ago.
O.k. so here's the deal. I shut off the breaker and disconnected the wires. Pulled out the old #8 wire that was in there. BUT>>>> The two black wires were #8 and one red wire was #10 which went to the neutral bar. This house was built about 32 years ago and color coding wasn't around then. so it was run what ya brung. I pulled 2 # 8 black wires and 1 #8 green wire. I know the black ones go to the breaker but my question is ...... Does the green wire go to the neutral bar??? Is that the same as ground?? Where does it go???
 
To avoid these ads, REGISTER NOW!

nate379

Banned
Joined
Feb 2, 2009
Messages
7,279
Location
Palmer, AK
What are you wiring? Normally if it's just 3 wire 240v it will go to ground. 4 wire you'd add the neutral into the mix.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,062
Location
Coronado, CA
If the panel we are talking about is your main panel the Neutral Bar is supposed to be connected to Ground, this is usually done with a long screw threaded through the Neutral Bar into the can. The can is supposed to be grounded.
 

LoneGunman

Well-known member
Joined
Mar 27, 2007
Messages
2,081
Location
The Gunshine state
As nadogail said, if it's your primary means of disconnect the neutrals and the grounds are connected. Color coding was very much around 32 years ago, of course that does not mean it was followed everywhere.
 
To avoid these ads, REGISTER NOW!
OP
P

pipehack

Well-known member
Joined
Feb 23, 2009
Messages
923
Location
chicago
It is done...... I was waiting for an electrician from one of the jobs I was working on to call me and possibly come over. He did call me and I told him what I had gotten done. He said "what the hell do you need me for?" Told me what to do with the green wire and the rest is history... Now I can weld!!!!!!!!!!!!!
 

checkthisout

Well-known member
Joined
Sep 5, 2008
Messages
5,232
It is done...... I was waiting for an electrician from one of the jobs I was working on to call me and possibly come over. He did call me and I told him what I had gotten done. He said "what the hell do you need me for?" Told me what to do with the green wire and the rest is history... Now I can weld!!!!!!!!!!!!!


That's nice but the wires aren't suppose aren't suppose to weld themselves together like that when you turn the breaker on.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
The original was likely safe, hooking a red to a bar isnt the thing to do though and replacing it was a good thing. You can use 10 for the ground with wires to 6 and 60A.
 