230V dedicated circuits?

vavet

Well-known member
Joined
Mar 6, 2012
Messages
5,363
Location
Ashland, VA
I'm planning to insulate and drywall my detached garage/workshop. In an effort to futureproof this, I'd like to add some additional 230V circuits.

I have a total of three 230V circuits currently: one for future mini-split, another for the the auto lift, and 3rd one where the autolift was originally planned.

This is a residential garage and I'm likely the only one to be working in there at, so it's unlikely to have more than one 230V circuit on at a time (with the exception of mini-split).

Is it permissible to daisy chain 230V circuit boxes together? It would be arranged so I would have one 30 amp breaker that would feed multiple junction boxes? My thought is I'll run the wire from the breaker box to a new junction box with wire nuts, but no receptacle. Then I'll run more wire to the next junction box 8 feet away. I've heard of something called non-coincidental loads - you wouldn't have your AC running at the same time as your furnace, so this is OK. Since they are not pre-defined loads, is this Ok to do?
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
If your locality follows IRC International Residential Building Code then no. Multiple outlet circuits are not to be over 20A.
 

Crazyjake8493

Well-known member
Joined
Sep 26, 2014
Messages
4,017
Location
Upstate NY
Nothing wrong with having multiple junction boxes on a circuit and installing one receptacle in the box needed down the road. If you're not sure where you'll want the 240V receptacles at this point, I'd consider surface mounting those circuits in the future, rather than having a bunch of boxes for nothing.
 

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
Future proof, run emt to a 4x4 box in the center of each wall, back to the panel.

You will be able to add outlets as needed in the 4x4, 240V or whatever...or attach a 4x4 ring to that box and then extend surface mount conduit left or right.
 
To avoid these ads, REGISTER NOW!

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
Put in a big enough panel to handle the later runs. I did - and I'm still out of room. SO go larger.
 

jtbinvalrico

Well-known member
Joined
Jan 2, 2010
Messages
1,376
Location
Tampa FL
I’d do the home runs for each circuit and be done with it. When you bring the wires into the panel, you can cap them and tie them off to the side...if you ever want to use that circuit, put a breaker in and run it....Future-proofed and you won’t have to tear into your walls later.

YMMV....This approach inspected and approved here in Hillsborough County, FL.


Sent from my iPhone using Tapatalk
 