3 Pole Switch for 2 Pole?

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
Is it OK to use a 3 Pole Switch for 2 pole?

If someone GAVE me a 60A 3 Pole Cutoff switch (Nice GE unit) which I assume came from a 3 Phase setup...could I just wire 2 poles and use it in my single phase 240v Application?
 
To avoid these ads, REGISTER NOW!

Beemer533

Well-known member
Joined
May 9, 2014
Messages
2,057
Location
Syracuse, NY
I don't see why not. We purchase bulk disconnects for a lot of jobs and they are all 3 phase; maybe half end up being used in 120/240 applications.
 
To avoid these ads, REGISTER NOW!

_Dock_

Well-known member
Joined
Jan 10, 2011
Messages
169
Location
Ky
Yes, its done all the time in commercial and industrial settings. Just make sure that the current rating of the switch is not less than your device and make sure it is rated for the exposure you are using it in.
 