4 Gauge wire into ground bar

Skooterj

Well-known member
Joined
Mar 11, 2021
Messages
758
Location
Indiana
Okay, so the ground bar in the panel I am installing in my detached garage says it will accept up to #4 wire, but there is just no way my stranded #4 MHF ground is actually going to fit. At least, I don't see how. I tried to test fit a piece, and it just looks too big. Does anyone have any suggestions besides getting a lug kit?
 
To avoid these ads, REGISTER NOW!

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,903
Location
Southern Oregon
Had that problem before too. It has to be perfectly round and the strands need to be tight. Try removing the screw. Try stripping it back farther and filing the end so it'll get started and push it in. Obviously don't file it down where it would be contacting the lug. Then give up and get an accessory lug for your panel/bar.

1680707347822.png
 
To avoid these ads, REGISTER NOW!
OP
S

Skooterj

Well-known member
Joined
Mar 11, 2021
Messages
758
Location
Indiana
Had that problem before too. It has to be perfectly round and the strands need to be tight. Try removing the screw. Try stripping it back farther and filing the end so it'll get started and push it in. Obviously don't file it down where it would be contacting the lug. Then give up and get an accessory lug for your panel/bar.

1680707347822.png
This is pretty much where I am at. I thought maybe I could pigtail a #6 CU on the end, but the splice is more than a lug kit. Then I thought I'd get an end pin. Again, more expensive than the lug kit. Figured heating it up would make it more malleable, but also larger. Guess I could try freezing it in dry ice, but that's probably more expensive than the lug kit too. So lug kit it is...
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
It'll fit. I'd considering stripping it long and cutting a few strands partway out to make a taper, like the suggestion of filing. Then use a flush cutter to trim the excess once it is in
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,759
Location
Long Island
Why would that matter in fitting them into a lug? They have different ampacity, but the same diameter.
Because #4 AWG refers to the cross sectional area and not the diameter. The diameter would be the same for solid wire, but stranded wire has a larger diameter that depends on the packing density of the strands, and that may be different when aluminum sometimes features non-round strands that pack more tightly.
 
Last edited:

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
Why would that matter in fitting them into a lug? They have different ampacity, but the same diameter.
Because I was tired and hadn't had coffee yet.

I had a similar issue and just bought the lug kit like why atg posted. I think it was $8 saved a ton of hassle
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
When buying a lug kit for a ground bar make sure the lug is the same brand as the ground bar, the screw size/threads are all different between manufacturers.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,366
Location
Coastal NJ
Because #4 AWG refers to the cross sectional area and not the diameter. The diameter would be the same for solid wire, but stranded wire has a larger diameter that depends on the packing density of the strands, and that may be different when aluminum sometimes features non-round strands that pack more tightly.

I agree there are differences from solid to stranded, but the OP has Aluminum MHF and it's usually packed pretty tight. Maybe his uses round strands. The ground bar is rated for #4 and while I can't say if they meant stranded or solid, I expect many users are using stranded wire.

Either way, the accessory lug others mentioned will work.

1680712766481.png
 
To avoid these ads, REGISTER NOW!
Top Bottom