Adding 200amp sub panel?

rodm1

Well-known member
Joined
Feb 17, 2008
Messages
2,273
I wont to add another 200amp panel to this main panel can I add a double lug kit to this panel in order to get the hot legs I need? Then add a ground kit to both neutral and ground bars?


p.s. any ideas on tying the main feed back away of the panel screws?


double lug kit
http://lugsdirect.com/images/2'0TP-1_500.JPG

Crimp terminals
http://www.grainger.com/Grainger/QUICK-CABLE-Wire-Connector-5LNC9
http://www.grainger.com/Grainger/QUICK-CABLE-Wire-Connector-5LNC5

Ground bar kit
http://lh4.googleusercontent.com/pu...KFSDMOd1fU9mRq84HdFrF19Ot95QwCLpD7X5pyVgkst7R




View media item 7047
 
Last edited:
To avoid these ads, REGISTER NOW!

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Good god!

I have a VERY hard time believing Sq D intended for lugs to be installed there! You can see those wires block all those breaker spaces! Factory feed-thru panels usually have the lugs at the bottom of the panel tapped right off the bussing, not in the middle of the panel like yours.

The proper way to install large feeders into a panel that didn't come with factory feed thru lugs is to use a sub feed lug kit, I did a little googling and it looks like the part # is QO2225SL from catalog page 7:

http://static.schneider-electric.us...eakers/QO-QOB Circuit Breakers/0110PL9401.pdf
 