I have a indoor swim spa that was installed by previous homeowner. The main panel is a 200a GE Powermark Gold Load center and it has a 60a 3 pole (non GFCI) breaker with 6/3 wire going out to the spa Cutler Hammer disconnect box. I was told by a spa service tech that the 60a breaker needs to be GFCI.

There basically are no available GE gfci breakers ( GE-THQL2160GF1) out there. Wondering the easiest (but safe) way of accomplishing this.

I came across a Siemens breaker on amazon and a reviewers post (see pic) who describes putting this breaker into his GE Powermark panel and "creatively" isolating the nuetrals at the disconnect but does not show this.

I am attaching pics my current disconnect box. Not sure whether I need to hook up a subpanel next to my main or in place of my disconnect (tight space). Thanks for any input!

Breaker-Amazon1.jpg
 

Attachments

  • IMG_20230217_054355986.jpg
    IMG_20230217_054355986.jpg
    489.6 KB · Views: 12
  • IMG_20230217_053951598.jpg
    IMG_20230217_053951598.jpg
    555.9 KB · Views: 12
  • Breaker-Amazon3.jpg
    Breaker-Amazon3.jpg
    92 KB · Views: 12
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
I am attaching pics my current disconnect box. Not sure whether I need to hook up a subpanel next to my main or in place of my disconnect (tight space). Thanks for any input!

1676635136659.png
What is that disconnect box attached to?

Where is it located relative to the spa?

As Mike said, changing the disconnect is likely the easiest solution.
 
OP
D

Donttouchthat

Well-known member
Joined
Apr 11, 2021
Messages
147
Location
CONNECTICUT
OP
D

Donttouchthat

Well-known member
Joined
Apr 11, 2021
Messages
147
Location
CONNECTICUT
What is that disconnect box attached to?

Where is it located relative to the spa?

As Mike said, changing the disconnect is likely the easiest solution.
Hey PC, It is attached to a 2x4. I don't see the box being grounded as the ground wire goes straight thru to one another. The box is right next to spa through an access panel. I forgot to ask Mike about the separation of neutral and ground in this new load center he posted. Do I need to get a neutral bar and isolate being that it is serving as a subpanel? Thanks
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Hey PC, It is attached to a 2x4. I don't see the box being grounded as the ground wire goes straight thru to one another. The box is right next to spa through an access panel. I forgot to ask Mike about the separation of neutral and ground in this new load center he posted. Do I need to get a neutral bar and isolate being that it is serving as a subpanel? Thanks
Beyond the first means of disconnect, the neutral and ground must be kept separate.

The Schneider website says it comes with a ground bar. See the product datasheet

 

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
Hey PC, It is attached to a 2x4. I don't see the box being grounded as the ground wire goes straight thru to one another. The box is right next to spa through an access panel. I forgot to ask Mike about the separation of neutral and ground in this new load center he posted. Do I need to get a neutral bar and isolate being that it is serving as a subpanel? Thanks
If you end up keeping the disconnect you currently have, the enclosure should be grounded. There should be a threaded hole on the back wall. Thread a ground screw into it, attach a ground wire to it (the same gauge as the ground wires in the cables), and connect it to the other 2 ground wires and wirenut them all together.
Also, get a knockout seal to plug up that hole in the upper right corner.

If you end up replacing the disconnect, you still attach the grounds the exact same way (unless it already has a ground bar, which would already be bonded to the enclosure. In that case, just connect the 2 ground wires to the ground bar). Since it has a GFCI breaker, there will be specific locations to connect the incoming and outgoing neutral wires.
 
OP
D

Donttouchthat

Well-known member
Joined
Apr 11, 2021
Messages
147
Location
CONNECTICUT
If you end up keeping the disconnect you currently have, the enclosure should be grounded. There should be a threaded hole on the back wall. Thread a ground screw into it, attach a ground wire to it (the same gauge as the ground wires in the cables), and connect it to the other 2 ground wires and wirenut them all together.
Also, get a knockout seal to plug up that hole in the upper right corner.

If you end up replacing the disconnect, you still attach the grounds the exact same way (unless it already has a ground bar, which would already be bonded to the enclosure. In that case, just connect the 2 ground wires to the ground bar). Since it has a GFCI breaker, there will be specific locations to connect the incoming and outgoing neutral wires.
Great, Thanks
 
To avoid these ads, REGISTER NOW!

Youngandfree

Well-known member
Joined
Dec 29, 2020
Messages
877
Location
VA
I have a indoor swim spa that was installed by previous homeowner. The main panel is a 200a GE Powermark Gold Load center and it has a 60a 3 pole (non GFCI) breaker with 6/3 wire going out to the spa Cutler Hammer disconnect box. I was told by a spa service tech that the 60a breaker needs to be GFCI.

There basically are no available GE gfci breakers ( GE-THQL2160GF1) out there. Wondering the easiest (but safe) way of accomplishing this.

I came across a Siemens breaker on amazon and a reviewers post (see pic) who describes putting this breaker into his GE Powermark panel and "creatively" isolating the nuetrals at the disconnect but does not show this.

I am attaching pics my current disconnect box. Not sure whether I need to hook up a subpanel next to my main or in place of my disconnect (tight space). Thanks for any input!

Breaker-Amazon1.jpg
Google seemed to find that model number pretty easily for me.

 
OP
D

Donttouchthat

Well-known member
Joined
Apr 11, 2021
Messages
147
Location
CONNECTICUT

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,409
Location
Minneapolis
I have a indoor swim spa that was installed by previous homeowner. The main panel is a 200a GE Powermark Gold Load center and it has a 60a 3 pole (non GFCI) breaker with 6/3 wire going out to the spa Cutler Hammer disconnect box. I was told by a spa service tech that the 60a breaker needs to be GFCI.
When did the previous owner install the spa, and what version of the NEC was in use when that happened? If it was done at a point where a 240vac GFCI wasn't required you shouldn't have to retrofit existing work.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,684
Location
VT
When did the previous owner install the spa, and what version of the NEC was in use when that happened? If it was done at a point where a 240vac GFCI wasn't required you shouldn't have to retrofit existing work.
Haven't spas required GFCI for a while?
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,409
Location
Minneapolis
Haven't spas required GFCI for a while?
Yes they have, I think the requirement was added in the 1995 revision of the NEC. Also, different states adopt the most current version of the NEC at different times; sometimes they'll stay with one version for years after a newer version is published or even make exceptions for certain parts of it, so in the OP's case his state may have added that requirement sometime after 1995. That's why I asked when the spa was installed.
 
To avoid these ads, REGISTER NOW!
Top Bottom