If you can trace the circuits, and replace the first receptacle in each circuit with a GFI breaker, you will have GFI protection for that receptacle and all the downstream ones. You can then replace two-prong downstream receptacles with 3-prong receptacles labeled "GFCI protected, no equipment ground". Tracing the circuits from the breaker box to the first receptacle can be quite challenging in an old house.
GFCI breakers aren't that expensive, at least for common brands like Square D or Siemens. Figure $20 to $40 per breaker depending on brand and where you buy it. Replacing the breakers in the panel is relatively fool-proof and saves tracing the circuits.
I hope you aren't thinking of splicing in extra GFCI receptacles right at the panel, just to save money on the breakers. The extra boxes, splices, wire, and effort will. cost more than the breakers, and the end result will look like amateur hour.