Advice for how to do feed wire
gearheads78
DFW TX
My old shop I just tore down had a 50A breaker inside the main house panel with 6/2 copper out to the shop through 1" Sch40 PVC. the run was about 50-60ft. I work by myself so I never had any problem with power. The new shop will be much larger and have more stuff but other than more lights my doing things at once power use should not change much. That being said I want to be prepared for 100A future use.
The new run will be about 40-50ft if I can go the same way or about 65-75ft if I have to go around the house outside.
So what is the best way to go about getting 100A to my shop with leaving the single residential meter? #2 cable probably what I need to use? If so what size conduit do I need for that? Any tips greatly appreciated
MrMark
Southern Cal.
2 inch PVC is plenty big and what I would use. You are talking individual wet rated wires, correct? #3 copper is rated right at 100 amps for that application. #2 copper is a little extra, of course.
ishiboo
Oshkosh, WI
Best is relative. Best what?
Aluminum URD (#2, or 2-2-2-4) is the cheapest and does not require conduit. Aluminum is 100% fine when used for feeders like this, and VERY common. Anti-oxidation compound on the exposed wire. You may be able to find this for ~$2.50 a foot.
Copper I believe you could get by with #4. It would be much more expensive than the aluminum. Grab an amperage chart to double-check.
mrb
Copper
#4 - 85 amps
#3 - 100 amps
#2 - 115 amps
Aluminum
#4 - 65 amps
#3 - 75 amps
#2 - 90 amps
#1 - 100 amps
Charles (in GA)
50 mi south of Atlanta
URD is not code compliant for use in a building, it must junction outside the building with something else, Most quadplex or "mobile home feeder" is URD and also marked XHHW, RHW, RHH-2, RHW-2 and needs to be marked with one of these ratings to be legit for in building installation.
http://www.garagejournal.com/forum/showthread.php?t=75484
Charles
Norcal
People keep using the table for residential service entrance conductors where it is allowed to UNDERSIZE the conductors, they do not apply to subpanels nor outbuildings. the column in 310.16 for 75 degree conductors is what is required.