My air compressor tag reads 15.0 amp 208-230 volt 5 hp. It will be about 25 feet from the breaker box. I have a bunch of #10 wire left from another project, is this big enough or do I need something bigger? Thanks Mike
My air compressor tag reads 15.0 amp 208-230 volt 5 hp. It will be about 25 feet from the breaker box. I have a bunch of #10 wire left from another project, is this big enough or do I need something bigger? Thanks Mike
because 230/1 draws close to 30A
30A seems like a lot for a 5hp motor. My 5hp 230 single phase has 21A-22.5A stamped on the motor plate.
Per the tables in the NEC, a 5hp 230vac single phase motor has nominal full load current of 28 amps. They can vary from that number, as shown by your motor.
It's probably 5hp peak. I.e., marketing HP.
15A @ 230VAC is about 4.6HP. 4.2HP @ 208V. That's assuming 100% efficiency, so more like 4HP tops in real life.
It's probably 5hp peak. I.e., marketing HP.
15A @ 230VAC is about 4.6HP. 4.2HP @ 208V. That's assuming 100% efficiency, so more like 4HP tops in real life.
Where do you get that from. A motor drawing 15 amps at 240v is about 3hp according to the info I have.
1 HP = 746W.
15A * 230V = 3450W.
3450W / 746W = 4.62HP.
That assumes 100% efficiency, which no motor has.
So at a best case scenario of 85% efficiency (possible, but inlikely since even 80% is considered "high efficiency", and that comes at a cost) you'd have 3.93HP.
At a 60% efficiency like ArthurPE suggested, you'd get 2.77HP.
So like I said, best case scenario you'd have about 4HP, but more likely much less.
5HP at 230VAC/15A is impossible, so somone is clearly fudging the numbers somewhere.
the actual effeciency of modern motors > 90% in larger HP...
it's the power factor that affects the power...
P = V I pf
pf = cos of the phase angle between V and I due to the inductive nature of the load...most 1 ph motors are ~ 0.60 range
efficincy = Pout/Pin...so for a 5 HP motor with 80% eff Pin = 4660 W, 6.25 HP
with a unity pf that's still 20A, with a pf of 0.8, 25A...
We're talking 3HP motors here. Hardly "larger HP".the actual effeciency of modern motors > 90% in larger HP...
Sounds like something I said earlier in the thread...the 5 HP is a peak torque number, not running...running is <3....
It's probably 5hp peak. I.e., marketing HP.
Actually, most single-phase induction motors in the 5 hp range are about 90% pf
or better
We're talking 3HP motors here. Hardly "larger HP".It's also single phase. The more efficient "larger HP" motors are typically 3-phase.
Again a simple question gets blown completely out of proportation.
"mike in ohio" has left the building.
Again a simple question gets blown completely out of proportation.
"mike in ohio" has left the building.
really?
3 phase motors are in that range
and 1 phase is MUCH less efficient than 3 phase for obvious reasons...
hence a 5 HP motor drawing 28 A per code
pf = (5 x 746)/(28 x 230) ~ 0.58...
it's hard to seperate pf from eff...but the eff is ~ 80%
therefore pf ~ 0.58/0.8 ~ 0.72, not close to 0.90

My bad - you are correct. I got 3P on mind!
![]()