Finally got wife-approval of finishing the garage. It's also hastened by my acquisition of a Millermatic 180 and the need for 230v service. Here's my plan tell what you think.
Electrical Plan for Attached Garage
Garage is 22 X 23 deep, 12' ceilings
Constant loads Lighting, beer fridge
Auto loads: 33gal, 110v compressor
1. Main Service to garage
100A double-pole breaker in main service panel (200A) in basement
3-3-3-6 Copper cable to subpanel (not sure if this is readily available, run is approx. 30' so cost of copper is negligible)
2. Sub Panel (Square D, same as house)
125A/12 space panel with 100A main breaker - going with a main panel due to typical 100A/6 space not being big enough
3. Breakers (Square D, same as house)
50A/230V for welder - 11' run of 8-8-10 Cu to 6-50r receptacle... welder only requies 30A service, but I decided to upgrade.
20A for garage door opener
20A's for outlets - planning on using rows of double gang boxes on North & South wall with outlets alternating between circuits, so there'll be: left North, right North, left South & right South circuits (saw someone else do this on here, makes sense)... probably 4 receptacles per circuit, 4 circuits total
20A for compressor - not sure where the compressor will be, but would like to run it off a dedicated circuit
15 amp for lighting - fluorescent (8) dual 8' T12 (75w per bulb) plugged into receptacles in the ceiling (currently have 2 incandescents)... these lights are currently on the kitchen light circuit
Note: 1st outlet in string will be GFCI outlets to protect the rest of the string.
Issues:
1. I suspect the answer is NO, but can I run the 3-3-3-6 thru the common wall to the new subpanel? The existing main service comes in the NW corner of the garage and runs up the attic and then down into the basement to the load center. It would cut the run in half to go directly thru the common wall, but I suspect that code prevents this due to fire protection.
2. Do I have to run the 6-6-6-3 THHN in conduit or should I (can I?) get some sort of all-in one cable? I'd imagine the boys at the electrical supply house could help me with this as well.
3. Do the 4 circuits of alternating 4 outlets make sense or should I be thinking something else?
4. Think I should add some 20A outlets in the ceiling, just because?
5. Receptacles in ceiling for plugging in lights an acceptable way to go? I'm planning this as this is what I'm used to.
6. How much PITA is it going to be to change lighting circuit from the kitchen to the new subpanel? The switch is on the common wall (the only one with drywall) and the wire runs thru the attic, so I'm anticipating a PITA. The kitchen light circuit currently has 2 - 50w bulbs and 5 - 60w bulbs plus the 2 - 75w garage lights. My calculations show I could put some of the lights I want on that circuit and no exceed the 1440w limit (80% of 15A @ 120v) if I reduce to 6 fixtures, but I hate reducing light as you can never have too much. I could keep the lights on the kitchen circuit, convert to 2-4 fluorescent fixtures and then add a light circuit & switch in the subpanel for additional lights, essentially making zone lighting. Maybe rewiring the switch won't be that big a deal, just not sure where everything goes and I hate pulling wire thru finished construction.
Thanks for looking
Electrical Plan for Attached Garage
Garage is 22 X 23 deep, 12' ceilings
Constant loads Lighting, beer fridge
Auto loads: 33gal, 110v compressor
1. Main Service to garage
100A double-pole breaker in main service panel (200A) in basement
3-3-3-6 Copper cable to subpanel (not sure if this is readily available, run is approx. 30' so cost of copper is negligible)
2. Sub Panel (Square D, same as house)
125A/12 space panel with 100A main breaker - going with a main panel due to typical 100A/6 space not being big enough
3. Breakers (Square D, same as house)
50A/230V for welder - 11' run of 8-8-10 Cu to 6-50r receptacle... welder only requies 30A service, but I decided to upgrade.
20A for garage door opener
20A's for outlets - planning on using rows of double gang boxes on North & South wall with outlets alternating between circuits, so there'll be: left North, right North, left South & right South circuits (saw someone else do this on here, makes sense)... probably 4 receptacles per circuit, 4 circuits total
20A for compressor - not sure where the compressor will be, but would like to run it off a dedicated circuit
15 amp for lighting - fluorescent (8) dual 8' T12 (75w per bulb) plugged into receptacles in the ceiling (currently have 2 incandescents)... these lights are currently on the kitchen light circuit
Note: 1st outlet in string will be GFCI outlets to protect the rest of the string.
Issues:
1. I suspect the answer is NO, but can I run the 3-3-3-6 thru the common wall to the new subpanel? The existing main service comes in the NW corner of the garage and runs up the attic and then down into the basement to the load center. It would cut the run in half to go directly thru the common wall, but I suspect that code prevents this due to fire protection.
2. Do I have to run the 6-6-6-3 THHN in conduit or should I (can I?) get some sort of all-in one cable? I'd imagine the boys at the electrical supply house could help me with this as well.
3. Do the 4 circuits of alternating 4 outlets make sense or should I be thinking something else?
4. Think I should add some 20A outlets in the ceiling, just because?
5. Receptacles in ceiling for plugging in lights an acceptable way to go? I'm planning this as this is what I'm used to.
6. How much PITA is it going to be to change lighting circuit from the kitchen to the new subpanel? The switch is on the common wall (the only one with drywall) and the wire runs thru the attic, so I'm anticipating a PITA. The kitchen light circuit currently has 2 - 50w bulbs and 5 - 60w bulbs plus the 2 - 75w garage lights. My calculations show I could put some of the lights I want on that circuit and no exceed the 1440w limit (80% of 15A @ 120v) if I reduce to 6 fixtures, but I hate reducing light as you can never have too much. I could keep the lights on the kitchen circuit, convert to 2-4 fluorescent fixtures and then add a light circuit & switch in the subpanel for additional lights, essentially making zone lighting. Maybe rewiring the switch won't be that big a deal, just not sure where everything goes and I hate pulling wire thru finished construction.
Thanks for looking