Cleaning up the old stuff and redoing the utility room in the basement. This room has the furnace and water heater(gas), water utilities, a toilet and wash sink, washer and dryer(gas), fridge and then a light or two(LED). So for electrical I'm going to need a circuit for the furnace, and then outlets for fridge, washer, gas dryer and lights. Fridge is 11.6A, dryer is 6A and washer is 8A.
My thought is to run a 12-3 wire for two 20A circuits in there and then another dedicated circuit for the furnace. So thinking to put the fridge on it's own circuit and then the washer and dryer on a circuit together since they are only 14 amps together. The washer and dryer are allowed to be together I believe? Then I could put the lights on either of those circuits. Or if it would be better I could put the lights on with the rest of the basement lights? I'm planning on redoing the rest of the basement in the near future so could just run another 15A circuit for the utility room lights for now and plan on tying the other basement lights into that circuit when I do them if that is a better way to do it? Does my plan for the circuits sound good or would you do it another way?
The washer will be next to the sink so I think that has to be a GFCI outlet right? So should I run the wire to washer first and then to dryer so they are both GFCI protected then?
Does the fridge need to be GFCI protected being that it's in a basement? Is there a code that the outlets should be at a certain height? My plan is to put them just above the washer and dryer so they are accessible. The walls are block so planning to use 4 square boxes with conduit running up to the floor joists. Is that fine to run romex from the panel in the floor joists and then stick it down the conduit? I know romex isn't supposed to go in conduit but it's only going to be a couple feet down the wall.
If I wanted another outlet in there just to be able to plug something in if needed can I put that on with one of the other circuits? If so which circuit? And is there any code as to what height this outlet has to be?
The furnace says "max amps 12.0, FLA 11.0, HP 1.0", should I do a 15 or 20 amp circuit for it? Right now there is a 20 amp but the romex is run sloppy so want to redo it anyway so could do either 15 or 20 amp.
My thought is to run a 12-3 wire for two 20A circuits in there and then another dedicated circuit for the furnace. So thinking to put the fridge on it's own circuit and then the washer and dryer on a circuit together since they are only 14 amps together. The washer and dryer are allowed to be together I believe? Then I could put the lights on either of those circuits. Or if it would be better I could put the lights on with the rest of the basement lights? I'm planning on redoing the rest of the basement in the near future so could just run another 15A circuit for the utility room lights for now and plan on tying the other basement lights into that circuit when I do them if that is a better way to do it? Does my plan for the circuits sound good or would you do it another way?
The washer will be next to the sink so I think that has to be a GFCI outlet right? So should I run the wire to washer first and then to dryer so they are both GFCI protected then?
Does the fridge need to be GFCI protected being that it's in a basement? Is there a code that the outlets should be at a certain height? My plan is to put them just above the washer and dryer so they are accessible. The walls are block so planning to use 4 square boxes with conduit running up to the floor joists. Is that fine to run romex from the panel in the floor joists and then stick it down the conduit? I know romex isn't supposed to go in conduit but it's only going to be a couple feet down the wall.
If I wanted another outlet in there just to be able to plug something in if needed can I put that on with one of the other circuits? If so which circuit? And is there any code as to what height this outlet has to be?
The furnace says "max amps 12.0, FLA 11.0, HP 1.0", should I do a 15 or 20 amp circuit for it? Right now there is a 20 amp but the romex is run sloppy so want to redo it anyway so could do either 15 or 20 amp.