Bad Habit
Well-known member
So, had a metal roof installed on our manufactured home. The State of WA, Department of Labor and Industries controls everything associated with Manufactured and Mobile Homes, along with all Electrical in the state. Seems they want to make sure every aspect of these structures is over scrutinized and regulated.
They require the roof to be bonded in 2 places, opposite corners of the structure down to the frame of the home. As I'm not really sure what the best way to attach a bonding wire (#8 min) to a tin can, I called the manufacturer (based here in WA) and asked them. They sort of chuckled and said they scratch their head about it too and didn't have any official info but gave me some ideas. So, I ended up with a crimped lugs, bolted through the seams, using paint piercing star washers at 2 places. Then brought these 2 bonding wires down and attached them to the service ground. I didn't attach them at the far corners however, I attached them under the ridge cap and ran the wire for the far one under the cap to keep it nice and tidy.
So, the inspector failed it. Because they apparently do inspections at random times, after some indeterminate amount of calendar days after the inspection request(s), no one was there at the time. I'm hoping he just didn't see what he expected to see and thought nothing was done, or maybe it's just got to be done the way he thinks it should be.
Anybody here have any experience with bonding a metal roof? No solar or power up there of any kind. Haven't seen anything saying why it would be a requirement other than the State saying it is.
They require the roof to be bonded in 2 places, opposite corners of the structure down to the frame of the home. As I'm not really sure what the best way to attach a bonding wire (#8 min) to a tin can, I called the manufacturer (based here in WA) and asked them. They sort of chuckled and said they scratch their head about it too and didn't have any official info but gave me some ideas. So, I ended up with a crimped lugs, bolted through the seams, using paint piercing star washers at 2 places. Then brought these 2 bonding wires down and attached them to the service ground. I didn't attach them at the far corners however, I attached them under the ridge cap and ran the wire for the far one under the cap to keep it nice and tidy.
So, the inspector failed it. Because they apparently do inspections at random times, after some indeterminate amount of calendar days after the inspection request(s), no one was there at the time. I'm hoping he just didn't see what he expected to see and thought nothing was done, or maybe it's just got to be done the way he thinks it should be.
Anybody here have any experience with bonding a metal roof? No solar or power up there of any kind. Haven't seen anything saying why it would be a requirement other than the State saying it is.
So to me the NEC need is good enough...