Breaker question

scofo

Well-known member
Joined
Mar 5, 2008
Messages
1,071
Location
Northshore of Lake Travis. Marble Falls, Texas.
I'm replacing the central HVAC furnace, evap, line set and condenser in my mobile home. 22 years ago I supplied and wired the breaker and external disconnect for the comp/condenser. It was supposed to be protected for 60amps @230v. It never tripped for the life of the old unit. I can't recall what led me to choose the pictured breaker.

The new comp/condenser calls for 40amps @230v protection. Do I need a breaker that is labeled 20a on each leg instead of the current ;-) breaker's 30a on each leg or did I just get lucky and the old unit ran fine on a severely under spec'd breaker? Thanks in advance
 

Attachments

  • 16349197862587304883311060609732.jpg
    16349197862587304883311060609732.jpg
    358.9 KB · Views: 51
To avoid these ads, REGISTER NOW!

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
12,061
Location
Austin, TX
Buy the look of the wires on that breaker, the wires are not rated for 60A. They look like solid 10GA wire to me, which is good for 30A.

Post up the data plate on the HVAC unit. You'll get more help that way. The way you are thinking about it (split current per leg) is not correct.
 
OP
S

scofo

Well-known member
Joined
Mar 5, 2008
Messages
1,071
Location
Northshore of Lake Travis. Marble Falls, Texas.
Well hell, I bought this one the other day thinking this would be 40amps of protection at 230v. Thinking the new unit would draw less current than the old one. I didn't even see a double pole 40 on the shelf for a square D homeline box. Still a bit confused maybe the 22year old r22 condenser required less current. I left the cover off the old one when i diagnosed the old compressor motor had windings shorted, so the old info sticker is gone.

If I truly need a double 40a to meet spec I would need to update wire size it would seem. I sure didn't want to buy wire right now.
16349307065107162399504559428905.jpg
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
That unit could be wired with 12 AWG THWN or 10 AWG NM cable with a 40A breaker. Since 10/2 NM cable is existing it’s fine with a 40A breaker.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,136
Location
Central Iowa
The 10/2 wire is fine. You will probably be ok using the 30 amp breaker too. If the breaker does trip, you can install a 40 amp breaker. It will look just like the breaker you posted, but have a 40 in place of the 20.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
I'm replacing the central HVAC furnace, evap, line set and condenser in my mobile home. 22 years ago I supplied and wired the breaker and external disconnect for the comp/condenser. It was supposed to be protected for 60amps @230v. It never tripped for the life of the old unit. I can't recall what led me to choose the pictured breaker.

The new comp/condenser calls for 40amps @230v protection. Do I need a breaker that is labeled 20a on each leg instead of the current ;-) breaker's 30a on each leg or did I just get lucky and the old unit ran fine on a severely under spec'd breaker? Thanks in advance
60a @ 240v would be a double pole breaker with 60a on both sides
40a @ 240v would be a double pole breaker with 40a on both sides

the 20a DP breaker you have is NOT 40a, it is 20a..... you dont add up the ampacity rating of each pole on the breaker....
Well hell, I bought this one the other day thinking this would be 40amps of protection at 230v. Thinking the new unit would draw less current than the old one. I didn't even see a double pole 40 on the shelf for a square D homeline box. Still a bit confused maybe the 22year old r22 condenser required less current. I left the cover off the old one when i diagnosed the old compressor motor had windings shorted, so the old info sticker is gone.

If I truly need a double 40a to meet spec I would need to update wire size it would seem. I sure didn't want to buy wire right now.
well we dont know how much current the old one drew as the breaker rating is not the load rating.... but if it required a 60a DP breaker, then it most likely drew more current than your new unit....

no you dont need to upsize the wire

AC circuit wiring is size by the MCA- minimum circuit amps. for your case the 10/2 is just fine since its rated for 30a. the breaker is oversized to stop nuisance tripping and it doesnt protect the wire from overloads. thats the job of the integral overloads in the motor....
 
OP
S

scofo

Well-known member
Joined
Mar 5, 2008
Messages
1,071
Location
Northshore of Lake Travis. Marble Falls, Texas.
Okay, got it. Thanks guys. 10/2 cable will stay and I'll trade my newly purchased 20a for a brite and shiny 40a breaker.

I guess I dont recall clearly what the old compressor was suppose to be protected at. Maybe I was thinking of the service disconnect. Its rated at 60a. Maybe that's where I pulled that figure out of the 22year old recollection.

Anyhow much oblighed
 
Last edited:
To avoid these ads, REGISTER NOW!

rawen2

Well-known member
Joined
Feb 26, 2021
Messages
173
Location
High Desert of CO
I'm not an electrician but isn't the max breaker size for 10 ga wire 30 amps?

Oops. Meant to quote scofo:
"Okay, got it. Thanks guys. 10/2 cable will stay and I'll trade my newly purchased 20a for a brite and shiny 40a breaker."
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
I'm not an electrician but isn't the max breaker size for 10 ga wire 30 amps?

Oops. Meant to quote scofo:
"Okay, got it. Thanks guys. 10/2 cable will stay and I'll trade my newly purchased 20a for a brite and shiny 40a breaker."
For general circuits yes. For motor and air conditioner condensor circuits no... have to read the exceptions to the ampacity rules in 240
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,893
Location
NW Iowa
I'm not an electrician but isn't the max breaker size for 10 ga wire 30 amps?

Oops. Meant to quote scofo:
"Okay, got it. Thanks guys. 10/2 cable will stay and I'll trade my newly purchased 20a for a brite and shiny 40a breaker."
In this case you're limited to 30A of load. The AC in question pulls about 19A +125% so #10 is fine. It needs the 40A breaker for startup.
 

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
Okay, got it. Thanks guys. 10/2 cable will stay and I'll trade my newly purchased 20a for a brite and shiny 40a breaker.

I guess I dont recall clearly what the old compressor was suppose to be protected at. Maybe I was thinking of the service disconnect. Its rated at 60a. Maybe that's where I pulled that figure out of the 22year old recollection.

Anyhow much oblighed
No need to use a 40a breaker,30a 2p is plenty.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Minimum circuit ampacity is 23.4 amps, so a # 10 is required. Maximum fuse/breaker is 40 amps . Nothing wrong with a 40 amp breaker on a #10 wire when it is a motor/AC circuit. It is allowed to be oversized for start up current. If you have a 30 amp already. Then you could try it, but personally if this was me installing this circuit for a customer, i would use a 40 amp to prevent a possible call back.
 
Last edited:

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,893
Location
NW Iowa
Yea, maybe if you already had a 30 I'd say try it. If you're going to buy a breaker anyway why wouldn't you get what it calls for.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,893
Location
NW Iowa
I install install lots of condensing units ,a 30a 2p is by far the most common breaker I ever come across in the field.
Unless you're installing a 4-5t condensing unit.
No one's saying it can't work. Just that if he's got to go out and buy a breaker why wouldn't you get what it calls for.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
I have wired a lot of condensers on a 30 amp. But I always check the plate and size the breaker per that. A lot of them now still need a #10 but only have a maximum breaker of 25 amps. So now I keep a few 25 amp breakers on the truck.
 