To avoid these ads, REGISTER NOW!

Campbell Hausfeld TQ3104

BretD

Member
Joined
Dec 26, 2017
Messages
5
Greetings, I recently had to purchase a replacement compressor for my shop and bought a CH TQ3104 5 h.p. 80 gal, single phase 230v unit, little larger than my last one that died. Paperwork recommends using 8 ga wire to power unit, that seems rediculously large. I would think 10 would be plenty - paired with a 30 amp double breaker. Any suggestions are appreciated. Very Best, Bret
 
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,931
Location
NW Iowa
If your using romex then #8 is required for a 5 hp motor. If your using wire in conduit then you could use #10 because you can use the higher temperature rating.

Max breaker size would be 70A, I would recommend a 40A minimum.
A 30A breaker may trip on startup with a real 5hp motor.
 
OP
B

BretD

Member
Joined
Dec 26, 2017
Messages
5
Thank you sir. The 10 gauge i was thinking of using is a rubber body 3-conductor stranded. I see what you're saying about if I were using romex. I will go with the 40amp on the breaker. Thanks again, Bret
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,279
Location
Modesto, CA
Thank you sir. The 10 gauge i was thinking of using is a rubber body 3-conductor stranded. I see what you're saying about if I were using romex. I will go with the 40amp on the breaker. Thanks again, Bret

Sounds like youre referring to cordage which cannot be used in place of building wire.
 
OP
B

BretD

Member
Joined
Dec 26, 2017
Messages
5
I'm talking about the cord / wire to connect the compressor to the wall outlet. These compressors do not come with a cord. My apology for not making that clear.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,279
Location
Modesto, CA
I'm talking about the cord / wire to connect the compressor to the wall outlet. These compressors do not come with a cord. My apology for not making that clear.

If that compressor is truly 5HP then you cannot use an attachment plug and outlet. It must be hardwired.
 
To avoid these ads, REGISTER NOW!
OP
B

BretD

Member
Joined
Dec 26, 2017
Messages
5
So... coming from a 230 outlet six feet away requires it hard-wired rather than being plugged in? I appreciate the information.

Bret
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,279
Location
Modesto, CA
So... coming from a 230 outlet six feet away requires it hard-wired rather than being plugged in? I appreciate the information.

Bret

Yes because there are no nema plugs or outlets rated for more than 3HP.

86 the outlet and do a hardwired whip from the PS to a j box on the wall.

You need #10 THHN in pipe or #8/2 NM-b for the circuit conductors.
 

shaggyant

Well-known member
Joined
Oct 10, 2011
Messages
201
Location
North Idaho
If that compressor is truly 5HP then you cannot use an attachment plug and outlet. It must be hardwired.

Not true, I use pin and sleeve style connectors for motors at work all the time. There are connectors rated for up to 100 horsepower.

However, I agree that the OP does not need or want a $500 plug and receptical connection and would be much better off hard wiring a compressor that will probably be bolted to the floor anyway.

Edit: link added

https://www.mc-mc.com/ASSETS/DOCUMENTS/ITEMS/EN/10362_APPA_specsheet.pdf
 
Last edited:

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,796
Although it's common around here to cord & plug connect furnaces in the attic, it is not really compliant to cord & plug connect a permanently installed piece of equipment, used the furnace as a example only.

wyliesdiesels did mention NEMA connectors which pin & sleeve connectors are not.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,279
Location
Modesto, CA
Not true, I use pin and sleeve style connectors for motors at work all the time. There are connectors rated for up to 100 horsepower.

However, I agree that the OP does not need or want a $500 plug and receptical connection and would be much better off hard wiring a compressor that will probably be bolted to the floor anyway.

Edit: link added

https://www.mc-mc.com/ASSETS/DOCUMENTS/ITEMS/EN/10362_APPA_specsheet.pdf

Doubt there is one person on here willing to spend as much money on an attachment plug as the whole compressor cost. That is why i didnt mention it. So pin and sleeve plugs and outlets are irrelevant.
 