Can I get 220 with this existing wiring?

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
An MWBC is only allowed to serve line to neutral loads (210.4(C)).
(C) Line-to-Neutral Loads. Multiwire branch circuits shall
supply only line-to-neutral loads.

Exception No. 1: A multiwire branch circuit that supplies only one
utilization equipment.
Exception No. 2: Where all ungrounded conductors of the multiwire
branch circuit are opened simultaneously by the branch-circuit overcurrent
device.


(AKA You have to have a common trip breaker)
 
Last edited:
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,268
Location
Modesto, CA
I just wanted to clear my part of this up. We all know, and hopefully the OP knows, that bringing current to the red wire cannot be from the same buss as the black. Said and done. What's left is the possibility of a MWBC. I did not know that was possible to an outbuilding. Then other possibility is a 240v supply to the existing panel in the garage. This is depending on the existing wire size. No point in doing 240v on 12 ga. or less as providing branch circuits in the garage would be limited to that which can be done with, say a 20 A MWBC on 12 ga. IOW, no ability to have both 120v individual circuits AND a 240v circuit in that existing panel unless the wire ga will support that.

Seems like the discussion did go 'off the rails' a bit but it's been an informative thread.

Now we must get down to brass tacks and determine what exactly this "armored cable" has AFA wire gauge.
And since the OP is not likely to change out the fused circuit to the garage, talk about tandem and quad breakers is moot.

One more thing: looking at Post #1 and the pics, I don't see how 3 breakers in a row on one side of that subpanel are all on the one leg. What am I missing there?

every single 3-wire (120/240v) and 4-wire feeder we discuss on this group is an MWBC. The service feeding your house is an MWBC.
 

TRWham

Well-known member
Joined
Aug 11, 2017
Messages
2,021
Location
East Cobb County, Georgia
Incorrect. Exception #2 allows for 240V loads on a MWBC when a breaker that trips both poles together is used.

Handle ties cover 210.4B for line to neutral loads, but for 240V line to line loads, you need a manufactured two pole breaker. Fuses of course are not acceptable.

(C) Line-to-Neutral Loads. Multiwire branch circuits shall
supply only line-to-neutral loads.

Exception No. 1: A multiwire branch circuit that supplies only one
utilization equipment.
Exception No. 2: Where all ungrounded conductors of the multiwire
branch circuit are opened simultaneously by the branch-circuit overcurrent
device.


(AKA You have to have a common trip breaker)

Yeah, I did not account for the exceptions.
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
every single 3-wire (120/240v) and 4-wire feeder we discuss on this group is an MWBC. The service feeding your house is an MWBC.

Understood. The issue remains as to how best solve the OP's circumstances. I suspect he's lost interest in all the technical comments.

This is a good thread with a lot of useful information and some of the forum's best contributors chiming in.
 