I want to convert my band saw and jointer to use 240 volts. I have the wire diagram for the motors and have no questions on that. The manual says that for 120 v, I should use a 5-20 plug, which is what it came with. For 220 v, it says to use a 6-15 plug.
So far, so good.
My 220 circuit is 20A so I will use a 6-20 plug.
You just de-railed.
While there may be some justification for using a 6-20R receptacle in the outlet box (tho' very little justification, if the outlet will be dedicated to that tool), there is
NO good reason to use a 6-20P on the tool itself, since it will ALWAYS draw (much) less than 15 amps @ 240V. Note that if you compare the two plug/socket types:
http://upload.wikimedia.org/wikipedia/commons/0/0d/NEMA_simplified_pins.svg
You will see that the 6-15P
WILL fit into the 6-20R.
The power cord on the band saw is made up of 16 gauge wire, according to the spec sheet. If, when running on 120v, it recommended a 20 A circuit, why does it have a 16 Gauge cord on it? I thought you needed a 12 gauge wire for a 20A circuit.
As others have pointed out, the "official" requirement to use AWG 12 (or heavier) for a 20A circuit is limited to permanently installed wiring. Plug-in power cords on (even nominally) "portable" devices are not covered by those regulations/standards.
That said, AWG 16 DOES seem somewhat on the light side for that application, by my lights, particularly if the power cord is more than a foot or two long.
Should I replace it when I get the new plug?
If that same AWG 16 cord worked OK at 120V, it will surely work OK (even better, really) at 240V, since it will now need to carry only half as much current to power the tool. So the short answer is, you probably don't NEED to replace the cord. But if you WANT to replace it with something a bit heavier, it surely won't hurt. The only cautionary note I'll sound is to make sure that wherever the cable connects inside the tool, the terminals will correctly accommodate the heavier wire.
And if I do replace the power cord, what do I replace it with? It obviously can’t just be a piece of romex and I doubt it would be an ‘extension cord’.
Actually, you very probably could cannibalize an old extension cord, if it was of adequate AWG and had the right sort of plug on it; but that probably would not be cost-effective if the extension cord is otherwise usable as-is. Ideally, you'd want some 3-conductor Type SOOW cord, of at least AWG 16 (but since most of the point of replacing the cord is to upgrade it, make that AWG 14 or heavier)
Systek P/N: 10523 would be suitable.
http://www.systekcable.com/wire/product_info.php?cPath=68&products_id=276
Or Omni B11403 / B11403-V:
http://www.onestopbuy.com//wire-cable/B11403-40198.asp?pt=frB11403
http://www.onestopbuy.com//wire-cable/B11403-V-42014.asp?pt=frB11403-V
Or, something like this
http://www.americord.com/6-15p-to-roj-2in-strip-1-4in.html
would also likely do the trick.
Assuming that the tool was designed properly from the factory, the wire was probably spec'ed out to meet the current draw of the tool based on whatever electrical standard the manufacurer certifies to. 16Ga stranded has a higher carrying capacity than solid (romex, etc.).
I would think the 16ga wire would be fine, there will be less amps drawn at 220v anyway (20A@120V = 11A@220V)
True, but it only is measurable, or having any noticeable effect under, if I recall, very high frequencies and voltages. given 60hz 120 or 240 v current, there will be no measurable difference in current carrying capacity of fine stranded vs solid. (even difficult to meausure under laboratory conditions, if even then).
Charles
Correct, sort of.
It's not even really a matter of "current carrying capacity", per se; but rather, stranded wire will exhibit somewhat less attenuation of VERY high-frequency (measured in MegaHertz, or at least dozens/hundreds of KiloHertz) signals than solid-core wire will. At 60 Hz, it is simply a non-issue.
I am not claiming to be an expert, but i have seen similar thoughts such as this:
Taking these "thoughts" one-by-one...
"since you have two wires carrying half of the amps, the wear on the switches are less,
Wrong. Wear on the switch contacts will be almost purely a matter of their mechanical properties vs. how often/roughly they are cycled. Higher-quality switches will last longer than cheap crappy switches.
OTOH, the higher voltage potential across the switch contacts MIGHT actually exacerbate wear, if it leads to (more) arcing.
the voltage drop is less,
True. HOWEVER, whether or not this will be significant in any given case depends on more variables than we have available here at the moment.
Maybe, but probably not
IF the building's electrical service is adequate and the wiring is designed and installed correctly. Your lights should not be on the same branch circuit(s) as your power tools (especially your BIG power tools). So if the lights are dimming AT ALL when you kick on one of those big machines, that implies that you're somehow dragging down the main feed to the sub-panel/building. If that is the case, the CORRECT cure is to upgrade the building's electrical service & wiring, not try to "skate by" by re-jiggering your tools to use slightly less current. In short, you'd be treating the symptom, instead of curing the disease.
and it balances the electrical load.
This depends on how "unbalanced" is is now, and why. In practice, it really shouldn't matter.
There is less heat, and wear on the motor it self.
Probably untrue -- or at least "mostly" untrue. While you are cutting the current in half, you are doubling the voltage; so exactly the same amount of POWER is being consumed. It is power which most closely correlates to heat.
IF the tool's internal wiring & such is inadequate, so that the higher current flow at 120V causes significantly more voltage drop, then going to 240V might somewhat ameliorate this; but then, this should NOT be the case in the first place, so...
There is faster recovery from bogging under heavy load and less bogging in general, which is an advantage in thicker materials."
Again, probably untrue, or at least "mostly" untrue, for most of the same reasons as in the previous answer, and again presuming that the building's electrical service and wiring are up to snuff.
Regardless, my 240 circuits are dedicated for my larger tools and my 120 lines are shared amongst my smaller tools. My jointer draws 15 amps at 120 and I don't want that to interfere with other things running on the 120 circuit.
Now THAT is actually a good reason to convert the stationary tools to 240V.

.