I want to run 6/3 copper cable (or individual wires in conduit) through my basement, from the main panel over to the other side of the house (30-40 feet), through the wall, and then mount one of the RV (or temporary power ) boxes on the exterior wall of the house. Most of these boxes provide a 20 amp GFCI receptacle, a 14-50, 50 amp 240 volt receptacle, and a 30 amp RV receptacle. I would use the 20 amp circuit for battery chargers, etc., and in the future want to use the 14-50 for a welder or for a plug-in EV charger. I don't currently have either a welder or RV charger, so those are future needs.
What confuses me a little is that the 14-50 receptacle is rated for 50 amps. If I plugged in an EV charger, some of them I've found draw up to 48 amps and the installation specs require a 50 amp breaker. If they are considered a 48 amp continuous load, don't you need a 60 amp circuit? Or maybe I don't understand the requirement.
Another option is to run #4 or larger cable to an exterior sub panel, and then install the temp/RV power box off that sub panel. However, then my cable costs go up a lot (unless I go to AL conductors), and it's harder to route it through the basement (bigger holes drilled in the joists, and/or use larger conduit).
What confuses me a little is that the 14-50 receptacle is rated for 50 amps. If I plugged in an EV charger, some of them I've found draw up to 48 amps and the installation specs require a 50 amp breaker. If they are considered a 48 amp continuous load, don't you need a 60 amp circuit? Or maybe I don't understand the requirement.
Another option is to run #4 or larger cable to an exterior sub panel, and then install the temp/RV power box off that sub panel. However, then my cable costs go up a lot (unless I go to AL conductors), and it's harder to route it through the basement (bigger holes drilled in the joists, and/or use larger conduit).