Code question - outlets

Mike662

Well-known member
Joined
Nov 19, 2009
Messages
303
Location
Colorado
Probably an obvious question, but there seems to be conflicting opinions on this.

If I run two separate circuits into the same box to power adjacent receptacles, do I need to use a double pole breaker for those circuits?

Here's my situation...I need to add a number of outlets around the garage. I was thinking that I'd like to install a series of double duplex outlets, with the outlet on the left on circuit #1 and the outlet on the right on circuit #2. That way, I could plug multiple tools in at the same location, without overloading a circuit.

I was planning to either color-code the outlets or label the outlet covers. And I was planning to pull two separate circuits from the panel, not do it as a MWBC with a shared neutral.

So, does the code require that I use a double pole breaker?

Thanks in advance! :thumbup:
 
To avoid these ads, REGISTER NOW!

bobadame

Well-known member
Joined
Dec 26, 2007
Messages
1,124
I just got dinged on this on my final electrical inspection. The inspector wanted me to use the type of 2 pole breaker that has the levers linked together. The reasoning is that without this, a person could turn off one breaker and still get zapped by the other circuit.
 

skeletonizer

Well-known member
Joined
Sep 25, 2008
Messages
1,320
Location
Michigan
I just got dinged on this on my final electrical inspection. The inspector wanted me to use the type of 2 pole breaker that has the levers linked together. The reasoning is that without this, a person could turn off one breaker and still get zapped by the other circuit.

Not sure about it being code or not but this makes sense to me and is how I would do it.
 

sdowney717

Well-known member
Joined
Mar 17, 2010
Messages
964
If you dont use a double pole breaker, someone might turn off the breaker think it is dead circuit and then he is working on it, but the other half is still live and he could be dead.
I suppose it makes sense.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I was planning to either color-code the outlets or label the outlet covers. And I was planning to pull two separate circuits from the panel, not do it as a MWBC with a shared neutral.

If you have several boxes like this, you might ask your supply house if they carry 12-2-2. It has two hots and two neutrals in one cable. It'll save you quite a bit of time...

If you dont use a double pole breaker, someone might turn off the breaker think it is dead circuit and then he is working on it, but the other half is still live and he could be dead.
I suppose it makes sense.

If a guy is too dumb to check power in a box after he shuts off the breaker he shouldn't be working with electricity. Period. This isn't rocket science..
 
Last edited:

Ray-CA

Well-known member
Joined
Jan 6, 2007
Messages
3,452
Location
San Diego CA
I was planning to either color-code the outlets or label the outlet covers.

That's basically what I did. I used orange outlets for one circuit and white for the other (these were the only two colors that I could find in sufficient numbers.)

Ray
 

yarddawg

New member
Joined
Aug 4, 2010
Messages
4
Nothing in the National Electrical Code against doing this. Your local codes may vary.
 

sdowney717

Well-known member
Joined
Mar 17, 2010
Messages
964
If a guy is too dumb to check power in a box after he shuts off the breaker he shouldn't be working with electricity. Period. This isn't rocket science..

The inspector is god I suppose.
 
To avoid these ads, REGISTER NOW!

robertlynk

Well-known member
Joined
Jun 1, 2010
Messages
323
Location
California
That's basically what I did. I used orange outlets for one circuit and white for the other (these were the only two colors that I could find in sufficient numbers.)

Ray

did you ground the orange receptacles properly? it is my understanding that the orange receptacles are grounded different than standard ie isolated ground
 

juicegoose

Well-known member
Joined
Aug 26, 2008
Messages
46
In line with the original poster but somewhat different question is this. If you want to run two duplex receptacle in adouble gang box like the original poster suggested and have them on seperate circuits can'tyou essentially run a 12-3 to the box, and share the neautral and ground of the 12-3 wire between the two circuits. Naturally at the panel you would have two 20amp breakers for the hots and the neutral and ground would go to the appropriate bus. Or am I mistaken and you can't share the neutral and ground of the 12-3 if your going to seperate the hots on two seperate circuits in the same box.
 

Ray-CA

Well-known member
Joined
Jan 6, 2007
Messages
3,452
Location
San Diego CA
did you ground the orange receptacles properly? it is my understanding that the orange receptacles are grounded different than standard ie isolated ground

Both sets of outlets were grounded the same way, there is no difference between them.

Ray
 

juicegoose

Well-known member
Joined
Aug 26, 2008
Messages
46
Answered my own question. For all that had this idea. If you are going to run two circuits off a single 12-3 wire they can share the neautral but at the panel you can not wire them on individual single pole breakers. They must be wired on a double pole breaker that has two 20 amp throws that are connected. This is to protect to neautral. The other option is to run two 12-2s for a single breaker.
 

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
Both sets of outlets were grounded the same way, there is no difference between them.

Ray

be carful what you say!!with isolated ground recep's the ground does not connect to the mounting strap.this is beacause where they used,they are installed in metal conduit.if ground was connected to strap,you could not isolate ground.recp's will be marked iso ground.not saying your's are iso recp's,just letting some here know the diff.
 

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
code say's that when both sides of a multi-wire ckt where a recp for each leg is mounted in the same box(two gang ect)has to have a two pole common trip breaker.the inspector is right.recp's or switches(devices)
 
Last edited:

sdowney717

Well-known member
Joined
Mar 17, 2010
Messages
964
on the 12/3 wire, I think that just ends up costing more money since you have to buy 12/3.
I know we had lots of extra 12/2 and there were times when I thought it would be nice to run 12/3 like in wiring up ceiling fans light with separate fan control.

Sometimes you need it for lights controlled from more than one switch.

wondering this here, say 12/3 to two oultets, the neutral gets shared. How about current flow threw that single neutral?
You got 2o wires feeding power and only one the same size returning it.
what happens when they are running close to ampacity of the circuit, will it overload the neutral? or is the power used up in the device.
 
Last edited:

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
on the 12/3 wire, I think that just ends up costing more money since you have to buy 12/3.
I know we had lots of extra 12/2 and there were times when I thought it would be nice to run 12/3 like in wiring up ceiling fans light with separate fan control.

Sometimes you need it for lights controlled from more than one switch.

wondering this here, say 12/3 to two oultets, the neutral gets shared. How about current flow threw that single neutral?
You got 2o wires feeding power and only one the same size returning it.
what happens when they are running close to ampacity of the circuit, will it overload the neutral? or is the power used up in the device.

NO.beacause you make a 240 ckt.they are on two diff phases.neutral only sees imballance current.
 

yarddawg

New member
Joined
Aug 4, 2010
Messages
4
code say's that when both sides of a multi-wire ckt where a recp for each leg is mounted in the same box(two gang ect)has to have a two pole common trip breaker.the inspector is right.recp's or switches(devices)

If he were running a multi-wire branch circuit, this would be correct. However, the OP specifically stated that he was not running an MWBC, therefore there is no NEC basis for an inspector to require a two pole common trip breaker.
 
OP
M

Mike662

Well-known member
Joined
Nov 19, 2009
Messages
303
Location
Colorado
Thanks again all.
The reason I wasn't going to run a MWBC was that I thought that GFI outlets could not be used. Now I realize that I can run a MWBC (12/3 romex) from the panel into the first box in the garage, put GFI outlets in that box, then chain the rest of the outlets from there using either 2 separate runs of 12/2 or the 12/2/2 (12/4) wire suggested above. Doing that, of course, will require a double pole breaker. Given the confusion, I probably would have used one either way, to avoid any unpleasantness with inspectors, etc.
 

oleguy

Well-known member
Joined
Nov 22, 2009
Messages
273
If he were running a multi-wire branch circuit, this would be correct. However, the OP specifically stated that he was not running an MWBC, therefore there is no NEC basis for an inspector to require a two pole common trip breaker.

just some info on the code.if that is ok with you...
 