jpcjguy
Well-known member
Hi all,
So i have made all my house side hookups and looking to install my 200A load center from Lowes (https://www.lowes.com/pd/Square-D-200-Amp-30-Spaces-60-Circuit-Main-Breaker-Plug-On-Neutral-Load-Center-Value-Pack/50311159 ).
I am thinking of mounting it upside down since that is where my feeder wires are coming from. It has the big knockouts in the center and found out they don't make a 2 1/2" offset PVC conduit fitting, max size is 2".
Suggestions? Wire size is 2/0 aluminum, I guess I could reduce to 2" conduit and then use the 2" offset coupling, or just angle the 2.5" conduit some?
Don't want the inspector to ding me for something...
So i have made all my house side hookups and looking to install my 200A load center from Lowes (https://www.lowes.com/pd/Square-D-200-Amp-30-Spaces-60-Circuit-Main-Breaker-Plug-On-Neutral-Load-Center-Value-Pack/50311159 ).
I am thinking of mounting it upside down since that is where my feeder wires are coming from. It has the big knockouts in the center and found out they don't make a 2 1/2" offset PVC conduit fitting, max size is 2".
Suggestions? Wire size is 2/0 aluminum, I guess I could reduce to 2" conduit and then use the 2" offset coupling, or just angle the 2.5" conduit some?
Don't want the inspector to ding me for something...