Do thermostats have a lockout for the compressor

Hobby_Man22

Well-known member
Joined
Nov 16, 2020
Messages
3,581
Location
tx
I read somewhere that said it's bad for the a.c. compressor to kick back on after a short period of being off. Mine will kick back on after 6-8 minutes in the heat of the day if I have the thermostat set low. Like 70. I've read that it needs a good 10 minutes to allow the pressure to go down before restarting again. Is this true? I just have too many air leaks in my building and that's why it does that. Unlike a house where it will stay off for a good 15-20 minutes.
 
To avoid these ads, REGISTER NOW!

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,750
Location
Long Island
I am not aware of thermostats that do exactly what you ask, but many smart thermostats will have programming to detect and possibly deal with short cycling.

I would suggest you replace your compressor contactor with a smart solid state unit that both prevents short cycling and brownout damage. Look into the Emerson 49P11-843 Sure Switch Relay

Also, perhaps you can increase the hysteresis range of your existing thermostat to extend the cycle times.
 
OP
H

Hobby_Man22

Well-known member
Joined
Nov 16, 2020
Messages
3,581
Location
tx
I do believe it has a 6 minute delay when switching between heating and cooling mode (heat pump) but I dont know if that extends to cycle times also where it prevents it from starting again for 6 minutes.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,894
Location
Fargo, ND
Some thermostats do have time delays built in, most do not. 6-8 minutes between cycles is fine, don't worry about it. The short time they talk about is 30 seconds, or maybe a minute. The pressures in the system will equalize in a short time. You just don't wan the compressor trying to start when the high side pressures are still up.
 
Last edited:
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,865
Location
NW Iowa
5 minute delay built into the thermostat is common. It's usually optional, you can turn it on or off.
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
Thermostats do typically have it built in now ...... there are also controls that you can put out at the compressor. It really depends on the age of all the components.

The old days with mercury switches -- no. You had to add it at the compressor. I first started seeing them built into the better condensers back in the 90's. With the advent of digital thermostats it seems the base units depend on the thermostats again.

Now the condensers have sensors and the thermostats talk to the condenser on the better units. If you are not holding temp for that short of a time you do have leaks/ insulation issues
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Most all thermostats have a delay, this allows your pressure's to equalize so the the compressor can start not under a load. I have also come across some condensors that also has a time delay in them
 