Electrical final inspect fix

alkech

Member
Joined
Sep 5, 2013
Messages
12
Thought the electrical final would be a breeze, but got a finding.

Didn't know fixtures hung by chain needs connected with stranded wire, not solid.

I only have two on chaings, all the others are afixed to the ceiling. So can I conclude if I just removed these fixtures off the chains and hard mounted these as well. that would satisfy the inspector?

Thanks
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Thought the electrical final would be a breeze, but got a finding.

Didn't know fixtures hung by chain needs connected with stranded wire, not solid.

I only have two on chaings, all the others are afixed to the ceiling. So can I conclude if I just removed these fixtures off the chains and hard mounted these as well. that would satisfy the inspector?

Thanks

He might go for it, but many of the fixtures that come with chains and hangars are not designed or approved to be hard mounted, as they get too hot.

Charles
 
OP
A

alkech

Member
Joined
Sep 5, 2013
Messages
12
He might go for it, but many of the fixtures that come with chains and hangars are not designed or approved to be hard mounted, as they get too hot.

Charles

Thanks for your response. They are 4' foot tandems. I have 10 hard mounted already and didn't get any grief about them. Just assumed if I hard mounted the last two like the other 10 it would suffice?
 
OP
A

alkech

Member
Joined
Sep 5, 2013
Messages
12
Merely replace the solid wire with zip cord.

Easy, cheap fix.

Uncle Bob

Thanks for your response.

I have Romex connecting them now. Could I just wire nut the appropiate size stranded to the Romex and connect?
 
To avoid these ads, REGISTER NOW!

sweetcretin

Well-known member
Joined
Oct 3, 2013
Messages
45
Location
Fargo, ND
Thanks for your response. They are 4' foot tandems. I have 10 hard mounted already and didn't get any grief about them. Just assumed if I hard mounted the last two like the other 10 it would suffice?

Don't assume that lack of comment by the inspector means that the fixtures are rated for the application; verify it yourself. The risk of fire far outweighs the 15 minutes to read the manual or look up the model on the internet. Just because it was inspected doesn't mean it's correct, it just means it was inspected.
 

JoeFin

Well-known member
Joined
Sep 13, 2013
Messages
717
Location
NorCal - where the Rednecks Race
Might want to check the code on want type of wire you use. Some of the options for stranded wiring are classified as "Temporary" wiring and may not be installed through the sheetrock or affixed to the permanent wiring.

Usually SO cord plugged into a receptacle works out fine depending on how much of a **** your inspector wants to be
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Use a whip.

PWHP-2A.jpg
 
OP
A

alkech

Member
Joined
Sep 5, 2013
Messages
12
Don't assume that lack of comment by the inspector means that the fixtures are rated for the application; verify it yourself. The risk of fire far outweighs the 15 minutes to read the manual or look up the model on the internet. Just because it was inspected doesn't mean it's correct, it just means it was inspected.

Yes, Simkar offers a variety of attachments to mount to the ceiling, although I did not use them.
 
OP
A

alkech

Member
Joined
Sep 5, 2013
Messages
12
I am getting the feeling I should just leave them as is and use the appropriate wire. As mentioned, right now I have Romex connecting them. So, could I just splice the Romex and wire nut the stranded to that, and then shove the wire nuts in the drywall so all you would see is the stranded running down to the fixtures?

Sounds sneaky.
 

signcrafter

Well-known member
Joined
May 9, 2012
Messages
12,660
I am getting the feeling I should just leave them as is and use the appropriate wire. As mentioned, right now I have Romex connecting them. So, could I just splice the Romex and wire nut the stranded to that, and then shove the wire nuts in the drywall so all you would see is the stranded running down to the fixtures?

Sounds sneaky.

NO NO NO

You can not have splices inside or wall. They must be inside a junction box. The easiest way to fix this is to cut the romex and put a receptacle and box where the romex comes out of the drywall. Then just wire the light with a whip to plug into the outlet.
 
OP
A

alkech

Member
Joined
Sep 5, 2013
Messages
12
NO NO NO

You can not have splices inside or wall. They must be inside a junction box. The easiest way to fix this is to cut the romex and put a receptacle and box where the romex comes out of the drywall. Then just wire the light with a whip to plug into the outlet.

Many thanks for the firm response, I will go this route.
 