Electrical wire check before purchase

1/4atatime

Well-known member
Joined
Jun 9, 2024
Messages
164
Location
VA
I'm getting ready to run the wire to my new garage and want some confirmation I'm purchasing the right things.

Here is my current order for the wire part of the installation
Screenshot_20250408_151819_Brave.jpg

So my understanding is that I can't run MHF under the house so that's what the SER will be for and I'll put that in conduit. Then I need to transition that out to the MHF so I'll use the inline splicers to handle that. The only question I guess I had was if I can run the MHF directly from outside into the panel in the garage or if I need a short piece of SER and more splicers. From what I've seen most just run it directly and not considered inside usage. Also I'll be using the 2 8ft 5/8 grounding rods and 6 awg copper so I can run it next to the building unprotected. I'm running 20amp outlets so I'll be using 12/2 MC for an all in one and save on conduit cost as local inspectors seem to be cool with MC around me in garages.
 
To avoid these ads, REGISTER NOW!

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,067
Location
Central Iowa
I'm getting ready to run the wire to my new garage and want some confirmation I'm purchasing the right things.

Here is my current order for the wire part of the installation
Screenshot_20250408_151819_Brave.jpg

So my understanding is that I can't run MHF under the house so that's what the SER will be for and I'll put that in conduit. Then I need to transition that out to the MHF so I'll use the inline splicers to handle that. The only question I guess I had was if I can run the MHF directly from outside into the panel in the garage or if I need a short piece of SER and more splicers
You can use MHF wherever you want to, it just has to be in conduit when it's not underground.
. From what I've seen most just run it directly and not considered inside usage. Also I'll be using the 2 8ft 5/8 grounding rods and 6 awg copper so I can run it next to the building unprotected. I'm running 20amp outlets so I'll be using 12/2 MC for an all in one and save on conduit cost as local inspectors seem to be cool with MC around me in garages.
You can use 20 amp outlets if you think it's neccessary, but you can use 15 amp receptacles on a 20 amp circuit as circuit as long as it's not a single. MC is fine, it just has to be protected from damage, which isn't defined so it's up to the AHJ.
 
OP
1

1/4atatime

Well-known member
Joined
Jun 9, 2024
Messages
164
Location
VA
You can use MHF wherever you want to, it just has to be in conduit when it's not underground.
Huh well SER is cheaper and I from what I understand that's fine in conduit under the crawlspace right? Just MHF has to be outdoors
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,067
Location
Central Iowa
Huh well SER is cheaper and I from what I understand that's fine in conduit under the crawlspace right? Just MHF has to be outdoors
MHF can be used anywhere, indoors or outdoors. It has to be in conduit when it's not underground. You can use SER if you want to. You might be able to route MHF so there are no splices, thus eliminating at least one junction box and splice taps.

SER can't be underground so if you want to use that, you'll have to splice it to the MHF.
 
OP
1

1/4atatime

Well-known member
Joined
Jun 9, 2024
Messages
164
Location
VA
MHF can be used anywhere, indoors or outdoors. It has to be in conduit when it's not underground. You can use SER if you want to. You might be able to route MHF so there are no splices, thus eliminating at least one junction box and splice taps.

SER can't be underground so if you want to use that, you'll have to splice it to the MHF.
I thought about doing a straight run but with all the angles I going to have more than the allowed 360 degrees of bends in the NEC code from what I read
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,111
Location
Modesto, CA
Huh well SER is cheaper and I from what I understand that's fine in conduit under the crawlspace right? Just MHF has to be outdoors
The SER doesnt need to be in conduit in the crawlspace. i wouldnt bother with conduit unless its gonna somehow get damaged.

The MHF is not restricted to outdoor use only. it can be used indoors but MUST be in conduit.... pick your poison...
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,067
Location
Central Iowa
True, you can't have more than 360° of bends, I like to keep it to a max of 270° but I don't know your route. You can use a box to change direction instead of a 90° elbow to pull through and not splice; the box has to be 6X the conduit size so a 1.25 pipe would need an 8X8 box minimum and at 10X10 or 12X12 would be better.
 
To avoid these ads, REGISTER NOW!
OP
1

1/4atatime

Well-known member
Joined
Jun 9, 2024
Messages
164
Location
VA
The SER doesnt need to be in conduit in the crawlspace. i wouldnt bother with conduit unless its gonna somehow get damaged.

The MHF is not restricted to outdoor use only. it can be used indoors but MUST be in conduit.... pick your poison...
Ok well that saves some money ser is cheaper and no conduit needed. I'll tap it into the MHF for outside
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,067
Location
Central Iowa
You aren't putting ser in conduit, right? That will be a nightmare to pull
It's not that bad unless an LB is involved. We can use SER outside, but it has to be in EMT or rigid so if I'm going across a crawl space, I use SER just to keep from having to run any kind of conduit. until I get through the wall.
 
OP
1

1/4atatime

Well-known member
Joined
Jun 9, 2024
Messages
164
Location
VA
Thanks everyone for the help. Sounds like the cheaper easier route then is SER under the house, then transition to MHF and direct bury it and then it saves me from having to pull through conduit anywhere (except of course some short pieces where it comes out of the ground outside to connect into the building.
 
OP
1

1/4atatime

Well-known member
Joined
Jun 9, 2024
Messages
164
Location
VA
One other question so I ordered these lights for my garage


However they don't seem to come with a plug to hardwire them like other led kits I have seen. Just the plug in the picture and plugs to link multiple together. Could I cut off one end of the plug that's used to link them together since it's a 3 wire plug and hardwire the light? Or do I need to keep them as is and plug them into an outlet. Just curious because if I can hardwire them it saves me having to run a GFCI circuit just for lights.
 

Attachments

  • Screenshot_20250409_135141_Amazon Shopping.jpg
    Screenshot_20250409_135141_Amazon Shopping.jpg
    280.7 KB · Views: 11

dutch724

Member
Joined
May 22, 2017
Messages
10
Location
Middlesex, NC
I don't see a reason why not. Cut it off and wire it in a j-box.