Emergency service disconnect grounding/bond question

OP
J

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
18,006
per their official load calc: 212A with a single EV charger.

Screen Shot 2022-11-05 at 8.59.08 AM.png
 
To avoid these ads, REGISTER NOW!

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,911
Location
Southern Oregon
this is the only 320a one they provide as best i can find with my google foo currently. i hope not since its OH entry.
For an UG feed the POCO wires will go up the right side gutter and loop over to the upper terminals.

Did you notice that panel has studs and not clamping lugs? You'll need some ring terminal ends or a dual lug kit.
 

Attachments

  • 1667613124466.png
    1667613124466.png
    1.1 MB · Views: 7

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,642
Location
BC
If one can be found somewhere. I have one back ordered, all the supply house will tell me is "sometime next year", When I ordered mine, they had 180 ordered and I was the 84th person to get my name on one. I have a friend that has one ordered from another supply house and they told him at least six months. In the mean time, there is a local mechanic that has a main that trips since he installed AC in his shop, now that AC season is over, he should be ok for awhile. (both meter mains are for the same job, when one of us gets one in, the other order is going to get cancelled.)
Good point. I forget about supply chain issues. I would probably postpone my project till I could get exactly what i wanted.

Ya, a bad main breaker is still a pita... whether in the can or main panel. I kinda like my fused disconnect 😆
 
OP
J

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
18,006
For an UG feed the POCO wires will go up the right side gutter and loop over to the upper terminals.

Did you notice that panel has studs and not clamping lugs? You'll need some ring terminal ends or a dual lug kit.

yup. 3/8 stud dual luggosss.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,642
Location
BC
bus bar rated to 225a is a thing i've seen. im still 20a short tho.
I was going by your 212A calculation.

I know I can get a 225A QO main breaker, and many of their panels have 225A rated bus.
 
OP
J

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
18,006
I was going by your 212A calculation.

I know I can get a 225A QO main breaker, and many of their panels have 225A rated bus.
oh thats just a load calc.

the issue is from the solar side. 21.6kw of panels going up.

there are 2 problems at hand to solve for.
 
OP
J

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
18,006
Well started dicking around with a conduit run. what does hive mind think on options:


Im not sure about this as it puts it right onto the window trim. not sure if code will even allow that. I cannot go under the pump control box. there is no room at all under it.

2022-11-05 12.11.17.jpg

if i go around the high side of the window and in plane with the electrical wall puts me on the trim again.
2022-11-05 12.11.53.jpg

i got room to bring it down off the trim. but a sweep 90 is too long and puts it off the boards. i'm thinking a piece of flex to bridge between. am i missing a much easier solution?
2022-11-05 12.12.03.jpg
 
OP
J

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
18,006
can you go underground?

my 3 ac condensers are right in this area. along with sewage and water supply line. its a tight area. even if i came down the left side of the window I hit the basement window.
2022-11-05 15.50.23.jpg


using the dryer exhaust vent as a reference to the prior photo: garage solar feeds coming in following the radon pipe on the left. going to 90 over to the security camera then pick up where the porch solar feeds come down. then over in a single pipe run over to the window area then the electric wall.
2022-11-05 15.50.28.jpg
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,642
Location
BC
Can you use a PVC jacketted armoured cable? Cable gives infinitely variable bends. It always impresses me how small they can keep the diameter for the ampacity.

Edit: I don't think landing it on the window trim is a problem other than appearances, so long as the window opening isn't compromised. Think of the mess that's otherwise attached to or crossing fascia boards, soffits, etc. Check with AHJ if in doubt.
 
OP
J

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
18,006
Can you use a PVC jacketted armoured cable? Cable gives infinitely variable bends. It always impresses me how small they can keep the diameter for the ampacity.

Edit: I don't think landing it on the window trim is a problem other than appearances, so long as the window opening isn't compromised. Think of the mess that's otherwise attached to or crossing fascia boards, soffits, etc. Check with AHJ if in doubt.
ah i think i have a solution. notch out the 6x6 and send it in on the back side to its panel. but that forces the panel to be on the left side. i gotta do a panel layout.
2022-11-05 16.33.19.jpg
 
To avoid these ads, REGISTER NOW!
OP
J

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
18,006
well holy **** I found a unicorn I think. I was looking at $90 to $150 for a main frame breaker replacement and $600+ for square D outdoor panel.



NEMA 3r rated
100a main breaker
225a bus rating.
Screen Shot 2022-11-09 at 5.38.54 PM.png

Screen Shot 2022-11-09 at 5.41.55 PM.png



someone wanna talk me outta this for my outdoor solar box? @wyliesdiesels ?
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
I guess this is gona turn into my drop point for info in case others decide to embark on this.

#6 solid for all the racking. the question now is can I use a ground bar in 4x4x4 pvc box to combine them into a single #6 to the ATS/solar main panel
I still worry that Leviton is going exit that market and the users are left with another Trilliant panel that breakers are hard to come by & a very high price when you do find them. If you do get it, buy spare breakers. Trilliant was a SQ D product that they discontinued, all non metallic panels, & proprietary breakers.
 
OP
J

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
18,006
I still worry that Leviton is going exit that market and the users are left with another Trilliant panel that breakers are hard to come by & a very high price when you do find them. If you do get it, buy spare breakers. Trilliant was a SQ D product that they discontinued, all non metallic panels, & proprietary breakers.

even if i buy an entire backup set of breakers im still cheaper than square D.
 

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,326
Location
Illinois near St. Louis, Missouri
Yes. All metal plumbing needs to be bonded. Its to prevent it from becoming energized. The bonding allows the breaker of the offending circuit to open and clear the fault current.

Ive seen what happens when plumbing isnt bonded.... have a i got a story for you...

Had a LL call years ago about tenants getting shocked when they touched the washer or a metal hose bib at one of her properties...

Took me a whole day of searching and then another to nail it down.

First thing i noticed was the water line wasnt bonded. When i bonded it to the meter main right above it, I got an arc and a breaker tripped (it was a shitsco panel).

So, then I knew the plumbing was energized but had to find where. This was a single family house that had been added onto and split into 2 units. (Oh boy; there was some other really questionable wiring like cordage running through the space between first and second floor to feed the detached garage sub-panel via overhead drop :shocking: , garage subpanel was bonded despite having 4-wires, dryer receptacle was installed out in the weather, was 4-wire but connected as 3-wire etc)

So through my searching i discovered the gas stove and refrigerator on the addition unit, were electrified also.... this started to get interesting.... finally i discovered that the ground terminal on the receptacle for the fridge and stove was energized.

Pulled the receptacle out of the j box but found nothing suspect.

Righ then i knew someone had ran an NM staple through the NM at some point in the wall.

But the EGC at the panel for this circuit was connected to the neutral bar..... :headscratSo that told me there was a splice somewhere and the EGC lost its connection at some point.

This particular circuit actually fed stuff on both units so would be a nightmare to find...

So off to demo some sheetrock to search. I didnt want to be responsible for the drywall so the LL had her handyman come over to start ripping sheetrock out.

We tore quit a bit out but i couldnt find the staple.

LL didnt want to keep going so i just disconnected the EGC from the receptacle, told her to plug the stove and fridge in elsewhere, dont use the receptacle and that she would need to have me or someone come back to find the issue.

This was a fairly large 2 story house on one side and single story on the other for the second unit.

Wouldve been a ***** to find the problem and with active tenants living in the unit im guessing the LL never bothered to dig further...
When I bonded the gas and water lines in my 2003 build the plumber looked at me with a wierd look and thought it was a safety issue having it bonded.

As for finding the offending staple I have used tdr to get some idea of the location. Saves a lot of work when the wires are buried. Found a junction box hidden in a kitchen cabinet soffit that way.
 
  • Like
Reactions: Max

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
When I bonded the gas and water lines in my 2003 build the plumber looked at me with a wierd look and thought it was a safety issue having it bonded.

As for finding the offending staple I have used tdr to get some idea of the location. Saves a lot of work when the wires are buried. Found a junction box hidden in a kitchen cabinet soffit that way.
sounds like the plumber wasnt an apprentice... how could it be a safety issue with it being bonded? makes no sense
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
He was quite experienced, in fact the head of a small plumbing company, and did a good job on the plumbing. Not sure why he thought bonding would be an issue. Maybe it was not regularly done in this area at the time.
The opposite is actually a safety issue.

Imagine the gas line not being bonded, becomes energized then someone goes to work on the gas line they shut the gas off but there’s still a little gas in the line. They disconnect a pipe get a spark which could ignite the gas
 
OP
J

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
18,006
The opposite is actually a safety issue.

Imagine the gas line not being bonded, becomes energized then someone goes to work on the gas line they shut the gas off but there’s still a little gas in the line. They disconnect a pipe get a spark which could ignite the gas

Code is written in blood. sadly.
 
OP
J

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
18,006
sticker to 225a, main at 100a. this lil guy saved me a few hundred easy. which means my AHJ will say no, white breakers actually are only rated to 10.0 amps and thus you need to pull in 3 phase 7.6kv. or something equally costly.

2022-11-13 17.59.48.jpg



Screen Shot 2022-11-13 at 6.54.03 PM.png
 
Last edited: