Extension Cord Question

tubamonster

Active member
Joined
Jul 23, 2012
Messages
32
Location
Alabama
I have a 3450 rpm 3/4 hp electric motor that came from a pool pump. The cord on it is only about 2 feet long. I am planning on using this motor to build a belt grinder, and I will need a 25 foot extension cord because their are only a 3 electrical outlets in my garage. The cord on the motor is 12/3. Because it is a pool pump, it says do not use an extension cord. I figure using an extension cord shouldn't be a big deal considering it will be nowhere near water and plugged into a GFCI outlet.

My question is do I need a 10/3 extension cord or will a 12/3 extension cord do just fine? I'm on a serious budget and cannot afford to spend a few extra dollars for a 10/3 extension cord if it isn't absolutely necessary.
 
To avoid these ads, REGISTER NOW!

malibu101

Well-known member
Joined
Jul 1, 2005
Messages
3,910
Location
Walnutport PA
I agree that a 12 gauge cord will be fine.
You are probably plugging it into a circuit that is protected by a 15 or 20 amp breaker. Right?

For this application I would certainly use no smaller than 12 but I can't see a real reason to go larger than 12 either.
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
12 gage will be fine. I built my building with a 1 1/2 HP compressor on the end of a 50' 12-3 cord.
 

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,931
Location
oregon
I have a 3450 rpm 3/4 hp electric motor that came from a pool pump. The cord on it is only about 2 feet long. I am planning on using this motor to build a belt grinder,

As others have said 12 ga should be fine. However pay attention to the grinder in operation as it is easy to overload the motor and put it to max current and beyond. If your using it hard enough to slow down the motor then back off a bit.

lg
no neat sig line
 

RECox286

Well-known member
Joined
Apr 11, 2012
Messages
1,399
Location
South Joisey (yeah, that is part of the USA)
Unsure of the reason for the warning about using an extension cord for the original

purpose of the motor, but since it is usually an outside application, I should think

that the use of an extension cord puts more connections in the circuit.


More connections to become corroded, and cause more resistance/heat, more

resistance, equals a burnt up cord or motor. (guessing but seems logical)

Since most people are unaware that extension cords come in different gages, I

might also expect to find a piece of 16-2 cord inbetween the receptacle and the

motor ! We do see anything and everything out in the field, do we not ?

Uncle Bob
 

rodm1

Well-known member
Joined
Feb 17, 2008
Messages
2,275
The warning is for people like my Mom that use a 16ga extension cord to run the refrigerator and everything else! The wiring in your home is not much different then an extension cord just sized properly.

You should only buy 14ga or 12ga extension cords any ways.
 
To avoid these ads, REGISTER NOW!

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,604
Location
SE MI
Unsure of the reason for the warning about using an extension cord for the original purpose of the motor, but since it is usually an outside application, I should think that the use of an extension cord puts more connections in the circuit.
More likely the manufacturer did not want to see some one trying to run it off the end of a 100' 16/2 cord !
 
OP
T

tubamonster

Active member
Joined
Jul 23, 2012
Messages
32
Location
Alabama
Thanks for the replies. I already figure 16 gauge wasn't a good idea. I'll be getting a 25 ft 12 gauge cord.
 

Kevin C

Well-known member
Joined
Aug 4, 2011
Messages
1,653
Location
Portland OR
Assuming the motor draws 9 amps ( 70% efficiency, 100% loading) the voltage drop on a 25 foot, 16 gauge extension cord would be about 1.8% or 2.2 volts.

A 14 gauge gets you a 1.4 volt drop. 12 gauge .9 volts... 10 gauge .5 volts.

Also, this application should be intermittent duty VS a pump that can be used continuously.

With a 16 gauge cord, so instead of 120 volts you get 117.8.

I dont see any issue using a 16 gauge extension cord.
 
Last edited:

rodm1

Well-known member
Joined
Feb 17, 2008
Messages
2,275
The problem with under sizing your extension cord is you are making it a fusible link instead of the breaker being the week link.
 

Kevin C

Well-known member
Joined
Aug 4, 2011
Messages
1,653
Location
Portland OR
The problem with under sizing your extension cord is you are making it a fusible link instead of the breaker being the week link.

This is based on ? Are you saying that a 16 gauge cord will burn out before it clears a short on a 20 amp circuit?

The one second fusing current of 16 gauge wire is 377 amps. At 32 ms the fusing current is 2100 amps. I know that will trip my 20 amp breakers.
 
Last edited: