Floating neutral generator to house

robh1

Member
Joined
Sep 17, 2019
Messages
8
Location
Cleveland OH
Hi everyone.

I've been reading multiple opinions on this and was hoping to get something definitive.

I bought and installed an interlock kit on my main panel and connected a separate 30A breaker to an inlet box for a generator.

My portable generator has a floating neutral.

For the purposes of (extra?) grounding, is there anything I need to do other than plug my generator in once Interlock & main breakers are swapped? Any issues with grounding or neutrals?

Thanks.
Rob
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,268
Location
Modesto, CA
You didnt specify generator size and voltage, number of wires in cord, etc

But the generator needs to have a floting neutral because neutral is already bonded in main service panel.
 
OP
R

robh1

Member
Joined
Sep 17, 2019
Messages
8
Location
Cleveland OH
Honda EU2200i for now. 3-wire to 4-wire cord to light up both hots in panel. I'm aware of the manual intervention for 220V circuits and the like.

Roger that on the floating... thank you!
 
To avoid these ads, REGISTER NOW!
OP
R

robh1

Member
Joined
Sep 17, 2019
Messages
8
Location
Cleveland OH
Yep, unfortunately. It's only a 2200/1800W generator, but I will have to be careful. I assume as long as I manage the load I'll be okay? The combined outlets are never used together.
 